Morningstar ts 60 mppt charge controller problems ?
Gator
Gator Registered Users Posts: 29 ✭✭
I shut everything down, panels, inverter and controller/battery disconnect in order to re route solar connectors on roof of my trailer.
I FINISHED THE JOB and came inside to turn everything back on.
Thats when everything went south...
I turned on the controller battery switch and waited till it came to screen that said night and the red/YELLOW led was on.
After a couple of minutes I turned the solar panels on.
Thats when the controller started alternating yellow/ red then green/ red  continuous and then after showing fault/absorb back and forth a few times it would say starting and amps showed different amounts dropping down to 0 amps and alternating absorb/fault, all the while.
I re booted the controller a few times from scratch with the same result.
1 time i turned on the inverter and it made a little poping noise and controller screen went blank.
Seems, i think that there is a short somewhere?
I'm really deoressed cuz i dont kno wat i did to cause any of this or how to fix it..
HELP ME PLEASE IF SOMEONE CAN?
AS I SAID ...MORNINGSTAR TS 60 MPPT CHARGE CONTROLLER (150 WATTS)...., SAMLEX 2000 WATT 24 VOLT INVERTER,....(3) PANASONIC H.I.T. 330 WATT. PANELS
TOTALLY OFF GRID!
.HELP...HELP
    You didn't happen to switch polarity?
  • littleharbor2
    littleharbor2 Solar Expert Posts: 2,137 ✭✭✭✭✭
    Hopefully you haven't series wired those high voltage panels. 3 in series have a Voc. of 209 volts. Magic smoke time.
  • Gator
    Not Series....all pos 3 into 1...all neg 3 into 1
  • Gator
    I couldnt switch polarity cuz mc4 neg and pos are different connectors, and i connected same as i took apart
  • Gator
    Thinkin....gotta chk inverter hardwire to ac panel...connection mighta come loose and is shorting possibly?
  • Gator
    But why now? B4 was working with no problems?
  • Estragon
    Do you have mc4 connectors at the controller? At the combiner?
  • Estragon
    Flip the Dc breaker to turn the inverter off until you're sure the DC side is righteous.
  • Estragon
    What is the actual battery voltage?
  • Gator
    Got inverter disconnect off....have (4) UPS batts. With 80 amh series / parallel .....batt voltage says 29.5?
  • Gator
    Chk'd each batt with meter varied bit round 13.5,but 1 was 10.3...obviously not balanced... but day b4 watched tv with no apparent issues
  • Gator
    2 begin with im way outta my pay grade with all this solar stuff....lol
  • Estragon
    With the pv input breaker OFF, what is the voltage at the controller battery terminals?
  • Gator
    With pv  input breaker off and batt. 2 controller breaker off..10.8 volts at batt. out-terminals
    So on controller info screen the 29.5 was feed from pv?
  • Estragon
    You want to read voltage at the battery terminals in the controller (battery + and common negative) with the pv input breaker open (off) and the battery breaker closed (on).
    To simplify things, you may want to disconnect the battery string with the 10.3v reading for now.
  • Gator
    If i dis connect the 1 batt. That reads 10.3 volts, then i wont b series/parallel for 24 volts anymore...correct?
    There are 4, 12 volt ups batteries all 2gether, wired series/parallel...if i disconnect 1 then i'd have 18 volts?
    How does that work?
  • mcgivor
    R-Y-G led sequencing would either be a  DIP switch fault or a self-test fault. You mentioned controller screen so assumption would be you havea remote meter, if this is the case have you gone into the diagnosis  menu?
  • Estragon
    edited May 2018 #19
    You have 2 strings of batteries. 2x 12v = 24v. One of those strings has a battery with a voltage of 10.3v. I'd take that string out to simplify troubleshooting. The parallel connection will be + to + and - to -. Lift a +to + connection and you break the parallel connection. Having taken the bad string out, you should be left with a + and - connection from the controller to the (24v) pair of good batteries.
    BTW, open the breaker to the controller when moving battery wires. Less sparky that way.
  • mcgivor
    Here is a list of fault codes, attached pdf
    What size, type, etc. Batteries are you using?
    10.3 volts is a dead 12 volt lead acid battery. And the longer it sits dead, the more likely it will never recover (it may already too late anyway).
    Normally, I would suggest you get all batteries quickly and fully charged before any of the rest go bad.
    It is possible that this battery has a shorted cell. Use a hydrometer to check the sg of each cell.
    Bill