Using existing thermostat for diversion water heating

northernsun
northernsun Registered Users Posts: 6 ✭✭
I'll be installing a 20 gallon hot water tank in my off grid cottage this summer. My plan is to replace the existing element with a 900w 24v dc element connected to the DC side via a SSR. Pretty standard setup so far. My plan is to run the aux 1 output from the Midnite classic through the stock AC thermostat on the hot water tank in series with the SSR. My thinking is that since its just 12v at very low amps coming out of the aux there should be little to no chance of arcing or pitting. Has anyone done this or can anyone see a problem with this setup?

Thanks in advance,

6x Hanwha Solar G4 305watts
Midnight Solar Classic 150 w/ wizbang jr
4x 6v crowm 395 ah
Xantrex SW4024
location - Lanaudiere, Quebec, Canada

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    You may need some snubber circuit, to absorb any inductive kick from the cables.
     is Aux 1 a voltage source, or dry relay contacts ?  if dry relay contacts, you need a 12VDC source too, to trigger the SSR
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • BB.
    BB. Super Moderators, Administrators Posts: 33,615 admin
    SSR's generally need a good sized heat sink (they can get hot and fail).

    You need a thermal/pressure relief valve (normal for most water heaters--If the thermostat or SSR fails, you don't want the tank to over heat/over pressure).

    A tempering valve is generally used to take the extra hot (scalding) water and mix it with cold water for safe temperature at the sink.

    https://www.homedepot.com/p/Honeywell-Thermostatic-Mixing-Valve-AM101C-US-1/202264710

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • jonr
    jonr Solar Expert Posts: 1,386 ✭✭✭✭
    Since you are using much lower voltage (240V->12V)  and much much lower current (whatever the SSR input draws), using these AC rated contacts for DC should be fine.  

    I am available for custom hardware/firmware development

  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Don't know if you have been there , but the Midnite Forum has had a lot of recent discussion about using Aux 1 and 2 for DHW heating    http://midniteftp.com/forum/index.php?action=unread

     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada