Need help with charging schedule for L16 interstate batteries
MauiSun
Registered Users Posts: 7 ✭✭
First, thanks for any help, this site has been a godsend.
I just upgraded my battery bank from golf cart batteries to L16s, and I'm having trouble finding the correct charging and EQ voltages.
I read somewhere that L16s should be charged at a much higher voltage, with absorption at 61.2V and float at 54.6, both which seem a bit high.
I couldn't find anything on equalizing voltage. It also said absorption time should be at least 3 hours long.
I couldn't find any information from interstate, and trojan recommends completely different numbers for their L16s, with absorb at 57.6 and float at 52.8, and EQ at 61.92
These seems like drastically different numbers..... which ones do i go with? and how often should i schedule an equalization cycle with these batteries?
Thanks for any tips!
I just upgraded my battery bank from golf cart batteries to L16s, and I'm having trouble finding the correct charging and EQ voltages.
I read somewhere that L16s should be charged at a much higher voltage, with absorption at 61.2V and float at 54.6, both which seem a bit high.
I couldn't find anything on equalizing voltage. It also said absorption time should be at least 3 hours long.
I couldn't find any information from interstate, and trojan recommends completely different numbers for their L16s, with absorb at 57.6 and float at 52.8, and EQ at 61.92
These seems like drastically different numbers..... which ones do i go with? and how often should i schedule an equalization cycle with these batteries?
Thanks for any tips!
Comments
-
From what I understand, therefore not 100% sure, Interstate batteries are manufactured by US Battery, perhaps someone who knows for sure can verify. Here is the pdf. for US Battery, if nothing else, it's information.
Edit. Johnson Controls may be the parent, manufacturer/owner of Interstate, or both? Who knows, major conglomerates are eating up everything, or so it seems.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
What does your battery dealer suggest?
Marc
I always have more questions than answers. That's the nature of life. -
You might find that time constraints with solar force the use of higher voltages than normal. Check specific gravity (SG) to verify.
I am available for custom hardware/firmware development
-
Some interesting reading regarding L-16 batteries.From Home Power Magazine.Battery management andmaintenance are significantconcerns in off-grid PV systems.Many of the user problems associatedwith these systems can be traced toimproper treatment andmisunderstanding of batteryperformance.Modern battery chargers use three charging stages—bulk, finish (absorption), and float. Bulk brings thebatteries up to the high voltage regulation point; finishholds it at this high voltage regulation point based ontime. In the absorption stage, the voltage is constant,and the current tapers off as the batteries are filled.Float trickle charges the battery to a lower, userdeterminedvoltage to keep it full.From my experience, the most common battery problemis undercharging, leading to sulfation, loss of storagecapacity, and shortened service life. Sandia NationalLaboratories recently published “PV Hybrid BatteryTests on L-16 Batteries” (see Access). Their testsrepresent several years of systematic testing of a PVgenerator(hybrid) system.The Sandia report is very thorough. Four differentbrands of batteries were tested. They were all flooded,L-16 type batteries, the most common battery used inresidential-scale RE systems. Tests were repeated sothat the data represents good averages, and theconclusions are based on good data and methodology.The study has four conclusions:1. The finish voltage (sometimes called the absorptionvoltage) for a flooded lead-acid battery operating at12 VDC nominal should be about 15.3 volts (2.55 percell) rather than the customary 14.4 volts.2. Finish charge time should be at least 3 hours andoften longer.3. The maximum interval between finish charges shouldbe about five days.4. Not all brands of L-16s are the same (though thereport names no names).The general conclusions of the Sandia report areconsistent with the number one problem experienced inoff-grid PV systems—undercharged batteries. RichardPerez has for many years advocated higher finishvoltages for PV-engine generator systems. As he says,“I like to run them hot.”Home Power technical editor Joe Schwartz adds somegood advice regarding flooded lead-acid batteries:• Higher finish charge rates result in significantly moregassing and potential for hydrogen buildup. Beforeyou crank up the finish voltage to 15.3 VDC (for anominal 12 volt system), make sure that the batterycontainment is well ventilated. The use of poweredbattery vents is recommended.• Batteries charged to a high finish voltage produce asignificant amount of waste heat. Depending on thetype and location of the battery containment, in warmclimates or seasons active ventilation may be requiredto keep battery temperature in check. Optimaloperating temperature for lead-acid batteries is 78°F(25°C). Higher battery temperatures (90°F plus; 32°C)result in increased self-discharge. Temperatures over120°F (49°C) can damage lead-acid batteries.• Batteries charged to a high finish voltage consume alot of water. Compared to charging at the traditional14.4 VDC finish voltage, the time period betweenbattery watering can easily be cut in half. Automaticbattery watering systems greatly simplify the process.• Use temperature compensation on all chargecontrollers and inverter/chargers.Finish Charging Is InefficientThere is one significant downside to the batterymanagement strategy presented in the Sandia report.Due to battery charging characteristics, efficiency isvery low during the finish charge phase. Very longengine generator run times were reported, sometimesfrom 6 to 20 hours. These long run times were requiredto completely refill the batteries to the manufacturers’stated ampere-hour capacity.The state of charge (SOC) of a battery is mostaccurately measured with a hydrometer, and isindicated as specific gravity (SG). Most RE users rely onamp-hour meters to provide convenient (althoughslightly less accurate) battery SOC information. Duringthe Sandia tests, full batteries had a SG in the range of1.290. The long, engine generator run times needed toachieve this SG translate into dollars and pollution (bothaudio and atmospheric). Perhaps there is a “middleway” that preserves the lifetime of the batteries whilereducing the time and cost of engine generator finishcharging.Revisit the AssumptionsThe batteries tested at Sandia were discharged by 60percent of capacity (to 40% SOC) and then chargedback to rated capacity. In these tests, the ratedcapacities were determined empirically, and in mostcases were close to the manufacturer’s stated value (inthe range of 350 AH for an L-16).These two points require comment. First, this depth ofdischarge is not typical of most well-designed, standalonePV systems. This point is clearly stated by theauthor of the study. Most stand-alone PV systems, bydesign, cycle batteries by about 25 percent daily, not 60percent.Second, the manufacturer’s rated battery capacity andthe way it is determined should be understood. Allmanufacturers recharge batteries on the grid. Using thegrid, they can finish charge the batteries for long periods(on the order of 8 to 12 hours), cramming maximumampere-hours into them. For a manufacturer, thismethod makes sense because it results in greater AHcapacity figures for their product.The long engine generator run times required by PVhybrid systems must mimic the finish charge conditionsthe manufacturers use to rate the battery’s capacity.Perhaps batteries should be rated based on theirapplication. For instance, a battery used in a standbyapplication (such as utility backup system with gridrecharging) might specify a full charge SG of 1.290. Thesame battery used in an application that regularlycycles the batteries (such as a PV system with enginegenerator backup) might have a recommended SG of1.250 to be considered full.It is true that a battery with a SG of 1.290 holds morecharge than the same battery with a SG of 1.250.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I have US Battery L16s, and use 58.8v for absorb, which seems to work fine, with EQs every month or two. Actual voltage is higher as the bank is almost always under 25°C. I use end amps at~1% of capacity for absorb time.
As the batteries age (currently in their 4th year) I expect I'll need to increase voltage and maybe end amps a bit.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed