Which setup would work better ?
arh
Registered Users Posts: 5 ✭✭
327 watt panel 54v 6amp with mppt charger or 2 155w 17v 9.1amp with pwm charger. Charging 4 6v batteries in my RV.
Comments
-
Either will work fine. If you will be camping in hot weather (deserts), the MPPT+54v panel will work better... Panels when they get hot have Vmp fall. The "17 volt" Vmp charging a 12 volt battery bank can be a bit of an issue. In very hot weather, the Vmp of the panel could fall below ~14 volts while the batteries (assuming flooded cell) need closer to 14.7 volts or so for charging. Not a deal killer, but if you are trying to get the most out of the panels in hot desert sun--It could limit your charging/equalization current.
Both panels are are a bit small... For a 5% rate of charge, you would need a bout 377 Watts of solar. And if you are full time off grid (muiltipe weeks of dry camping without genset charging), it would be nice to have ~10% minimum rate of charge. For weekend camping, 5% rate of charge can work OK.- 14.5 volts charging * 2 strings of batteries * 200 amp (Golf cart) batteries) * 1/0.77 panel+controller derating * 0.05 rate of charge = 377 Watts minimum
- 14.5 volts charging * 2 strings of batteries * 200 amp (Golf cart)
batteries) * 1/0.77 panel+controller derating * 0.10 rate of charge = 753 Watts nominal
- 14.5 volts charging * 2 strings of batteries * 200 amp (Golf cart)
batteries) * 1/0.77 panel+controller derating * 0.13 rate of charge = 979 Watt "cost effective" maximum
Otherwise, what fits best and is most cost effective for your needs. Any of the three setups are very typical configurations.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset - 14.5 volts charging * 2 strings of batteries * 200 amp (Golf cart) batteries) * 1/0.77 panel+controller derating * 0.05 rate of charge = 377 Watts minimum
-
I already have 1 of the 155w panels, can I combine it with a 1 of the high voltage 280 to 300watt panels with an mppt controller?
-
arh said:I already have 1 of the 155w panels, can I combine it with a 1 of the high voltage 280 to 300watt panels with an mppt controller?
*If you did, you would lose 100% of the extra power from the larger panel, making it not at all the way to go.
DoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
Thank you
-
So I have decided to go with an epever 4210a, 40amp mppt charger. I found 140 watt panels that based on there dimensions I can fit 3 panels on my rv. Panel specs are VOC 42.8, VMP 33 , 4.7 amp. . What would be the best way to wire them to get the most charging power for my 4, 6v batteries wired for a 12v system. I am very mechanically inclined but don't know much about solar. A simple diagram on how to wire them would be much appreciated.
Thanks,
Adam -
Since you are planning on using a 12V nominal system, you cannot wire 3 panels together. At least you can't without buying what is called a combiner box. The combiner box will allow you to run the outputs from all 3 panels into the box, then only run a single set of larger diameter wires (one positive, one negative) out of the box, to your charge controller. You'll want to use 12 gauge wires into the box, one positive and one negative per panel, then use an 8 gauge pair out of the box, into your charge controller, right above your batteries. This is the box you'll want to use:
https://www.solar-electric.com/mnpv3.html I would highly recommend also buying three of these DC breakers in the 12A or 15A* version, as well:
https://www.solar-electric.com/mnepv.html
edited the breaker sizes above, after the lady reminded me that they are supposed to be somewhat oversized
*12A if you live in the south, where it doesn't get very cold, or 15A if you live very far above the Mason Dixon line, or live on a mountain, places where it gets considerably colder
DoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
This video may help illuminate what myocardia has described,
https://www.youtube.com/watch?v=iOqY6QqFopA
4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Other than illustrating some bad practice, such as placing multiple stranded conductors under a single terminal, reference to the SPD, along with the fact two strings of equal capacity don't need a combiner, the video demstrates the importance of using hair spray to keep the head moving without the hair.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I ordered the charge controller today but have not bought panels yet. If i wanted to use my existing 155w panel, how close in watts, volts and amps do the rest of the panels have to be?
-
MPPT chargers check every few seconds for which voltage is going to provide the most amperage. Since the technology behind "12V" solar panels hasn't changed in a very long time, besides their efficiency, you only need to find a panel or two that have absolutely as close as possible to the same VMP as your current panel, and is/are rated for 150, 155, or 160 watts. Note that spending more money on higher wattage panels will do you no good. You will only get the wattage of your lowest producing panel, multiplied by the amount of panels you install. IE, you want a panel or two that are rated for either 150 or 155 watts, at the exact VMP of your current panel, or absolutely as close as possible. I wouldn't buy panels that were more than 0.1V more or 0.1V less, if it were me.
DoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
You probably would be OK with panel in the range of Vmp~17.5 to 18.6 volts or so when paralleling panels. Going much below 17.5 volts Vmp can reduce charging current (Vmp falls when panels get hot).
With MPPT controllers and higher voltage arrays (i.e., a 12 volt battery bank and Vmp~30 volts), you can run 10% (or ~3 volts) between the high and low panel Vmp (30 volts to 33 volts, or 30 volts to 27 volts) and be pretty much OK.
I think +/- 0.1 volts is a bit severe of a Vmp limit here. Vmp curves are fairly flat going +/- 5% to 10% off the peak does not "kill" the output.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:I think +/- 0.1 volts is a bit severe of a Vmp limit here. Vmp curves are fairly flat going +/- 5% to 10% off the peak does not "kill" the output.
-Bill
*Bill/BB. is an engineer.
edit: Not that I disagree with Bill, mind you. My point was only that anytime my opinion differs from Bill's, listen to Bill every time.
DoD= depth of discharge= amount removed from that battery SoC= state of charge= amount remaining in that batterySo, 0% DoD= 100% SoC, 25% DoD= 75% SoC, 50% DoD= 50% SoC, 75% DoD= 25% SoC, 100% DoD= 0% SoCA/C= air conditioning AC= alternating current (what comes from the outlets in your home) DC= direct current (what batteries & solar panels use) -
I am always learning--And I am certainly not correct all of the time--Ask my wife.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
mcgivor said:...the video demONstrates the importance of using hair spray to keep the head moving without the hair.
-
BB. said:I am always learning--And I am certainly not correct all of the time--Ask my wife.
-Bill
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed