parbob1
Registered Users Posts: 40 ✭✭
Long story short build a house in the middle of the woods 2001 in the Northeast ...purchased SW 4024 inverter disconnect and battery pack charged by generator
. Sold the house and ended up getting it back in 2017. With every intention of installing solar panels. Inverter went bad so solar panels will be moved to a 2019 project
what I have now 8- 6vt 235 batteries and a 6500 Honda generator and disconnect/breaker.
What I’m shortly going to,purchase
Schneider SW4024 Inverter 120/240V
Schneider Conext System Control Panel
Schneider Conext Auto Start Control
12/24V Battery Vent Fan Control
am I missing anything, or making any mistakes
. Sold the house and ended up getting it back in 2017. With every intention of installing solar panels. Inverter went bad so solar panels will be moved to a 2019 project
what I have now 8- 6vt 235 batteries and a 6500 Honda generator and disconnect/breaker.
What I’m shortly going to,purchase
Schneider SW4024 Inverter 120/240V
Schneider Conext System Control Panel
Schneider Conext Auto Start Control
12/24V Battery Vent Fan Control
am I missing anything, or making any mistakes
SW Conext 4048
AGS
Combox & Conext battery monitor
16- 235 6V batteries
Honda 6500 gen
Combox & Conext battery monitor
16- 235 6V batteries
Honda 6500 gen
Comments
-
Missing loads? Maybe 24v makes sense,, or maybe 48v? 120/240v inverter suggests maybe some bigger loads that might be better at 48v?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
I'd suggest getting the ComBox instead of the SCP - if you are able to connect a router and computer to it. The SCP is lots of manual button pushing and scrolling. The combox lets you use a mouse and PC to do that, and see a bit more, install firmware updates (or brick it if you do it wrong)With 8 batteries, wire in series and use a 48v system, not 24VPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Thank you I did not know Com box could replace scp. Is the com box windows or will apple work?..
and I was mistaken I have 12 6vt 235 batteries.
my old inverter was 24vt and supplied all power needs.
With the new inverter producing 240v I was going to add 1/2 hp water pump
SW Conext 4048AGS
Combox & Conext battery monitor
16- 235 6V batteries
Honda 6500 gen -
If the batteries are fairly new and in decent shape, I'd consider adding to get 2 strings at 48v. Keeps wire/connector sizes more reasonable, and less voltage sag on larger loads.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
So if I go 48v, can use my 250amp dc breaker box and 4/0 cable (10’)?
Batteries are newer.SW Conext 4048AGS
Combox & Conext battery monitor
16- 235 6V batteries
Honda 6500 gen -
4/0 wire should be fine. You'd want to check the inverter spec/manual for max breaker size.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Thank you for your help. I think I’ll go with 48 v and the com box.SW Conext 4048AGS
Combox & Conext battery monitor
16- 235 6V batteries
Honda 6500 gen -
250amp is spec for all of the SWs in the install guide on the Schneider web site.
REC TwinPeak 2 285W 3S-3P 2.6kW-STC / 1.9kW-NMOT Array / MN Solar Classic 150 / 2017 Conext SW 4024 Inverter latest firmware / OB PSX-240 Autotransfomer for load balancing / Trojan L16H-AC 435Ah bank 4S connected to Inverter with 7' of 4/0 cable / 24 volt system / Grid-Assist or Backup Solar Generator System Powering 3200Whs Daily / System went Online Oct 2017 / System, Pics and Discussion -
The combox is a web interface, works with a browser, on my android or my win laptop. Should work fine with a mac too
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 623 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed