OFFGRID Over Voltage problem

Options
This is my setup.

6x 250w solar panels= 1500watts
8amp x 6 = 48amp.
specs: http://www.solardesigntool.com/components/module-panel-solar/Helios-Solar/1637/6T-250/specification-data-sheet.html


2 x 55ah lead acid batteries.
1 Solar30 30A charge controller purchased on ebay.
specs: http://www.chinasolarregulator.com/user-manual/SOLAR30.pdf

30A Spare Charge controller:
http://www.ebay.com/itm/361122416453?_trksid=p2057872.m2749.l2649&ssPageName=STRK%3AMEBIDX%3AIT

The problem?
My charge controllers stops working with weird message, not understandable on LCD. I press load button and returns back to work.
Spare charge controller first light will blink , and as I understand its because over voltage protection.


As you can see I have in my array more Amps than supported by Solar Charge Controller, but isn't the controller just going to take 30Amps and leave the 18 remaining amps available on the string ?

I measured the voltage and it was 26v, 28v, 32v maximum. Charge controller its supposed to handled less than 48v DC.


I connected solar30 and 30A Spare controllers in parallel expecting a total load of 60A to be handled , but the spare controller almost immediately activated over voltage warning.


Over voltage means over DC Voltage or Over DC Amps?


Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Welcome tot he forum Carlos.

    PWM controllers are "on/off" type of charge controllers. They really do not have the ability to limit current. So, to high of current solar panels can damage the charge controller. So, these controllers are really too small for your application--You would need a higher rated controller for that amperage of solar array.

    In any case, I have quite a few questions about your setup.

    First, what is the voltage of your battery bank? 12 volts or 24 volts.

    Next, a PWM charge controller really needs to match the Solar array Vmp-array with the battery bank voltage. For a 12 volt battery bank, Vmp-array should about 18 volts. And for a 24 volt battery bank, Vmp-array should be about 36 volts.

    If you have a Vmp~30 volt array with a 12 volt battery bank, you will only get about 1/2 of the array wattage charging the battery bank. If you are charging a 24 volt battery bank, Vmp~30 volts is too low--The solar array will not generate enough voltage to properly recharge the battery bank. Vmp of solar panels is temperature dependent. For a hot panel, Vmp falls as the sun warms them up. On a very hot day, Vmp-array can fall towards 24 volts for a Vmp 30 volt panel. And to properly charge a 24 volt lead acid battery, you need around 29 volts minimum to do that.

    Next, you talk about a 60 amp load... If you are using the load terminals on the charge controller--That is too high. At best, the terminals are probably rated for 30 amps--And some controllers, they are rated for 8 amps maximum. 60 amps is way too much.

    And finally, the battery bank. 55 AH at 24 volts (two batteries in series) or 110 AH @ 12 volts (two batteries in parallel) is a very small battery bank for a 60 amp load and for 48 amps of charging current. If these are flooded cell batteries, you would be hard pressed to support a 60 amp load--I would expect the battery voltage to collapse. If these are AGM batteries, they may support the load--But they will not last very long (you will take them flat in less than two hours or so @ 12 volts, or less than one hour @ 24 volts)--Plus it is very hard on the batteries (they will not last very many cycles).

    Plus, having too high of charging current available for a small battery bank--The solar panels can take the 12 volt battery bank to >> 15 volts charging. Solar charge controllers are not really designed to "regulate voltage"--The battery bank really regulates voltage short term. A charge controller does regulated long term voltage to manage the rate of charge/state of charge of the battery bank. If this is a 24 volt battery bank with your solar panels--Even though this is too high of charging current--These panels are not really capable of over voltaging the battery bank (they may over voltage the battery bank on cool days/short periods of time--but there are a lot of details and "what ifs" that I really cannot answer with the information available).

    To help you with your system--We really need to understand your loads (amps, amp*hours per day, battery bank voltage, etc.)... That will let us define the optimal battery bank. Then we can look at the size/type/configuration of solar array and charge controller needed to meet your needs.

    In general, it appears you are expecting a lot from a smaller off grid solar power system. For a reliable/long term operational off grid power system--I would be suggesting a much larger battery bank, and a different charge controller (more expensive MPPT type for use with your present solar panels). I don't think you can do what you want/need with the present setup.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • porrascarlos80
    porrascarlos80 Registered Users Posts: 4
    Options
    Hello Bill (BB).

    Thank you!! I really appreciate your help!


    What is the voltage of your battery bank? 12 volts or 24 volts.
    24volts

    What inverter do I have?
    1200Watt / 2000W Peak Pure sine wave inverter 24v to 110v.


    In regards to the load:
    Basically the way I have it, is :
    PV - / + array terminals connected to +/- terminals of the SOLAR30 charge controller.
    24v dc batteries connected to +/- terminals of SOLAR30 charge controller.
    24v dc relay , connected to load terminals on SOLAR30 charge controller. When to load turns on, it energizes the dc relay, and it switches on / of my inverter.


    I purchased a small DC relay, when the load goes on , it will activate the switch and therefore power on the inverter.

    When the battery its getting low, load should go off, relay should switch off the inverter.

    I will take pictures , create diagram, ideally capturing charge controllers errors. Or perhaps better a video.

    2 batteries in Series, 24volts its what I have.

    I have other things in place but I will include those things in a diagram hope later.

    thx again.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    OK... So how many Watt*Hours or Amp*Hours per day do you plan on using... You can get (or sometimes borrow from a local library) a Kill-a-Watt type power/energy meter.

    The Kill-a-Watt meter and this relatively cheap (and "good enough" for our needs) DC/AC Current Clamp DMM from Sears will give you some very nice tools to understand your loads and how it all plays together (plus let you debug stuff when needed).

    I hesitate to tell you how to "fix" your system without more information on loads. If your AC inverter is your loading needs... A rule of thumb system design would look like this (a reasonably reliable system that you could run full time off grid power/loads with).

    First the battery bank... For a 24 volt battery system, you want about 200 AH per 1,000 Watt of AC inverter rating minimum (you could have a 2x or larger battery bank if your peak loads are low but you use a smaller amount of power over 12-24 hours per day):
    • 1,200 Watt AC inverter * 200 AH (@ 24 volt battery bank) / 1,000 Watts of AC inverter = 240 AH @ 24 volt battery bank minimum
    Also, that rule of thumb works out pretty well for estimating the largest solar array you should connect to a battery bank...
    • 6*250 Watt array * 200 AH / 1,000 watt of solar panels = 300 AH @ 24 volt battery bank minimum based on your solar array
    To charge such a battery bank, you would need 5% to 13% rate of charge. 5% for seasonal/weekend power... Recommend 10%+ for full time off grid power (i.e., off grid cabin/loads). In your case, I would suggest 300 AH @ 24 volt minimum battery bank based on your array size:
    • 300 AH * 29 volts charging * 1/0.77 panel+controller derating * 0.05 rate of charge = 564 Watt array minimum
    • 300 AH * 29 volts charging * 1/0.77 panel+controller derating * 0.10 rate of charge = 1,130 Watt array nominal
    • 300 AH * 29 volts charging * 1/0.77 panel+controller derating * 0.13 rate of charge = 1,469 Watt array "cost effective" maximum
    You can rewrite the math and, for example if you pick 10% rate of charge, your 1,500 Watt array would support a battery bank of:
    • 1,500 Watt array * 1/29.0 volts charging * 0.77 panel+controller derating * 1/0.10 rate of charge = 398 AH @ 24 volt battery bank (nice nominal design)
    So--for your present system, a 240 AH to 398 AH battery bank would be a really nice size.

    Now, what could such a battery bank support. Say we choose 398 AH @ 24 volts (4x 6 volt @ ~200 AH "golf cart batteries in series, and two parallel strings for a total of 8 batteries). Generally, 2 days of no sun storage and 50% maximum discharge on an AC inverter system:
    • 398 AH * 24 volt battery bank * 0.85 AC inverter eff * 1/2 days storage * 0.50 maximum discharge (for longer battery life) = 2,030 Watt*Hours per day for 2 days of "no sun"
    And you also have a 1,500 Watt solar array... You sun may vary between 2 hours of sun (average) per day in winter to over 6 hours per day in summer. You can use a tool like this to figure out "how many hours per day" by month for your system. Assuming you live in a relatively sunny region with 4 hours of minimum sun for 9 months of the year:
    • 1,500 Watt solar array * 0.52 off grid system eff * 4.0 hours of sun per day = 3,120 WH per day in "nominal sun"
    Of course, actual solar radiation varies with weather (and seasons)--Your "base loads" should probably be around 65-75% of your "predicted output power"... You don't want to be on the "edge" of loads vs available power--You end up having to "manage" the system and loads every day--Some people love that, others hate it.

    Then there is picking a solar charge controller... Because you have Vmp~30 volt solar panels, you need a MPPT type charge controller (maximum power point tracking) to charge your battery bank efficiently. The minimum size controller should be:
    • 1,500 Watt array * 1/29 volts charging * 0.77 panel+controller derating = 39.8 amp minimum recommend MPPT controller (price/performance minimum)
    MorningStar makes a nice TS MPPT 45 amp charge controller. Midnite and Outback make larger (60-90 amp) charge controllers too... Any of those would be good choices (read the manuals/ask questions--These are very complex pieces of hardware--And not cheap). There are other, less expensive charge controllers out there--Some good, many not so good... Do your research.

    If you get flooded cell batteries, another needed tool is a hydrometer to measure specific gravity for each battery cell. The "gold standard" for estimating battery capacity/health. This one is pretty nice. Be sure to rinse with a couple squirts of distilled water before putting away (drying electrolyte gets sticky/gummy).

    I will stop here--There is a lot of math and choices to be made--And your loads is the information we need to make these system design choices. I have made lots of guesses--This will help you narrow your choices, but the details of your needs are all that matter--My guesses are just guesses.

    Hope this helps.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    One thing Bill did not mention is that you will need a combiner. You will be putting two solar panels in series to make a 60 volt (Vmp) string, and then combining three of those strings in parallel to go to the MPPT controller. Since you have more than 2 strings you must have circuit breakers on each string. I suggest you take a look at the Midnite MPV3 combiner and use it with 3 Midnite circuit breakers.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • porrascarlos80
    porrascarlos80 Registered Users Posts: 4
    Options
    Bill,

    thanks for the clamp on meter recommendation. I will buy my own one.

    I tried to create my own diagram using visio but that was not possible as for now . then I created my hand made version.

    At this point , I just want to use batteries as transient storage for the energy taken from the sun. Energy hits panels, I download it to batteries using a charge controller, and I get it out using my Inverter not discharging batteries more than 60% to increase life cycles . I wont at this point save energy for nite. When batteries voltage decreases a automatic transfer switch , will get power from my provider. Later when I build my home, then I will consider re working and expanding.


    thanks for the suggestions and I do agree , I need more and bigger batteries, but unfortunately i purchased these ones and I have to live with them until the end of their days or mines. Meanwhile I am looking to buy in the future trojan 6v 270ah , buy a pair and put them in series. Perhaps 4 batteries.

    In regards to the current Yes! I have more current than expected by controllers and that may be causing SOLAR30 Controller errors or causing it to HALT.

    I created a couple of videos , see links below. The SOLAR30 has that error on the lcd screen , however measuring the battery terminals I see current , probably charging battery.

    So, I need to buy a bigger capable CC . Something curious is why the other 2 etracer MPPT 20A charge controllers doesn't complain? could it be because MPPT controllers supports 150V DC? but MPPT ones are just 20Amps.

    My plans are to build 3 independent circuits but connected to the same solar panel array, and according to the mathematics shown by Bill these may need additional stuff to work:

    Circuit one (5 LED Lights 5w each for home barely used):
    1 MPPT charge controller 20A , 150VDC
    1 AGM 75ah Battery
    1 300 Watts pure sine wave inverter
    1 SOLAR30 charge controller to power on and off the inverter only.
    1 Automatic Transfer Switch 110v 15A.

    Circuit 2 (TV, Refrigerator, computer stuff)
    1 SOLAR30 charge controller 30A 48v DC
    2 Batteries lead acid 55ah each.
    1 1000/2000 watt Pure sine wave inverter.
    1 SOLAR30 charge controller to power on and off the inverter only.
    1 Automatic Transfer Switch 110v 15A.

    Circuit 3 (Cofee Maker, Rice Cooker or any other kitchen device not exceeding 15A 110V AC , one at the same time
    1 MPPT charge controller 20A , 150VDC
    1 GEL 100A Battery
    1 1500/3000 w pure sine wave inverter 12v
    1 SOLAR30 charge controller to power on and off the inverter only.
    1 Automatic Transfer Switch 110v 15A.


    So, I need to buy a bigger capable CC . Something curious is why the other 2 etracer MPPT 20A charge controllers doesn't complain? could it be because MPPT controllers supports 150V DC? but MPPT ones are just 20Amps.


    Possible solutions:
    1. buy bigger solar charge controller to be in safe spot lets say 60A even better 80A.
    2. separate panels in parallel chunks of 25Amps. assign a controller to each chunk.
    Correct?

    Videos:
    System overview, sorry not studio made footage.
    https://youtu.be/6UN96MlvRgQ

    Solar30 working but spare charge controller complaining about over voltage
    https://youtu.be/iFhtMtwJNCA

    Solar30 error but charging?
    https://youtu.be/DD_vuNV9rp8

    Diagram attached. Attachment not found.

    Thanks Bill and VTMAPS for your comments and feedback.





  • Photowhit
    Photowhit Solar Expert Posts: 6,003 ✭✭✭✭✭
    Options
    You should disconnect every thing and create a balanced system, and fix some glaring problems.

    You appear to have much too small a battery bank for your arrays or your planned uses.
    You appear to have the potential of @ 35 amps going into a battery bank of 55 amps.
    You have solar panels that are NOT designed to charge 24 volt batteries without a MPPT type charge controller, hooked up to PWM charge controller and a 24 volt bank.
    Most PWM charge controllers will try to pass along all incoming current, Some/Most MPPT charge controllers can limit the amount of current passing through.
    With out some fancy switching one array will charge one battery bank (some charge controllers will charge 2 but they are few and far between). You may divide the array into several smaller array's each charging it's own battery bank.

    Examples;
    A refrigerator will use @1Kwh of electric in a day, 2 - 12v - 55 ah batteries will store 2x55ah x 12 v = 1.320 Kwh not enough storage for sunny days and no reserve for cloudy and you also want to use other items on this circuit?
    1 - 100 ah gel(do they still make gel batteries?) stores just over 1 Kwh of electric at a 20 hour discharge. Doubt it will run a large coffee maker for an hour....

    1 large system tends to run better than many small systems.
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    GEL batteries are not a good choice (in general) for off grid solar power systems... They can take about C/20 or 5% rate of charge. It can take several days to recharge a GEL battery because of the slow rate of charge. High rates of charge (C/10 to C/5+) will damage GEL batteries (there seem to be some European GEL batteries which are rated for higher charging current--But no US batteries that I recall).

    Next--If these three "circuits" are all in the same location--I would design one large array+battery bank to support your loads. Fragmenting into multiple small systems is a huge pain in the behind (3x more parts to maintain/debug/fail--You cannot easily move "excess" energy between systems, etc.).

    And yes, good quality MPPT controllers can support 140 to 150 VDC Vpanel input -- or even higher for some vendor/models.

    To properly recharge your 24 volt battery bank, you need to put two 30 volt Vmp panels in series and use a MPPT controller with a minimum rated Vpanel input of ~100 VDC minimum. A good MPPT controller will limit its output current to its rated value. These typically have a "switch mode/buck converter" in them--Has some very nice properties for use with solar panels and battery banks.

    Even though you want to run your loads during the day--Solar charge controllers are typically "relatively slow" when adjusting charging voltage. Basically, the battery bank is what regulates the system DC voltage between ~11.5 to 15.0 volts (12 volt battery bus). If you supply too much charging current to a small battery bank, it is possible that the solar array will raise the battery voltage >> your 13.2 to 14.4 volt nominal battery voltage--You may fault the AC inverter (most fault around 15 to 16 volts on the DC bus for 12 volt inverters) before the solar charge controller can shut down/back off on the charging current (actual solar charger voltage response is variable on brand/model--I don't have that information).

    For most people/applications, we really want to use significant power at night/during bad weather... So a typical "balanced" system design has a large enough battery bank to manage several days without sun--Which also is a large enough battery bank to not "over voltage" relative to the array size.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    My plans are to build 3 independent circuits but connected to the same solar panel array

    This will not work. You must have one controller per array. You can split your array into three separate arrays, each with its own controller.

    There will be no problem if you want to have three controllers charging the same battery.

    Remember, you must have two solar panels in series (Vmp=60) if you wish to charge a 24 volt battery, and you will lose half your power unless you use an MPPT controller.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • porrascarlos80
    porrascarlos80 Registered Users Posts: 4
    Options
    Thanks everyone for your great feedback.

    to summarize recommendations basically are:

    1 split the solar array in series.
    2 do not use cheap controllers use mppt
    3 increase battery bank size.

    I certainly will do that , but as for now I have to use those batteries until they die.

    What about the trojan 6v 210ah batteries are those the cheapest way to go with high ah rate?
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Options
    to summarize recommendations basically are:

    1 split the solar array in series.
    2 do not use cheap controllers use mppt
    3 increase battery bank size.

    I certainly will do that , but as for now I have to use those batteries until they die.

    If you put your solar panels in strings of two (Vmp=60), you can still use PWM controllers (assuming they can handle the 60 volt input). You will lose half your power, but that is not a problem because your battery is not large enough to handle the power that your panels can make. You will certainly want an MPPT controller when you upgrade your batteries.

    You still seem a bit confused about how all these components fit together... don't spend any more money without getting some specific advice.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    Depending on the size of battery bank, golf cart batteries can be very cost efficient.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • sohel95
    sohel95 Registered Users Posts: 1
    Options
    Yesterday  i was purchased mppt solar inverter highbrid . But when i connect properly display showing output over voltage fault. And red light showing. Not working inverter. Code OVA-   But new inverter.  How to solve  
  • BB.
    BB. Super Moderators, Administrators Posts: 33,447 admin
    Options
    What is the the brand/model of Inverter-Charger?

    What is the DC input voltage--I assume a 24 VDC battery bus--But should be sure that it does not require a 12 volt bus.

    -Bill 
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Options
    How much load do you have on the inverter?

    I am available for custom hardware/firmware development