Oversizing an array with mppt controller
ayurtdweller
Registered Users Posts: 26 ✭✭
Let's say we you have a 40 amp mppt controller rated for 500 watts input at 12v. 1000 at 24v.
What would. The result be if you were to exceed the max watt input while remaining within max voltage input?
What would. The result be if you were to exceed the max watt input while remaining within max voltage input?
Comments
-
Controllers generally can tolerate over paneling, the amount by which is different between manufacturers, the maximum current capacity is usually a fixed value, so the only advantage will be in less than full sunlight. Before considering over paneling check with the manufacturers recommendations, those with string a calculator will let you know if the amount exceeds limitations.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
There are a lot of variables, but as a general proposition you can hook up more wattage, within reason (say 30% more), of pv without problems This can be quite useful in getting some meaningful charging current on lightly overcast days.
Generally speaking, charge controllers won't put out more than rated, so overpanelling within reason is okay. In an extreme situation (like 2-3x overpanelling), it's conceivable that the controller couldn't react fast enough to an edge of cloud sort of situation to limit output, but otherwise the panels simply won't put out more wattage than the controller calls for.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Here's what EPever says about their Tracer MPPT controllers.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
One reason that way too high of input power is hard on MPPT controllers is that when they limit, they usually have to run at a higher input voltage to do the limiting. This makes them (typically) run hotter at that voltage.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed