Can't find whats going on

My morningstar ts mppt 60 amp charge controller has flashing green light (or occasional solid green light) when charging.
On the graph meter it shows full ("V") graph bar...
But for the amp ("A") sometimes very few bars, but mostly just flashes "A" then the word "Alarm", back and forth.
What does this mean?
Have (3) Panasonic H.I.T. 330 watt panels hooked up in parallel.
(4) USP 80 Amh Batteries (series/parallel)
Samlex 2000 watt dc/ac Inverter (24) volt
Probably everything is wrong here?
On the graph meter it shows full ("V") graph bar...
But for the amp ("A") sometimes very few bars, but mostly just flashes "A" then the word "Alarm", back and forth.
What does this mean?
Have (3) Panasonic H.I.T. 330 watt panels hooked up in parallel.
(4) USP 80 Amh Batteries (series/parallel)
Samlex 2000 watt dc/ac Inverter (24) volt
Probably everything is wrong here?
Comments
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Sounds really small for that much panel, wonder if that could cause an issue?
Just a thought.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
The 3 Led's are an indication of battery voltage, primarily during charging, the transition from red, yellow/red, yellow, yellow/green and green are dependent on voltage during charging. The green when solid indicates a voltage close to the absorption, when the green flashes at1/2 second intervals it is in the absorption stage, during which the current will continue to drop, as indicated on the bar graph ( I'm assuming reference to the meter) until fully charged. When there is a transition to float, the voltage will drop along with the green Led flashing at one second intervals. If there are no loads the current will be low, as soon as a load is applied, the status of the green Led may change back to solid green or lower, yellow/green etcetera, depending on the load, then once the load is absent the transition to solid green or flashing green will occur, as long as there is sufficient PV and time available. Once there is insufficient PV input, the Led's will change depending on the voltage as a guide to the state of charge. The Led indication are akin to idiot lights on a car, they provide very limited information, though once understood they are useful for a quick glance. As far as the alarm is concerned, go to the diagnostics menu to see the code, or better still connect to a PC with MS View software to access all parameters.
Your battery capacity is extremely low in relation to the inverter capacity, if high loads are used there could be excessive voltage sag which could be problematic.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.