Solar PV system DC fuse keeps blowing

Hi!


I have a 6.5Kw system installed with a SMA Sunnyboy inverter. Works great normally. One DC fuse blew 2 years ago and I replaced. However, it blew again repeatedly every 6 months. There are four DC fuses and this particular one keeps blowing. Any idea why this is happening?


I am not a Pro.

Comments

  • PhotowhitPhotowhit Solar Expert Posts: 4,769 ✭✭✭✭
    So, I'm guessing these are fuses for the incoming solar panels, perhaps someone with a dc clamp meter could check to see if the current coming in from each string is even...

    Perhaps they wired your panels incorrectly. Do you have panels in a multiple of 4? maybe 28 panels which would be strings of 7 panels...
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Prosine 1800 and Exeltech 1100, 660 ah 24v ForkLift battery. Off grid for @16 of last 17 years. Assorted other systems, and to many panels in the closet to not do more...lol
  • PhotowhitPhotowhit Solar Expert Posts: 4,769 ✭✭✭✭
    Alternately, you might shut everything down and read the voltage coming in on each fused string one at a time. Or at least do the one that keeps blowing and another to get a comparison. The fuses are rated for amps, which shouldn't change regardless of how many panels are in a string. but they could be past the max voltage with additional panels.

    What mightbe happening is a bad connection internally, if the string is plugged into the inverter near the fuse and the connection is a bit loose or other connections are loose, the added heat will run along the line and may trip burn the fuse.
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Prosine 1800 and Exeltech 1100, 660 ah 24v ForkLift battery. Off grid for @16 of last 17 years. Assorted other systems, and to many panels in the closet to not do more...lol
  • BB.BB. Super Moderators, Administrators Posts: 28,186 admin
    What size or amp rating of fuse?

    Around 1 amp is s ground fault detection fuse.

    Most arrays, if you have any fuses, are around 15 amps or so.

    Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset