Use of Xantrex Freedom sw3000 in residential Solar application?
In 2010, I purchased a Xantrex freedom Sw3000 and a Sw SCP to be used on a marine application.
The project failled and the units has never been used. Now I am embarking on a home
Solar project. Does anyone knows if the Freedom sw3000 and the SCP can be used in residential Solar installation?
Also, I recently accquired a XW mppt 60-150. Is there any firmware upgrade which will allows the 3 units
to interface?
Re: Use of Xantrex Freedom sw3000 in residential Solar application?
Well maybe...
It has UL certification for marine use(UL458 ), and doesn't has a shroud(?) so that you can't put the battery cables in conduit, required to meet current code. So if you have to have your system inspected, no or ask the inspector if they are OK with it. It's not uncommon for even UL 1741 to be installed with exposed wires in my experience, I'm not sure when the code changed. I have a Prosine 1800 watt inverter that clearly has UL 1741 on the back but has no provision for battery cables run in conduit.
I asked the engineers over at the Midnite forum and they say that has always been the requirements for inverters. For the record you have to buy the conduit parts seperatly for the Magnum and Outback inverters either from them or as part of an installation package from them or some E-Panels designed for particular brand of inverters.
It's a large inverter on a 12 volt system, so you'll need large wires/cables and short DC wire runs, to run it properly. 3000 watts on 12 volts 3000/12=250 amps so your looking at 4/0 cable for short wire runs, and this doesn't take into account 6000watt surge.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
One issue your going to have is with the Neutral - Ground bond. When it transfers to Invert it will make the bond automatically, so you will not need to have the sub-panel grounded with a bond screw. That means you'll have to put in a ground rod on the chassis ground of the Inverter.
I am not sure the sw3000 will allow the SCP to communicate with another device, once it identifies the Inverter the menu is pretty limited. it might , guess you'll have to plug it in. If you can control it from the SCP, I wouldn't think they would have to talk, they would be two separate items, with their own menus. -
What should be the best cables/wires size should I consider to safely handle the 250A nominal curent as well as the 500A surge? -
Re: Use of Xantrex Freedom sw3000 in residential Solar application?What should be the best cables/wires size should I consider to safely handle the 250A nominal curent as well as the 500A surge?
NEED Help Designing my Installation
I am in the process of putting together a 12V solar installation in the Caribbeean.
My daily energy usage is about 6.5 Ah. I have about 51/2 to 6hrs of Sun daily.
Here are my gears:
1 Freedom SW3000w 12v inverter charger
1 AGS box
1 SCP Box
10 100 ah AGM trojan batteries,
1 MidniteSun 150 charge controller
8 345w Seraphin solar panels
1 MidniteSun Combiner box (6 strings)
The panels will be installed at about 30ft from the combiner which will be at about
15ft from the Charge Controller.
Charge Controller will be about 10ft from the battery bank and 8ft from the inverter.
I already have about 120ft of awg #8 of pv cable, and 16ft of awg #4/0 batterycable
Can you guys guide me in putting all this stuffs together for the best possible performance.
Any help will be appreciated.
I would humbly suggest that you first focus on your loads and electrical needs. Trying to shoehorn in existing hardware is not always a good solution--Ideally, you want to match the system to your power needs--And before that, look into heavy conservation efforts for yoru loads as solar power is many times more expensive than utility power (i.e., if you had to pay $1-$2 per kWH vs $0.10 to $0.20 per kWH for typical utility power--Would you do something "different" with your loads...).
Inverters tend to be the cheaper components in an off grid power system. I understand your desires, just don't get them wrapped around the off grid axle.
When you say 6.5ah daily consumption, what voltage is that at? What kind of loads (any high amp / surge draw stuff like pumps)? Are some loads 12vdc? That inverter will use a fair bit of power just being on.
With 8 panels, 4 strings of two panels makes sense. Distance is reasonable, so no big need for higher voltage strings.
At 12v though, a single classic won't work. Even accounting for warm panels, you're at around 170a output, which would require a second classic.
It may be a good idea to take a step back and look carefully at loads to see if it makes more sense to rethink the inverter, or to add a second classic.
I assume the batteries are 12v? If so, that would be a bank of 10 in parallel. Especially with AGMs, it may be difficult to avoid balance issues. Going to a higher system voltage may be worth considering.Off-grid.
From what I read you seem to want a DC power supply for 6.5 Ah and an unspecified AC load(s).
You did not tell us if the loads are during daylight hours only or during the dark period?
10 batteries in PARALLEL is not a recommended arrangement in any voltage...
Based on the AC loads you have, 24 volt may be a better choice.
Thank you guys for the quick reply.
The AGM batteries are 12volt. The 6.5ah is at 110 volt, it assumes I have all my loads on at the same time.The daily loads consist of: DPl projector 3.7A, water pump 5.4A, 24000btu air conditioner 12.20A, 32inch Tv 1.15A, water filter 0.4A, Hunter fan 0.75A, Casablanca fan 1.00A, ceiling lights 0.85A, Freezer 2.5A, 7.5cubic fridge2A.
Estragon, can you elaborate more on difficulties of balancing the battery bank.
Tks
Like Bill said, it all comes down to loads. Assuming the 10 batteries are 12v, OP could wire them as 2 parallel 48v strings, with 2 left over in parallel to support 12vdc loads (if any) and/or run a smaller inverter for lights overnight or whatever. Could do 24v, but that's still 5 parallel strings to keep balanced (and needing a fuse for each string).Off-grid.
OK with that list, please estimate the amount of time each item will be running, It is MUCH more than 6.5Ahr per day.
Correction:
I meant to say my daily use is about 6.5kw instead of 6.5AH
To clarify, 6.5 is amps (a), not amp-hours (ah). Ah is a measure of current over a period of time (generally 1 day). Amps is a measure of current flow at a given instant. Both are important in designing a system, but shouldn't be confused with each other.
The amp ratings you've given may be running amps. Some of the loads may have significantly higher starting currents, so it would help if you could establish if some have locked rotor amp ratings. Also, as @westbranch notes, you need to estimate how long each load will be needed each day. With this, you can estimate ah (a times hours used).
The balance problem arises when parallel banks of batteries have varying resistance (either within the batteries, or in interconnects). Some batteries get fully charged before others, so the less fully charged ones tend to sulfate faster, which makes them harder to charge, and so on. If caught early, the weaker batteries can be charged apart from the stronger ones periodically in an attempt to bring them into better balance, but this takes constant vigilance to do. With AGMs, it can be harder to catch early, because there are no regular specific gravity readings to alert you to a weakening battery. Proper wiring can reduce, but not completely avoid the issue.
If not caught early, the sulfate hardens and the weaker cells are permanently damaged. At some point, the better batteries could end up being overcharged, vent gas, and also be permanently damaged.
The problem increases with the number of parallel connections. The rule of thumb here is 2 is okay, 3 is marginal, and more than 3 is very likely to be problematic.Off-grid.
We still need to understand how you need the power over the 24 hr period, ie how much of the load is during the Sun UP period and how much at night...
ie during the daylight hrs the loads would be carried by the panels once the batteries are charged.... and also to estimate the amount of draw down on the batteries overnight.
The air conditionner will be used 1 or 2 hours during day time when the batteries are fully charge and
same duration at night. The ceiling lights will be used mostly at night. the freezer and fridge will be on 24hr. Water pump will be used mostly during the day when the water pressure tank is below 32 gallons.
The projector will be in use for about 2 hrs a day and the32 inch tv will generaly use at night 3 or 4 hres.
If my night consumption warrant it, I can set up a night system using 2 from the 10 batteries. I already have a spare 12volt 400w pure sine inverter and a 20a mppt charge controller. I will just have to purchase a 12v battery charger, thus avoiding the snagg of charging all 10 batteries with the sw3000 inverter. Is that a vailable a solution?
Good idea about the 12V loads. Now that you have identified the 3 heavy loads , Fridge, Freezer and A/C, you need to determine how to power all 3 loads at one time. Note all 3 will have a SURGE when they start and your battery config may not be able to handle it... the surge can run as high as 10 times but if they are inverter type motors it should be lower.... you may have to contact the manufacturer for that info...
When you set up your inverter you should have your battery cables professionally made. Crimping lugs onto 4/0 cable needs to be done correctly, with the proper tools.
i am considering upgrading my solar system from 12v to 24v. I am looking at magnum pure sine wave inverter/charger Ms4024 PAE to replace my xantrex freedom sw 3000w, I just purchased 6x 420w solar panels with the intend of adding 3 more of the same soon, Those panels are Qcells Q.PEAK DUO L-G6.2-420 (420 Watt Mono G6). Voc 48.84v, vmp 40.89v, isc 10.79A, and Imp 10A. I will need a second charge controller to parallel with my current midnite solar clasic 150. I have been looking at the Epever 80A mppt. Does anyone knows if these 2 charge controller can be paralled. I will be running 10x 12v Agm batteries combined for 24v. Are there any other obstacle I should consider. Any advise will be appreciated. tks
If you have an insured home, you should ask your building department. In a fire or loss, the insurance can make a valid point that this installation was not inspected and deny the claim. If it is inspected, then you will learn the requirements by asking the building department what they require."we go where power lines don't" Sierra Nevada mountain area
Any reason to not go all the way to 48 volts? I am not a fan of 5 parallel strings (2s x 5p) 12 volt batteries...
Also, at the higher battery voltage, you do not need as many solar charge controllers either (i.e., a charge controller can output ~80 amps at 12/24/48 volts--i.e., 4x larger array with one controller at 48 volts vs 12 volts--Power=Voltage*Current).
I understand that you (presently?) have some DC loads--And finding 24 VDC version of pumps/leds/etc. is easier than finding 48 volt versions... But at this size of system, running everything from 120 (or 120/240 VAC) is probably the next step anyway.
And longer term... Looking at large AH batteries (in 6/4/2 volts) would be better (my humble suggestion) to keep to one single string of batteries, or no more than 2 or 3 parallel strings (if you have issues finding 2 volt XXX AH cells).
jbdpark said:. I will be running 10x 12v Agm batteries combined for 24v. Are there any other obstacle I should consider. Any advise will be appreciated. tks
Batteries come in many voltages and ah ratings to size properly without paralleling issues
- 616 Discussion Forums/Café