Worth converting from 24 to 48 volt system?

I currently have:
*24 volt, 405ah battery bank in the form of 4, 6 volt batteries in series
*2 series strings of 3, 295 watt panels (about 110 vdc comes in to the controller)
*Classic 200
*lights, ceiling fan, and 'fridge are 24vdc
*24v, 2kw inverter
I'm planning to add two more strings of 3 panels each and another Classic 200. I could double my battery capacity with either
*two parallel 24v strings of 4, 6 volt batteries, or
*a single series string of 8 batteries for 48 volts.
In either case they'll all be new batteries. I understand that (1) it's better to avoid parallel battery strings if possible, and (2) the controller is more efficient as the input voltage is closer to the battery bank voltage. In order to convert to 48vdc I'd need to (1) sell my 24v 2kw inverter and purchase a 48 volt unit, and (2) purchase a DC-DC converter to run my 24v loads.
Here's the question: Given the above, are the benefits of going to 48vdc worth the cost?
Thanks!
*24 volt, 405ah battery bank in the form of 4, 6 volt batteries in series
*2 series strings of 3, 295 watt panels (about 110 vdc comes in to the controller)
*Classic 200
*lights, ceiling fan, and 'fridge are 24vdc
*24v, 2kw inverter
I'm planning to add two more strings of 3 panels each and another Classic 200. I could double my battery capacity with either
*two parallel 24v strings of 4, 6 volt batteries, or
*a single series string of 8 batteries for 48 volts.
In either case they'll all be new batteries. I understand that (1) it's better to avoid parallel battery strings if possible, and (2) the controller is more efficient as the input voltage is closer to the battery bank voltage. In order to convert to 48vdc I'd need to (1) sell my 24v 2kw inverter and purchase a 48 volt unit, and (2) purchase a DC-DC converter to run my 24v loads.
Here's the question: Given the above, are the benefits of going to 48vdc worth the cost?
Thanks!
Comments
Another option have 2 × 24V systems, one for DC loads and the other for inverter loads, always good to have the redundancy of a second system.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
I don't have the 24 volt loads, but wish I was at 48 volts in general. I'll switch when I replace my battery.
An advantage to parallel banks is the option to live on a single string for a bit when cell(s) eventually start failing, and limp by for a while by swapping out weakening batteries from the in-use string and replacing with stronger ones from the decommisioned string. This might be more of a factor if you're really remote and replacing the bank requires lots of planning and logistics. Having a second classic also gives some redundancy.
The voltage question comes down to expected current and future loads. You could do without the second classic at 48v, and if you were starting from scratch it would probably make sense (depending on inverter loads) to go to 48v. As you're already set up for 24v though, it depends on your priorities and loads.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter