New System, LOW OUTPUT. Neet help
Problem two, I can only hook up two of these at a time. It doesnt really matter which ones. I can hook up any two and get 260w, but when I hook up the other three, they only put out about 25w each of additional power. It doesnt matter which combination I use. Any ideas?
I see you have posted in the grid tie category. Please describe your components, wiring scheme and whether you have an agreement with the power company.
I am wired from the panels to the grid tie inverter. It is 1000 watt capacity. It is wired parallel. I do not have any agreement with the power company.
Can you link to the gt inverter you are using?
Also, exactly which solar panels you are using?
And how you know the watts you are generating? (Meter on gt inverter, utility meter?)
Details matter here.
- BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Assuming you have one controller, You can have two parallel strings of two panels, or two strings of three panels, but not one string of two and another string of three. You will essentially never see power from the 5th panel. Also, is it possible your batteries are already charged up? Maybe it only takes 260 watts to keep them floating... What kind of charge controller do you have? How are you connecting your panels? Must be very clear about it...
I see... my mistake. and I really don't know Grid Tie very well. But it's a curious question then... still. How is he "hooking up the other three"? In series with the first two? In parallel along side the first two (would only really double the amps - but will the inverter take that many amps?)... maybe the controller is limited on amps? Or volts? What's the O.C. max voltage of the inverter? so many questions!
@bloodofheroes
you say "it is wired in parallel"... exactly what is wired in parallel? Are all five solar panels wired in parallel? What do you mean? -
With these "burn your house down"/"Power company please disconnect me" grid tie inverters. I don't know what the most energy they can use is.
Please understand that the panel rating of the panels is somewhat over rated for Normal Operating Cell Temperature of the panel. Many panels publish a NOCT value, it is generally 75% of the name panel or a 100 watt panel could be expected to produce 75 watts while angled close to directly perpendicular to the sun. This could explain much of your loss.
The charge controller can only process one voltage level at a time, so if you have 60 cell panels that produce 31 volts and have a string of 2 so that the voltage adds to 62 volts, adding a single panel of 31 or 36 volts or a 72 cell panel or string of panels, can confuse the inverter making it search for a correct Maximum power point (MPPT Maximum Power Point Tracking)Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
This is how I have them wired.
I do not have a charge controller or batteries. It goes directly to the grid tie, Which I have two of, and both work great with the other three panels that I have. (The other three are different than the five, so I keep them separate.)
This is my grid tie inverter, yes, it is cheap, but as I said, it will work great with my other three panels, and even one of these if I want to hook it in.
And these are the panels that I am having trouble with. Its almost like I am capped at 260 watts. Two will go to 240-260, and any additional panels that I hook up will only give me about an additional 25w. I have hooked them up several different ways and its consistently the same.
All my panels are the same.
So all the positive wires from the panels come together, and all the negative ones do as well?
How are the positive wires joined (combiner box - if so, what kind)?
How long are the common positive and negative wires between the combiner and the inverter, and what wire size?
Do you have fuses or breakers anywhere? If so, where and what size?Off-grid.
Just wondering if it's those three panels. Do all of the panels work? Meaning, can you hook up any two of the five and get 260 watts?
If you take one out in the direct sun, cover it, connect it's wires together, and then uncover it, and measure the amperage flowing through the wires (the Short Circuit Amperage). You should see something close to it's Isc ratings (8.xx amps). Disconnect the wires and verify the Open Circuit Voltage (37.x). This would at least verify if the panels are good...
If you look into the manual for that grid tie inverter, is there a maximum input Amperage (Current). 1000w / 45volts is just over 20 amps. Two of your panels together in parallel make up to max 16 amps... but due to sunlight conditions your actual operating input voltage and amperage might be way down... like even down to 20 volts. You hook up another panel and you have max 24 amps flowing into the unit but still . Probably you don't get the full rated sunlight.... so If the unit was limited to perhaps 22 amps, it might not give you any more power unless you were to increase voltage up to the max of 45 volts...
You said you have other panels on a different inverter. Have you tried any of them on this inverter (removing all of these panels and using the others to test this inverter)???
I have mixed and matched. Outcome doesnt change.
I am getting about 24v while it is on the inverter, and when it is disconnected I get about 36v.
According to the manual, the inverter will take 45 amps. It is almost like it is limiting me to 10 amps though.
It may or may not be the inverter limiting you to 10a. It would help if you could answer the question about the wiring.Off-grid.
@bloodofheroes
The inverter states what looks like 20 -15 volts DC input, the panel voltage is too high. Looks like it requires 12 volt nominal panels, 17 to 21 volts. Check the voltage on the 3 panels that do work.
Rick4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset. -
Looks like 20 -45 volts.
If you have the 22.5 volt panels parallel wired ,the 22.5 volts is open circuit voltage. The Vmp. of those 12 volt panels is less than 20 volts. So which panels are giving you trouble The 12 volt panels or the 250 watt panels? I may be reading this wrong . Where are you getting the 22.5 volts number from? 22.5 volts sounds like a 12 volt panel.
Its 20-45VDCRaj174 said:@bloodofheroes
Rick
I have about a forty foot run of 14/2. No fuses or breakers (yet). They are just wired together with wire nuts. -
Opps, my bad.4480W PV, MNE175DR-TR, MN Classic 150, Outback Radian GS4048A, Mate3, 51.2V 360AH nominal LiFePO4, Kohler Pro 5.2E genset.
MY BAD!!! SORRY!! The wiring diagram reflects nothing in the way of the ratings of my panels. I was just trying to show how I have them wired with that picture. It doesnt reflect the panels that I am using. Sorry for the misunderstanding.littleharbor2 said:If you have the 22.5 volt panels parallel wired ,the 22.5 volts is open circuit voltage. The Vmp. of those 12 volt panels is less than 20 volts. So which panels are giving you trouble The 12 volt panels or the 250 watt panels? I may be reading this wrong . Where are you getting the 22.5 volts number from? 22.5 volts sounds like a 12 volt panel.
My panels are all 37.5 VOC. and 30.1 Vmp.
!4 ga. wire is awfully light gauge for 80 running feet of low voltage dc power.
What do you recommend? Do you seriously think that this is the problem? Its 40 foot.littleharbor2 said:!4 ga. wire is awfully light gauge for 80 running feet of low voltage dc power.
40 run is 80 feet round trip which is what you need to figure with DC. Look up a voltage drop calculator online and plug in your numbers as accurately as you can. You could be losing a good portion of your power. 14 ga. wire may be acceptable for higher voltage in your case being that you would be pushing much less amperage at high voltage. I wouldn't use anything smaller than 8 ga. for that low voltage run. Still you won't find much love for that type of grid tie inverter here. They are potentially dangerous. If, in the event of a fire, it's discovered you are using this kind of inverter you will likely be found liable for property damage and possible death. Not a good scenario.
What's probably happening, IMHO, is as you put more current through the wire it heats up, increases resistance and voltage drops below the 20v min the inverter needs. The wire nut connections also may not stand up to high currents. As LH2 suggests, you should look up values in a table (NAWS has them online). Something like 4ga for 40' with 5% voltage drop.
The five panels have potential current of ~40adc. 14ga is good for 15aac - using it for 40adc is dangerous. Also, you didn't say anything about fuses or breakers. Each parallel positive wire should be protected, as should the common run to the controller.Off-grid.
You need to use 8ga wire. The fact that you are trying to run over 30 amps through 14 ga wire and that you are using an illegal inverter makes me suspect you need to unhook those inverters until you've double checked everything and read up on the islanding requirements and certifications. As of a few years ago there were no "plug into the wall receptacle" UL certified inverters available in the US. If you do have a fire I doubt your homeowners insurance will pay. If you kill a line repair man because you're illegally back feeding the grid with a non UL approved inverter life will not be good.
48v Rolls 6CS 27P
I appreciate all the help. I thought that I was pretty smart, but found out really fast not as smart as I thought I was. I am going to add fuses, ect. but right now I am just trying to get this running. What kind of connections do you recommend? Keep it cheap. I am 1k in on this so far and dont really want to spend $300 on a connector box.Estragon said:> @bloodofheroes said:
I dont know what the risk of burning down a house with less than 1000w being separated between two inverters, but I promise i will be careful.
Simple 6 breaker combiner box from our host $88.50 + 5 breakers @11ea. A midnite baby box for the breaker ahead of the inverter, $29 + ~15 for a breaker (it should also fit a 2nd breaker for your other inverter if they're close together). Fuses are a bit cheaper, but by the time you get holders, not that much. Breakers are also handier as disconnects than fuses. Max 15a breakers in the combiner box. The bigger one for the baby box depends on the wire size you end up using.
40adc is nothing to sneeze at. DC will sustain an arc better than AC, which makes it more of a fire hazard.
@WaterWheel - according to NAWS chart, 8ga is too small for the 40' run.Off-grid.
Just sayin, according to his diagram, each panel has it's own set of wires... but do they go all the way (40ft) from the panel to the inverter and then combine together? Or, do they first combine and then run 40ft through 14/2? If the latter is true, then yes, I would agree with @Estragon and @WaterWheel and the rest of the long run comments. You need bigger wire. Also, the manner in which you connect your panels together in parallel is important. Wire nuts will not do for more than three individual wires. At least get a couple of Bus Bars from the electrical section and use the screw terminals to secure each wire. And yes, DC breakers!