Welcome to the forum,
The first step in designing a system is to know the purpose of the system. The purpose of the system is to power your loads. So, what are your loads? You need to know the peak load (watts) and the daily energy usage (kilowatthours).
We have all sorts of formulas to calculate battery size, size of array, etc... but these formulas use numbers. In order to help you, we need to know your energy usage numbers. Similarly, if you asked us what pickup truck to buy for your trailer, we couldn't answer without knowing the weight of the trailer.
Some of your loads may be problematic if you only have 800 watts of array... electric heater, coffee pot, microwave. What about refrigeration? Air conditioning? water pumping? Do you have a generator? Do you have the capacity to carry a thousand pounds of battery?
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
use propane for the coffee, that is a huge electric drain. A microwave for 30 seconds is a manageable load. Heating functions that can convert to propane, have to be done before thinking of solar. An electric room heater is completely out.
There are several solar design stickies of how to calculate your loads, how to size the batteries for them, and finally calculating the size of the PV array to recharge.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Danny, you can waste a whole lot of precious time/energy/money by not following vtmaps simple, but dead accurate first paragraph.
Get a handle on your loads. Figure out what you will run, what the power draw is and how long each one needs to run. Until you do that, you are sort of just peeing into the wind
Once you have a list of your "wants" you can get GREAT input from the experienced folks here, on how to balance what you want and what fits your budget - whatever it is.
Investing the time at this phase is a critical step to success!
Marc
I always have more questions than answers. That's the nature of life. -
All the above are good points; one not mentioned is how often do you dry camp? a couple of times a year for a week at a time and solar won't pay for itself.
-
Unless you have a huge solar array, it is almost always a bad idea to heat water/cook or rooms with solar.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Vtmaps' and others' suggestions are correct - know your loads. However, 800W of panels on an RV roof probably won't generate as much power overall as the same amount of panels on a house roof, because RVs often are not oriented ideally to the sun or are partially shaded. For this reason alone, I suggest carpeting your roof with as many panels as will fit! PV is still cheap, so a few more panels aren't much more in the context of what the RV will cost you anyway. Just don't put panels next to roof-mounted A/Cs or stink pipes or fridge vents or whatever sticks up above the roof - even the slightest partial shading such as from RV roof impedimenta will drastically reduce their output. If you can mount your panels on tiltable mounts they will produce slightly more power in the summer but probably appreciably more power in the winter when the sun is lower. 1000W of panels is about the most that a charge controller can handle for a 12V system (which your RV is). If you can charge your batteries at a 10 to 13% charge rate they will charge quickly, maybe allowing you to also power opportunity loads in the afternoon after they're fully charged, such as power tools or a washing machine or other non-time-sensitive but power-hungry loads.
Have fun!
John
40' Crown bus with 2kW of tiltable panels on the roof:
Eight Sharp 255W, two Morningstar TS-MPPT-60, Magnum MS2000, Champion C46540 generator converted to propane, eight golfcart batteries, and maybe a small Exeltech inverter for the fridger.
Southern California
-
I believe that poly panels perform better when partial shade is an issue.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
No--I do not believe there is any advantage of mono or poly crystalline panels when there is shading. They both operate with pretty much the same physics (I could be wrong--But I do not see any reason for a "difference" during partial shading).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
You are probably right about that. When I was comparing the two technologies, one web site made that claim. Not "scientific proof" by any means. Though "scientific proof" is getting "more affordable" every year. A jab at the current crop of "scientists".
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Some have claimed that Mono panels do better in overcast skies vs poly crystalline--I have no opinion on that (other than it probably does not make enough difference to spend more on Mono panels because of this).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
4 x 110 amp batteries with 800 watt panels seems like a ratio to use if your in sunlight most of the time.
I live up in the Northwest and that panel wattage to batteries amps wouldn't work out very well as often you can go days without sunlight, possibly a week to a couple of weeks, then several days with sunlight. Depends on you location and altitude, weather in the mountains is usually not the same as weather along to coast, low lying areas, etc. There are areas that average over 150 inches of annual precipitation, 20 miles or so away only around 20 inches of annual precipitation.
For up here in the Northwest I would want more battery storage as I never know how much sunlight will be available.
However the previous comments are correct. You also need to figure the demand or common daily loads. Do you require AC, TV, Computer, Microwave, etc.?
When off-grid a stock RV won't operate without a certain amount of 12 volts power to run a Fan for RV furnace (which often are 7+ amps, check the amp rating of your RV furnace) and 12 volts to run the RV gas absorption refrigerator. (12 volts is normally required for a RV gas frig to operate) Plus a few other items such as the water pump, bathroom and stove fan.
What I did with my RV was to install an additional Catalytic Heater in the RV that requires no elect. to operate. It's best to get a catalytic heater built for an RV such as Olympian or a heater that designed for a permanent installation. One that puts out a constant heat where the btu ratings may not be as high as portable camping heater, etc. These are much more reliable and maintain room temperatures throughout the day and evening.
When the batteries become drained it often requires from a half to a full day to recharge (sometimes a bit longer, depending on the size of your battery bank). If no sun a geny is usually relied upon. Also it's not a good idea to run batteries below 50 percent then recharge again, potentially shortens the life of the batteries. As a general rule you want to try to keep the batteries maintained and charged somewhere above 50 percent of their capacity. At least this is what I have read about charging battery banks, perhaps others have other ideas about keeping batteries charged.
-
I'm in the same boat as OP Danny Coffin. I'm buying all my solar gear, directly from manufacturers in China. China owns the world solar market can/t beat 'em, buy from 'em. Some vendors will do business with individuals. Others, ehh, not so much. Watch out for shipping costs. Unlike American companies, they will haggle like crazy. One way I have dealt with them and been successful is offering to buy from them, pay their price without haggling, for a shipping consideration (sometimes even free). I figure the worst they'll do is say no, and honestly it's been a glimpse into a VERY different culture. That alone has been worth the time invested. No money has changed hands, yet, but I can get two (count 'em) 12v 200AH batteries for a grand. I'm so looking forward to the adventure.
-
Hi all, I’m new here gathering materials for an install on our RV. So far 6 Suniva 275w 60 cell panels, my calcs so far lead me to thinking I need 2 MPPT morning star TriStar 60s . My thoughts are to run 3 panels in series on each charge controller . My system is 12v starting out I’m planning on 6 225ah deep cycle golf cart batteries. 2 batteries in series 3 sets tied in parrellell for 12 v. Also I have yet to size my inverter charger ,based on my charging needs on shore power. Anybody have any suggestions or thoughts on my setup. Opinions welcome this is my second setup so far first one was for remote gate opener on1 panel and battery. It worked great but this conserderably more costly, so I don’t want to make any big mistakes. I want to recover the maximum of output from my panels I’m making dual tilts for the mounts.Thanks in advance for any advice,
Jim -
You mentioned "system is 12v starting out" - does this suggest you may consider going to a higher voltage system in future?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Sorry I mis spoke 12vdc always, I left out a comma. Starting out with 6 batteries.
-
I'd suggest sizing the inverter based on AC loads, not shore power charging capacity. Depending on loads, you may want to consider a standalone charger or chargers.
Basing the inverter on charger capability may lead to choosing a much larger inverter than required (eg 2500w), which means higher self-consumption just to have the big inverter supplying small loads. A big inverter can use 30-50w on top of the small load, which could be (eg) 40w x 24hrs = 960wh/day. The bank will be 675ah@12v= about 8kwh. You don't want to run in down more than about halfway, and a 2500w inverter can get there pretty fast.
Using 3 strings of batteries in parallel isn't ideal. You'll want heavy, short interconnect wire, quality connections, and a fuse on each string. A clamp-on current meter would be helpful to ensure balanced charging.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Ok that’s good advice, the lager than normal charging capacity was more for when we are on shore power. But your point is taken. I have T&B crimping tools for up to 250MCM so good connections are no problem. I have 400 amp welding cable for interconnects on bank.
-
Ok sounds like good idea ,and sound advice thanks for your thoughts. Your suggesting larger Ah batteries and fewer as more optimal solution?
Jim -
Yes. Ideally whatever AH capacity required in a single series string. This can be done using large lower voltage batteries as needed (eg 6x700ah 2v cells), or by increasing system voltage (which is why I asked about possibly wanting to increase it later).
Two strings (eg. 4x350ah 6v L16 type batteries) can work if monitored carefully. I use this setup for my 700ah 12v bank, and it has worked well. As the number of strings increases, so does the difficulty in keeping strings balanced. Three may work okay with your good connections, and regular monitoring and maintenance. If one string is reading low during regular specific gravity checks, it should be charged separately to get it to the level of the other strings. 6v GC type batteries are nice in that they're widely available and generally pretty cheap for their capacity, so it may make sense to use them anyway. It's just a bit of a trade-off in terms of a bit more careful monitoring and possibly periodic remediation with the three strings. With more than two strings, you should also fuse each string as well as breakers on the controllers and inverter, because a short in one can put the current available from the remaining strings across the short in the bad one.
Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
JimDiesel, Just a thought, but it seems to me you could save some money and hassle by using two less expensive 40a mppt controllers into four 6v batteries wired in series at 24v, a 24v inverter, and then a 24v to 12v converter for any 12v loads. Your controllers get cheaper, batteries less complicated and failure-prone, and less wiring losses and the more efficient inverter should offset conversion losses for 12v loads. Don't rule out 24v just because you have some 12v loads...
-
softdown said:I believe that poly panels perform better when partial shade is an issue.
I agree with those who say run your AC appliances in the peak generating hours of the day. I also agree, using propane for coffee. That Coleman stove-top drip coffeemaker is pretty cool, just be sure you have a spare carafe in a soft, safe place, or an alternative you can use until your new carafe arrives. But I'd also say, you can run your AC more if you're using lithium-iron batteries (LiFePo4) because you can draw them down 80 percent, as opposed to lead-acid's 50 percent usable power.
-
RE: LiFePO4 batteries... unless you want to obsess about the batteries being "100% FULL" that is the zone between 80% and 99.9999%, use 60% available power as the safe bottom is 20%, the safe top is 80%
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed