Registered Users Posts: 439 ✭✭
I'm going to upgrade my 12 volt battery bank to 416 amp hrs. 416x14.4÷.77×.13=1011 watts. 400 watts on a 30 amp and 600 watts on a 50 amp cc. Winters i stay close to myrtle beach With 4.08 sun hrs in Dec. Daily useage 25%. After a rainy day at 50 % soc and 13% charge rate. wouldn't I come close to full charge in 1 day with clear sky's on mppt?
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Comments
-
Seems to me that could work, as long as array can be tilted (~30°) and faced south. If mounted flat, it looks like pvwatts has Dec at more like 2.5hrs full sun equivalent.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Panels would be on a pole and adjustable.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
I have found that due to the way batteries accept a charge getting them to 80% SOC works well with solar, but getting them to 100% on solar alone when they are used every day is almost impossible even with very long sun hours. I am a newbie so I am hoping I am doing something wrong, but what I found is that once the batteries hit 80% and the cc switches to absorb the amperage charging the batteries starts to drop fairly quickly making my 640 watts of panels put out way less than what they will do when bulk charging, no matter where the sun is.My original thinking was I might get 50amps to the batteries for 4 or so hours, but in reality the 50 amp of charge only occurs when the batteries are being charged in Bulk mode. I have seen the charge at 10 amps at solar noon in ABQ after watching 45 amps going into the battery at 10am.Basically I have to run the genny in my RV to get them to 100%. I found that running it in the morning to bring them up to 80% screws up my Victron CC by making the starting voltage the cc see's higher and shortens the absorb charge to maybe an hour or two when it should have been on absorb for 6 hours. Still a work in progress for me. Hope your's works better, but with just 4 hours of sun I would like to hear how it works. From what I am seeing, adding more panels isn't as effective as I once thought it would be.-Bill4 each Renogy 160w Solar Panels mounted flat on RV roof, Serially connected @ ~80v, Victron 100/50 MPPT controller. 520AH LA batteries @ 12volt, 2800w PSW Magnum Inverter. Bogart Trimetric.
-
In my humble opinion (I am not a battery engineer), you do not need to reach 100% every day--And in fact, it is bad for lead acid batteries to do this. Basically "Equalizing/Gassing" FLA batteries every day is pretty hard on them (plate corrosion, plate erosion, loss of water, elevated temperature).
The goal should be >90% State of Charge at least once per week. As long as the batteries are cycling (say somewhere in the range of 50% to 80%) during the week, they will be fine.
Batteries sitting below 75% state of charge (day/days/weeks) uncycled--That is when the batteries begin to sulfate more quickly.
On battery mfg had suggested to one of our members that you only needed to get the battery >90% SoC once a month...
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
bigbillsd said:... but what I found is that once the batteries hit 80% and the cc switches to absorb the amperage charging the batteries starts to drop fairly quickly making my 640 watts of panels put out way less than what they will do when bulk charging, no matter where the sun is....
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
IMHO, 6 hours is too long for absorb. With a grid connected charger, maybe a longer, lower voltage absorb would make some sense for some batteries. Off-grid charging with generator/solar and healthy (lead acid) batteries though, voltage should be high enough to get current down to 1-2% of capacity in a couple of hours.
If it's taking 6hrs, I'd wonder if the absorb voltage is too low (so it goes into absorb too early), or too high (batteries are full and current is heating the bank instead of charging it). Is charging voltage adjusted with a remote temperature sensor?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I wasn't trying to hijack this thread, just wanted to point out to the OP that solar charging batteries may not work as he was thinking. I will call Crown, my battery manufacturer to get their take on how often I should take my batteries to 100%. I had always heard our LA batteries want to be at 100% all the time... Yes, 6 hours might be too long, but 15 or 20 minutes seems way too short if it went for hours at Bulk then less than an hour in Absorb when it dropped to float..
4 each Renogy 160w Solar Panels mounted flat on RV roof, Serially connected @ ~80v, Victron 100/50 MPPT controller. 520AH LA batteries @ 12volt, 2800w PSW Magnum Inverter. Bogart Trimetric. -
I looked at pvwatts at 37° gives me 4.31 hrs in dec So back to my question. Bulk charging stage 1000 watts roughly 55 amps 416 amp hrs @12 volts from 50% soc to 80% with losses 135 amp hrs needed about 2.5 hrs. Leaving 1.8 hrs in absorb 80% to 90 % is around 42 amp hrs. Would 1.8 hrs get me to 90%?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Keep in mind 4.3hrs is an average full sun equivalent. Some days will be cloudy, with little/no sun, others will be longer. Also, once you get to absorb current drops off anyway, so even the low afternoon sun might be enough to keep absorbing. Bottom line is I think some days you should get to full, and others you won't.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
@mountainman If I am reading your post correctly, you will be using 25% of your 416AH battery bank. You roughly have to replace 104 AH of power, probably more like 114+ AH. If it were all in bulk charging you could reasonably expect to accomplish that. But in reality you will probably only be in Bulk for an hour or so then the panel output will throttle down quite a bit once it hits absorb. My guess is you will not be able to get to 90% SOC in your 4 hours of sun from 75%. And from 50% SOC you will be very lucky to get to 80% in 4 hours. Also, when using 2 controllers you should check with the vendor to see how they will interact. Some do not play well with others.
4 each Renogy 160w Solar Panels mounted flat on RV roof, Serially connected @ ~80v, Victron 100/50 MPPT controller. 520AH LA batteries @ 12volt, 2800w PSW Magnum Inverter. Bogart Trimetric. -
@bigbillsd from 75%to 90% is only 15%. 62 amp hrs. If a 1000 watt array in 4 hrs wouldn't produce 62 amp hrs, then I need to spend the cash on a bigger fuel container for the generator.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
My 1000w array would do close to the 15a needed even in light overcast conditions.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
If I understand it correctly from 50 to 80 fla will accept what ever amps you put in. At 80% the battery starts accepting less amps at a constant voltage. Close to the end of absorb 3 to 5% roughtly on a 416 amp hour bank 2 or 3 hundred watts would surfice. no matter how large your array is the rest is not producing anything. After many hrs of research on line, rolls has a formula for absorb time on there batteries at 10% rate of charge. From 80 to 100% Time=0.42×416/41.6=4.2 hrs. bulk from 50 to 80% soc. 125 +10% 137 amp hrs needed ÷41.6=3.3 hrs. . So 7.5 hours from 50.to 100%. Conclusion lead acid takes more than 4.2 hrs to complete a full charge even with perfect sun from 75% soc.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Give up and quit now... Just a suggestion.
Flooded lead acid will accept about 13% of it's capacity in bulk, (When 50-80% SOC) More in some batteries dependent on design and thickness of plates. I was told 15% with my forklift battery, I suspect Rolls high capacity batteries are made with similar thick plates.
Of course the array can and will produce more than is used for battery charging, that is the reason most people living off grid load shift to use energy when the sun is shining and the batteries don't need the extra... Also starting 'opportunity loads' in my case I run a water heater.mountainman said:Conclusion lead acid takes more than 4.2 hrs to complete a full charge even with perfect sun from 75% soc.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
To me, a 10% rate of charge is the bank capacity rating (20hr room temp) x 10%. Most FLA are okay at, and will take 15% or a bit higher rate (if available) at under 80% SOC, and are quite efficient in that range. This implies roughly 3hrs for 50-80% SOC at a 10% rate.
I consider my bank full when absorb current drops to a bit over 1%. This generally takes 2-3hrs. Total time from 50-100%SOC ~5-6hrs with good sun. From 75%, it would be roughly 3hrs.
4.2 hours on pvwatts is full sun equivalent hours. That would be 4200watts/sq.meter on average daily. Even full sun at noon may not be "full" (defined as 1000w/sq.m), but rather (eg) 500w/sq.m, so it would take two hours at that insolation to make one full sun equivalent hour.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
One reason I use rules of thumbs is they are "good enough" to design and run systems that will meet most people's needs (if you have low current drain 24x7, that is a different system that runs 5 hours in the evening, or runs high power during the day for irrigation, etc.).
Here is a nice article that shows the "complexity" of trying to understand a Lead Acid Battery:
http://www.scubaengineer.com/documents/lead_acid_battery_charging_graphs.pdf
People are (generally) very inconsistent about their use of energy... Some base load systems (like refrigerators) and more variable like tools, when to run the washing machine/pump water, kids inside playing on the computer/watching TV. Toss the variability in solar radiation (seasonal, time of day, weather, haze, growth of the trees next door, etc.)--And it is much easier to (conservatively) design your solar power system so that it will support most of your needs and you can use a genset (or stop using optional power) to carry you through when the sun isn't shining or you use more power than average.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
In my original post I had planned to use a 30 amp mppt cc with 400 watts.And 600 wattson 50 amp cc. but on second thought. Someone please correct me if I'm wrong. With 400 watts on cold days I could possibly see 27-30 amp peaks? 600 watts on 50 amp cc again on coldest 25f days 43-45 amppeaks 75 amps on a 12 volt 416 amp hour battery? Wouldn't it be better to run 2 30 amp controllers 500 on each. To limit charge amps in winter to a more reasonable 13 or 14% limit? My thoughts are in the heat of summer. 500 *.77=385/14.5=26.5 x 2 arrays 53 amps close to 13%. Any suggestions or criticism would be appreciated.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Personally, I'd run two 50a controllers. Most can limit output in settings.
IMHO it's better to not run controllers at near max capacity for long periods.
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Well since i already have a 30 amp pwm and a 30 amp mppt, 4 100 watt panels and 4 6 volt 208 batterys this is what im trying. I bought a 265 and a 260 watt 60 cell panel. On mppt for a 12 volt bank (not sure if I should wire them in parallel or series?) I'm thinking 525*.77=405 watts /14.5 volts 29 amps+ 400 watts on pwm 22 amps. 51 amps total. Roughly a c/8 charge rate on a 416 amp hr @ 12 volts with a 925 watt array. If and when my controller crashes and burns I'll get a bigger one while limping on the other one.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
All I'm reading here makes lithium look like a GREAT choice.
-
By cariboucoots calculations even on pwm 525/17.5=30 amps 400/17.5 =22.85 (52.85) close to 13%. What if I put 1 panel on 170°and 1 on 190° wouldn't that bring the peak down and give more over all production?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Lithium? Very often in winter we have 15f temperatures.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
mountainman said:Lithium? Very often in winter we have 15f temperatures.
https://batteryuniversity.com/index.php/learn/article/charging_at_high_and_low_temperaturesLi ion can be fast charged from 5°C to 45°C (41 to 113°F). Below 5°C, the charge current should be reduced, and no charging is permitted at freezing temperatures because of the reduced diffusion rates on the anode.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Is it possible to aim 2 panels in series in slightly different positions on a single mppt controller?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Generally speaking, you want to avoid putting different oriented arrays on a single mppt, as they can have different maximum power points much of the time.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
mountainman said:Lithium? Very often in winter we have 15f temperatures.
-
mountainman said:$2600.00 for a 200 amp hour battery.You got that right about bringing it inside.@Oldman does it pull power from the night air?
-
Ease up on the "mind reading"... Personally, whether or not I watch Fox News--I cannot, simply because I am too cheap to pay for cable.Same thing with statements how/where/why folks store their batteries... Provide answers (temperature range for active batteries) and/or ask the questions.There is no body language with forums, or instant one on one feedback for jokes and snark (and I love snark). Just be upfront and treat all visitors/members with honor and love.Take care and happy holidays,-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
Thanks all merry Christmas2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed