Battery Upgrade
nickdearing88
Registered Users Posts: 100 ✭✭✭
I finally took the plunge and purchased 2 - 12v 100Ah LiFePO4 batteries from Battleborn (via our hosts).
Per the manufacturer's recommendations, I wired the batteries in parallel (12v 200Ah) and charged to ~14.4v with a 30 minute absorb. I set the CC to 14.3 because the meter usually reads the battery voltage a few tenths of a volt lower than actual.
The balancing system is passive (using resistors) and top-balances between 14.2v and 14.6v (max). Battleborn has had really good luck with cell balancing using only the passive system and it saves costs, lowers self-consumption, and complexity.
I then switched to series configuration for 24v 100Ah. I've only played around for the past two days but I'm watching charge and discharge voltages very closely. It's amazing how flat the discharge curve is compared to LA. The OC resting voltage when full is about 13.6v so I set my float voltage at 13.5. Therefore no real charging should occur during float unless a large load turns on. It even took several amp-hours of use after completing absorb before the batteries dropped from absorb voltage to my float setting!
I plan to cycle between 20% - 90% SOC but I figured a full absorb was important for balance purposes during commissioning.
I'll update with my experience as I go, but so far -- I'm happy.
Per the manufacturer's recommendations, I wired the batteries in parallel (12v 200Ah) and charged to ~14.4v with a 30 minute absorb. I set the CC to 14.3 because the meter usually reads the battery voltage a few tenths of a volt lower than actual.
The balancing system is passive (using resistors) and top-balances between 14.2v and 14.6v (max). Battleborn has had really good luck with cell balancing using only the passive system and it saves costs, lowers self-consumption, and complexity.
I then switched to series configuration for 24v 100Ah. I've only played around for the past two days but I'm watching charge and discharge voltages very closely. It's amazing how flat the discharge curve is compared to LA. The OC resting voltage when full is about 13.6v so I set my float voltage at 13.5. Therefore no real charging should occur during float unless a large load turns on. It even took several amp-hours of use after completing absorb before the batteries dropped from absorb voltage to my float setting!
I plan to cycle between 20% - 90% SOC but I figured a full absorb was important for balance purposes during commissioning.
I'll update with my experience as I go, but so far -- I'm happy.
Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter
Comments
-
I had a look at the documentation on your battery, looks like a nice battery. I really liked to see the spec saying the battery lifespan in Ah cycled through it rather than in number of cycles!
It is a shame that the battery doesn't have a way that you can measure the individual cell voltages.
I agree with your strategy of charging to 14.4 during the commissioning. On a regular basis I would charge a battery like yours to 27.6V (3.45V/cell) and terminate the charge at C/20-C/50 or set the absorb time at 15 minutes and set the float to 26.8V (3.35V/cell), slightly less than your setting.
Once a month I would do a charge and absorb at 28.8V (3.6V/cell) to balance the battery. If you wanted to automate this process and if your charge controller will allow it you could set the charge controller to do an equilise cycle at 28.8V (14.4V/cell)
Simon
Off-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
Is there any information regarding ambient temperature verses life expectancy? Can't seem to find any on the Battle Born site.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Warning. If you are going to top balance this battery, you better keep the EQ amps BELOW the amps the BMS / balance vampire boards can handle, or you will overvoltage some cells
And same theory about Absorb and Float, don't push more into the cells, than the balancer boards / BMS can handle
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
karrak said:I had a look at the documentation on your battery, looks like a nice battery. I really liked to see the spec saying the battery lifespan in Ah cycled through it rather than in number of cycles!
It is a shame that the battery doesn't have a way that you can measure the individual cell voltages.
I agree with your strategy of charging to 14.4 during the commissioning. On a regular basis I would charge a battery like yours to 27.6V (3.45V/cell) and terminate the charge at C/20-C/50 or set the absorb time at 15 minutes and set the float to 26.8V (3.35V/cell), slightly less than your setting.
Once a month I would do a charge and absorb at 28.8V (3.6V/cell) to balance the battery. If you wanted to automate this process and if your charge controller will allow it you could set the charge controller to do an equilise cycle at 28.8V (14.4V/cell)
Simon
Great idea about the equalization voltage for balancing, I never thought of that but it's perfect!Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
mcgivor said:Is there any information regarding ambient temperature verses life expectancy? Can't seem to find any on the Battle Born site.Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter
-
Update: I did run into a BMS issue but as soon as I mentioned it to Battleborn, they knew exactly what it was. Apparently they discovered a small number of BMS units had an issue and I just happened to get one of them. They are promptly sending me two new batteries with correct BMS system and pre-paid return labels. The customer support seems to be awesome.
During specific discharge parameters (after 20 minutes, between 25-50 amps), the BMS would cut the voltage to 9.5v for a second, then back to normal. Under 25 amps or over 50 amps discharge, the issue doesn't occur.Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
Here are is the discharge curve chart from Battle Born if anyone's interested.Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter
-
mike95490 said:Warning. If you are going to top balance this battery, you better keep the EQ amps BELOW the amps the BMS / balance vampire boards can handle, or you will overvoltage some cells
And same theory about Absorb and Float, don't push more into the cells, than the balancer boards / BMS can handleCurrent system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
nickdearing88 said:Once I'm more comfortable with the LI characteristics, I would likely make my own "pack" with prismatic cells and a custom BMS/active balancer.
Personally, I can't see much point in doing this as the amount of energy that is lost in just passively balancing using resistors is negligible. In the last twelve months I haven't had to balance my battery at all, in the twelve months before that I would have wasted about ~10Wh to balance my battery. I also can't see much point in having automatic balancing unless you want a "set and forget" system or it is operated by someone who didn't have enough technical expertise to do the balancing manually.
Simon
Off-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
nickdearing88 said:mike95490 said:Warning. If you are going to top balance this battery, you better keep the EQ amps BELOW the amps the BMS / balance vampire boards can handle, or you will overvoltage some cells
And same theory about Absorb and Float, don't push more into the cells, than the balancer boards / BMS can handle
Simon
Off-Grid with LFP (LiFePO4) battery, battery Installed April 2013
32x90Ah Winston cells 2p16s (48V), MPP Solar PIP5048MS 5kW Inverter/80A MPPT controller/60A charger, 1900W of Solar Panels
modified BMS based on TI bq769x0 cell monitors.
Homemade overall system monitoring and power management https://github.com/simat/BatteryMonitor
-
karrak said:nickdearing88 said:Once I'm more comfortable with the LI characteristics, I would likely make my own "pack" with prismatic cells and a custom BMS/active balancer.
Personally, I can't see much point in doing this as the amount of energy that is lost in just passively balancing using resistors is negligible. In the last twelve months I haven't had to balance my battery at all, in the twelve months before that I would have wasted about ~10Wh to balance my battery. I also can't see much point in having automatic balancing unless you want a "set and forget" system or it is operated by someone who didn't have enough technical expertise to do the balancing manually.
Simon
Good to know. I'm still learning the nuances of various balancing. When I first looked at Battle Born's information, I read "Automatic Cell Balancing" and interpreted as "Active Cell Balancing". When he said it was a passive system with resistors, I figured it was a cost savings measure. By the sounds of it, your system is also using resistors for balancing? I just figured most of the systems people installed used active balancing to move the current between cells rather than eat it up via a resistor as heat. But, I was expecting large imbalances based on some posts here.
Another +1 on your lower Absorb rate and using Equalize monthly at 3.6v/cell for balancing. Really good idea and although it's only been a few days, seems to be working great!Current system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter -
karrak said:nickdearing88 said:mike95490 said:Warning. If you are going to top balance this battery, you better keep the EQ amps BELOW the amps the BMS / balance vampire boards can handle, or you will overvoltage some cells
And same theory about Absorb and Float, don't push more into the cells, than the balancer boards / BMS can handle
SimonCurrent system: 8-100w Renogy panels mono/poly, 2 strings of 4 panels in series - 24v 100Ah AGM Battleborn LiFePO4 batteries - Morningstar MPPT40 CC - 1500W Samlex PSW inverter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed