live amps & neutral amps
solarking
Registered Users Posts: 67 ✭✭
why there are neutral and live amps reading on electric meters? what is the real purpose of neutral amps
The north American 120/240 60Hz residential feed is split phase (180 degrees apart) between the two hot leads.
Simple way is that it is a center tapped transformer feeding the home.
You cannot measure the current in just one leg. The neutral leg current is the sum of the A and B hot leg currents. Remember that A and B are 180 degrees out of phase. So 10 amps on A, 0 amps on equals 10 amps on neutral.
10 amps on A and 10 amps on B equals 0 amps on the neutral.
So, our electric meter needs to measure current on two legs of the three wire circuit.
And remember 10 amps × 120 volts = 1,200 Watts. And 10 amps × 240 volts = 2,400 Watts.
So the meter needs both voltage and current to figure out the billing.
As to 120 vs 240 vac, probably because the first power systems were DC and Edison's filament light was designed for 110 vac. The first A.C. systems were designed to support the 110 VDC bulbs and appliances.
Tesla wanted 220/240 VAC but, by this time, major appliances like refrigerators and such were already in wide use in the US and expensive to replace. In Europe, not so much at the time.
Also 110 volts is much lures likely to injure or kill vs 220 volts. The danger of electricity was a big issue back in the days of Edison and Tesla.
- BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
He also wanted to have his free distribution of power without wires to be set up all over the us. If that had been done, there would be no off-grid anymore. The air is the grid.
But since Morgan couldn't meter it, it was shot down and buried. -
The amps in the Neutral Wire is always equal to the difference between the amps measured in Hot Line #1 and Hot Line #2.
If all of your loads were 240 Volts ( ie 240 Volt Water Heater ) then the neutral wire is "technically" not needed ...
Line #1 @ 10 Amps - Line #2 @ 10 Amps = Neutral Wire @ 0 Amps.
However, when you have unequal 110 Volt loads (very likely) then the neutral wire must carry the difference ...
Line #1 @ 10 Amps - Line #2 @ 5 Amps = Neutral Wire @ 5 Amps
Line #1 @ 10 Amps - Line #2 @ 0 Amps = Neutral Wire @ 10 Amps
Things get more complicated if you have a GTI and one leg is consuming power and one leg is providing power to the grid.
"Smart" Utility Meters can detect this, but most humans using a typical DVM cannot.
What happens when neutral line is only fed to the input of the inverter and only the phase from the inverter output and neutral from the input is supplied to the load.
solarking said:What happens when neutral line is only fed to the input of the inverter and only the phase from the inverter output and neutral from the input is supplied to the load.
The GTI will reduce the loading on that half of the 240 V AC transformer and the Power Meter will slow down appropriately.
I do not believe that my Residential Meter actually measures the amps flowing through the Neutral.
I am billed for the SUM of ...
Line #1 Watts = Amps through Line #1 x 120 V AC
Line #2 Watts = Amps through Line #2 x 120 V AC
Total Watts
It does not matter if there are any amps in the Neutral Wire or not.
I believe the Neutral Wires are simply connected to a Lug inside the Meter Box.
I believe @solarking is in India so no split phase involved .1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
I wonder if it's a power factor related meter function (KVA vs Kwh)?Off-grid.
solarking said:why there are neutral and live amps reading on electric meters? what is the real purpose of neutral amps
The Grid in India appears to supply 230 Volts 50 Hz AC Residential.
Do you use 2 prong plugs or 3 prong plugs? ( BS-546 )
If your neutral wire is bonded to the ground wire then
I do not see why the Power Meter needs to measure the amps in the Neutral Wire.
The energy (kwh) consumed by the residence can be determined by measuring the amps in just the Hot Wire & Volts.
Maybe, they want to verify that you are, in fact, using the Neutral Wire as your return and not the safety ground wire?
If there is a difference beteen Hot & Neutral amps then you have safety issue?
In the USA, our Power Meter does not measure the Neutral Amps, so this is very hard to solve.
Below is a page from the India - 2011 National Electrical Code
The Single Phase Energy Meter appears to measure ...
1) The AMPS in the (P)ower wire only and
2) The VOLTS between the (P)ower wire and the (N)eutral wire
And I did not see any diagram showing where or if the (N)eutral Wire is ever bonded to the Ground Wire.
The (N)eutral WIre typically connects to the common of a 3-Phase WYE on the Power Pole
I do not see the answer to the OP's question "Metering amps in the neutral wire" in the India 2011 NEC.
Maybe the OP has newer Power Meter?
You guys are probably correct and I am miss-remembering (aka "wrong"). The split phase meters do not measure current in the neutral leg.
Because the Neutral is (in the US) bonded both at the pole and at the main panel, there are possibilities for parallel current paths (through ground paths) that would make reading the neutral current inaccurate for billing.
Not sure why they monitor the neutral, the billing is off volts and amps used.
I have heard of unscrupulous users taking the 12 volts off a phone line to run 12 volt loads illegally before though, so maybe they are looking for something similar? -
Why does the meter shows negative watts(showing minus sign while displaying watts)
Main causes of neutral reversal and ground fault ? how to troubleshoot
Lumisol said:Not sure why they monitor the neutral, the billing is off volts and amps used.
BB. said:You guys are probably correct and I am miss-remembering (aka "wrong"). The split phase meters do not measure current in the neutral leg.
what is the main reason for neutral reversal and ground fault? Sometimes it shows reversal and ground fault what could be the reason?
What do you mean by neutral reversal?
The two reasons a utility meter would read negative.
First is the power in and power out leads are reversed.
Second is a power source (gt inverter, synced genset, even an induction motor driven by a gasoline/diesel engine) can drive power backwards through the meter.
Is this single or three phase meter?
BB. said:What do you mean by neutral reversal?
- Bill
Strange thing is on my 12v inverter I get the phase reversal and ground fault but if I use 24v inverter I get no reverse current issue on the utility meter.
It is a single phase meter, power factor on metes shows .75 sometimes .65 is it worse?
- 628 Discussion Forums/Café