Shared neutral?
                    Estragon
                    Registered Users Posts: 4,503 ✭✭✭✭✭
                    Likely a bad idea, but here goes...
My boat has a 2000w MSW inverter run off a pair of 6v GC batteries. It's only significant AC load is a small microwave used only rarely away from the dock. I'm redoing wiring for it, and was wondering if it would be possible to wire the AC input and outputs with separate live (hot) conductors, but a single neutral conductor and chassis ground? The wire path from the inverter to nav station panel is really tight, and having one less (10ga) conductor would make the run much easier.
            Typically when a shared neutral is used it is with a split phase system or branch circuit such as a kitchen split receptacle, the neutral caries the unbalanced load. Being the inverter is single phase the additional live conductor would be of little benifit as a single 10 gauge circuit would exceed the inverters capacity and distance would not be a factor in the confines of a boat.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
            I'd need to see a drawing.I am available for custom hardware/firmware development
            To clarify, one line conductor would be ACin (shore power when available), the other would be ACout. In thinking more about it, the neutral can't be shared.
 Too many projects on the go, and I was thinking the in and out wouldn't be live at the same time. Of course this isn't true, as the inverter out is passing shore power (from the ACin) through to the ACout, so obviously the neutral can't be shared.Off-grid.
            Sometimes it helps to just draw it. But you do not need to now "we go where power lines don't" Sierra Nevada mountain area "we go where power lines don't" Sierra Nevada mountain area
            Boat wiring for AC can get very complicated (between shore/genset/inverter power, ground fault protection, isolation, etc.).
 But--Be very careful here. Most MSW (modified square wave) AC inverters do not have an Isolated AC output. There is not "neutral" for MSW inverters--The AC outputs are both "hot" with respect to the DC battery bus.
 If you make an AC "Neutral" and tie it to boat/safety/chassis ground. And have your (typical) DC negative battery connection connected to the same green wire/safety/chassis ground, you will effectively short out your MSW inverter and fry it.
 Most Sine Wave (pure/true PSW/TSW) AC inverters use an isolation transformer and you can can make a grounded neutral AC output.
 Notice I say "most"... You need to check the manuals to see if your inverter is "most" inverters or not. Most MSW inverters will say nothing about grounding the AC output/creating a neutral.
 Many TSW/PSW inverters over ~2,000 or 3,000 Watt output actually have a true grounded bonded neutral internal to the inverter (similar for AC gensets too).
 This can create issues... Multiple Neutral Neutral Ground bonds (at shore power, AC genset, AC inverter) is not a good thing either (in most cases)....
            Definitely grounding on boats can cause electrolysis! But, this is a working system right Estragon? You are simply moving wires around?
 No history with zincs cooking off too fast?"we go where power lines don't" Sierra Nevada mountain area
 Yup, shoulda drawn it... I more or less did a mental one when I got a chance to go for a walk and clear the deck a bit, which is when it dawned on me it couldn't work.
 It is a working system, but the admiral wanted the inverter going pronto (to run the nuke on the hook to foam milk for coffee, which it turns out the NG stove does better anyway), so I used parts available at the time from the local orange box etc. That was c.2009 or 2010. I know it isn't done right though, so hoping to get at it this year.
 No problems with galvanic corrosion, but it's a freshwater boat. We probably get away with a lot more than we should.
 I'm also redoing some of the DC side, but will start a new thread on some questions with that.Off-grid.
            Bill - It's been a while since I've had the panel apart, so I'm guessing a bit. IIRC, there's nowhere the DC negative is bonded to AC neutral. The inverter transfer switch makes an AC NG bond when inverting, and lifts it when ACin is live from shore power or whatever, but I think the AC ground is separated from DC negative. Will need to check that though.Off-grid.
- 232 Forum & Website