What size fuse should I attach to the positive terminals of my AGM battery bank?
Matty
Registered Users Posts: 36 ✭✭
I am trying to determine what size fuse I should attach to the positive terminals of the batteries in my AGM battery bank. I am confused as to whether the selection of amperage is related to the gauge of wiring used to connect the batteries, the size of the load that is to be placed on the batteries, the size of the current that would be drawn by inadvertently connecting the positive and negative terminals with a conductive material or a combination of some or all of these factors?
Comments
-
The value of the over current protection device (OCP) is directly related to the capacity of the conductors it is protecting in the event of a short circuit event, not the anticipated load. Batteries can supply enormous amounts of current, so the fuse/breaker will limit the current so as not to make the conductors themselves become the fuse. The value of the OCP can naturally be less, but never more than the conductors rating.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:The value of the over current protection device (OCP) is directly related to the capacity of the conductors it is protecting in the event of a short circuit event, not the anticipated load. Batteries can supply enormous amounts of current, so the fuse/breaker will limit the current so as not to make the conductors themselves become the fuse. The value of the OCP can naturally be less, but never more than the conductors rating.
-
Without protective covers on the terminals there's really nothing to stop a dropped non insulated tool from turning into a red hot puddle of molten metal if accidently dropped across battery terminals. It's a good idea to use insulated tools in this situation. There's a product called Plastidip, I think, that can be used to insulate the handles of wrenches. As already mentioned by mcgivor the fusing/breaker is sized to protect the conductors its connected to. The size of the conductors in the case of an inverter for example, would be recommended by the inverter mfg.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
The use of tables is generally a good starting point, wether it be IEE regulations for the UK, or NEC for the U.S., they are all very similar, depending on insulation type, ambient temperature and so forth. The values are usually pretty conservative but it is wise to follow guidelines as there is no way of knowing how a short circuit may occur, by shifter I would assume British, that would be a worst case scenario, but this would illiterate what is possible. My advice, would be to follow the guidelines provided within the regulations relevant to the location the installation.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
You are in Australia, and I do not know your electrical codes and wire designations... Here is an example of US codes and how we would size a system.
Say your maximum load current is planned to be 100 Amps continuous (many minutes to hours of continuous usage).
In the US, I use a 1.25 derating factor (our fuses/breakers are generally rated to break, eventually, at 100% rated current, and not breaker at 80% of rated current):- 100 amps * 1.25 NEC derating = 125 Amp minimum rated branch circuit (wiring and breaker/fuse)
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
Wire AWG (American Wire Gauge) ranges from 2 AWG (high temperature rated insulation) to 1/0 (heavier thickness wire, lower rated temperature insulation).
Or you can use the Marine Recommended ratings (note that SAE gauge is slightly smaller than AWG gauge):
https://www.westmarine.com/WestAdvisor/Marine-Wire-Size-And-Ampacity
Note that (very roughly) the Marine rating is 2x that of our NEC current capacity... I highly recommend that you use the conservative NEC ratings and not use the less conservative Marine ratings.
Also, on that above link, is an example of wire length vs AWG vs current... You want heavy/short wire runs to keep voltage drops low.
For 12 volt battery systems, I suggest 0.5 volt maximum voltage drop (you may need heavier wire for longer runs--You can "up rate" the fuse/breaker because you use heavier cable if you wish, or not--Your choice).
Circuit breakers are very nice... Both for protection and to use as on On/Off switch.
Good quality fuses are not cheap (as you get higher current ratings) and the holders are not cheap either (plus you need to keep a couple spares on hand if you pop a fuse while out camping).
However, fuses can be nice for tight spaces... BlueSea makes a very nice/small fuse holder:
https://www.bluesea.com/products/category/16/72/Fuse_Blocks/Terminal_Fuse_Blocks
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I like the blue seas battery terminal fuses (dual is handy, one for loads 200A , one for charger 60A )
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed