String Design
Hi Everybody,
I have the following question and would appreciate all advise and tips. Thanks
in advance
I have a charge controller with the following specs:
It's the Growatt 5000 SPF Off Grid Inverter/charger
PV Array MPP voltage range
60 – 115
VDC
Max PV Array open circuit voltage
145 VDC
Max solar charge current
70A
Number of MPP trackers / number of string per MPP tracker
2 / 1
Maximum input power
3500 Watt
PV Module Data:
250 Wp
Voc 36,5V
Vmp 30,4V
Isc 9,21A
Imp 8,22A
I want to connect 14 PV Modules of 250 Wp
How would the string design be?
Looking foreward to your reactions
Thanks in advance
Regards
Johan
Is the 70A the total for both inputs, or for each input? Can't seem to find specs on the SPF, the panel count 14×250W is the maximum input wattage, but the open circuit voltage only allows 3 per string and 3 doesn't divide into 14.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Hi Mcgivor,
Thanks for your reply. That's exactly my point. I think connecting 14 panels to this inver is not possible.
If someone has any other ideas
Please let me know
Thx -
What is your system voltage? Are the 2 inputs independent?
While they have only one input, I would think, if you have a 48 volt system, you could run 2 parallel strings into each input. The manufacturer should have some information. If they are independent you could run them without a fuse or breaker for each string, but safer just to go ahead and have a breaker for each string.
This would still be below the 70 amp output, and unshaded strings, in parallel should not create a tracking problem. Still can't get 14 panels in there, since the VOC would be too high.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
Is the MPP 70A for both, or one input, this would be very helpful in answering questions.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Temperature at your location is also a factor. The strings need to be set up so that Voc at record low temps at your location is <145v, and Vmp at highs >60v.
If Vmp is low with hot panels, you just won't charge. If Voc is too high though, you can damage equipment and void warranty.
Voltage drop in the wire from array also needs to be considered.Off-grid.
Best configuration would be 4 strings of 3 panels. 2 strings into first MPPT and 2 into the second. 12 panels total.