Pwm vs mppt amps
mountainman
Registered Users Posts: 439 ✭✭
With 12 volts 400 watts on pwm the most amps I've ever saw was 16 on a 50% soc unless I was running a load then around 20 amps. In the real world on mppt how many charge amps should I see?
2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Comments
-
Trick question?
16 amps...
If you are getting more amps when running a load the batteries are limiting the input.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Might describe your system with battery type and size.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
mountainman said:With 12 volts 400 watts on pwm the most amps I've ever saw was 16 on a 50% soc unless I was running a load then around 20 amps. In the real world on mppt how many charge amps should I see?
https://www.solar-electric.com/learning-center/batteries-and-charging/mppt-solar-charge-controllers.html1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Gc fla 208 ahr2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
I'm in the mountains 3000 feet. With clear skies and 10f what should I gain with mppt ?2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
If the batteries are capable of only absorbing 16 amps that's all you will get. Are they older batteries?
The general idea is that if you have 17.5 volts coming in up to 18.9 volts, that the wattage above the voltage that the batteries are charging at the amperage they are providing will be converted into amperage at the lower voltage. Clear as mud?
So if you are in bulk near absorb or close to absorb voltage say 14.8 volts, at 4 amps and your panels are providing 17.5 volts, you would gain about 1.7 volts x 4 amps or about 7 watts per panel, or 28 watts for the 4 panels. This pretty much only applies in bulk, once you hit absorb the batteries start accepting less current. 28 watts is about 10% of the 300 watts you should expect from your panels.
If they panels can produce 5 amps then a few more watts, but apparently your battery is accepting a maximum of 16 amps. Most MPPT CC work at a very high rate of return around 95%. You would also want to reconfigure your array so that you had strings of 2 panels. Most/All MPPT type controllers need a bit of head space above the charging voltage to operate properly.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Batterys are only 3 or 4 months old. Don't understand the 230 watts 14.4 volts 16 amps peak charging. If I run the furnace and tv while in bulk 308 watts 21.89 amps 14.1 volts. Panels are 5.29a 18.9v. So normally 18.9-14.8=4.1×5.29= 21 more watts per panel2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
If your charge controller says you are getting 21.89 amps from the array when you have a load, but only 16 amps when you are just charging, then it's not a problem of available current/amps. The batteries are only accepting 16 amps....
Do you have a single unit charger/inverter? perhaps it's a mis-understanding of the values?mountainman said:Don't understand the 230 watts 14.4 volts 16 amps peak charging.
Before MPPT type charge controllers, panels were made in voltage ranges to charge batteries. The higher STC VMP is for several reasons, one of the major reasons is the loss of voltage in Normal Operation. I couldn't find a panel in the 100 watt range that had published NOCT values, but here's specs of a Astroenergy panel;
You can see that the voltage drops from a VMP of 35.77 to 32.67 or about 9%, this is at the panel. Note the over all drop of wattage from 305 watt to 213 watts, about 70% of the rated power vs the Normal operating power.
Just want to give you a feel, 21 watts is "sort-of" right, but the loss at the panel has already been taken into account using the PWM controller.
In addition, the times when a MPPT type really make a difference is during bulk charging and over cast days. In normal operation, you may well see zero benefit from MPPT type charge controller. In general systems are designed to discharge only the top 20% during a normal daily cycle. Well the top 20% barely gets you out of bulk. Once a system reach absorb or shortly after the batteries limit the amount of charge they can take in and an array if designed to charge at 13% of the battery capacity will not rely on the 'extra' available since the batteries are already limiting the current.
Hard concept to explain. If you have the capacity an additional panel might be cheaper than a MPPT charge controller, though keeping an even number of panels would be advised as if/when you switch you will want to run strings of panels so you can provide about 30% more voltage than the charging voltage so a MPPT charge controller can work properly.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
mountainman said:Batterys are only 3 or 4 months old. Don't understand the 230 watts 14.4 volts 16 amps peak charging. If I run the furnace and tv while in bulk 308 watts 21.89 amps 14.1 volts. Panels are 5.29a 18.9v. So normally 18.9-14.8=4.1×5.29= 21 more watts per panel
Now let's consider the battery was heavily used one night, the morning battery voltage is 11.5V, the weak morning sun can only bring the voltage up to 12.0V when the prime sun hours begin at 10am (approximately), now is when the current will start to climb, because the battery is accepting all that can be produced, the maximum production would occur when the sun is directly overhead, if the voltage at that time is below 14.4V, then the maximum output would be observed.
What's being seen is the battery nearing full charge, therefore reducing current, adding a load is offering somewhere for the otherwise wasted energy to go. As an experiment disconnect the PV at the end of the day, reconnect the next day at noon, this will demonstrate what's being explained, the battery will take everything available, until the voltage set-point is reached, you need to discharge the battery overnight to some degree of course.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Photowhit said:
Before MPPT type charge controllers, panels were made in voltage ranges to charge batteries. The higher STC VMP is for several reasons, one of the major reasons is the loss of voltage in Normal Operation. I couldn't find a panel in the 100 watt range that had published NOCT values, but here's specs of a Astroenergy panel;
You can see that the voltage drops from a VMP of 35.77 to 32.67 or about 9%, this is at the panel. Note the over all drop of wattage from 305 watt to 213 watts, about 70% of the rated power vs the Normal operating power.
Here's a 120 watt STC rated panel showing a mere 87 watts at NOCT level output.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
What gauge and length wire between the controller and battery? Remote voltage sensing? Too much resistance can limit the battery current, too.
-
With high charging current (good sun, low battery State of Charge, and/or DC loads on battery bus), what is the voltage at the charge controller output terminals and at the other end of the cables at the battery bus connection terminals? Ideally you would want a maximum of 0.05 to 0.10 volt drop for a 12 volt battery bank (2x that for a 24 volt bank, and 4x that for a 48 volt bank).Looking for voltage drop for both wiring and connections (loose, dirty, poor connections can cause problems too).-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
Cc only accepts 8 awg so I used 4 awg and trimmed to fit the cc lugs. On calculator .net 5 ft at 12 volts .052 v drop. No temperature compensation. All connected tight no extremely hot terminal. I think what mcgivor said could be the answer. I get great east and south unobstructed sun. The battery bank slowly fills earlier on. When the sun is at peak the batteries can only apcept 16 amps. Just my opinion I'm still very much tring to learn. I do appreciate all of your help. In cold Mountain air my arrays putting out more amps than stc 21.89 (rated at 21.16) as for the question of mppt amps maybe theres to many variables for an answer short of hooking it up to see. But if any one knows how to do the math what peak amps could be possible with mppt x 4 22.5 voc 18.9 vmp 5.29 imp 5.75 isc temperature Co ef of pmax -.44%/°c in 10f temps? Again thanks very much to all that are helping me understand my curiosity on solar.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Thought this might be of help2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Wrong thread....-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
Bill wasn't this intended for some one else2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
Yes, thank you MountainMan.I am posting to correct thread now.-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
-
Mcgivor. weather app for Virginia says we'll have sun next Wednesday think I'll try your experiment. I'll post results2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion -
If my arithmetic is right (25°C STC to -12°C ambient is 0.0044 x (25+12) = 0.1628, so Vmp of 18.9 + 18.9 x .1628 = 21.98v) about a 3v higher voltage?
In theory, a ~16% potential better output with mppt, but not likely in real world use. Ambient temp may be -12°C, but the panel will be much warmer than ambient in full sun. Using ambient with the temp coefficient is really only useful in sanity checking string config so as not to overvoltage a controller on a cold morning (when panels are near ambient before being warmed by the sun).Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Mcgivor you were right. I Did the test as you instructed unhooked my solar array.yesterday left my tv on all night. Noon today I reconnected it to see 21 amps going into the 60% soc batteries.2kw array 6 345 q cells make sky blue 60 cc
6 230ah GC @36 volts
18 amp accusense charger. 3650 champion
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed