Charging a battery
kau
Registered Users Posts: 8 ✭✭
Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.
Comments
-
If your panel has 36 cells it would be a 12 volt nominal panel. When connected to the battery you will notice the voltage output drop to somewhere below 14.4 volts depending on the state of charge of the battery. You can crudely charge your battery by monitoring the voltage but to do it properly you need a charge controller to do the absorb phase which holds the voltage steady at a predetermined voltage and allowing amperage to flow and complete the charge cycle . After absorb the controller will go into float and maintain your battery at 100% full until your battery loads pull it below full at which time the charging cycle begins again, provided there is sun, Ie; the next day.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
The short answer:
No.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
If you check every 15 minutes, log when the battery is at the proper absorb voltage, and disconnect before you cook the battery, it's easier to get a charge controller, unless this is a one time thing.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
kau said:Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.
Generally, it is never a good plan to feed batteries uncontrolled voltages.
Marc
I always have more questions than answers. That's the nature of life. -
littleharbor2 said:If your panel has 36 cells it would be a 12 volt nominal panel. When connected to the battery you will notice the voltage output drop to somewhere below 14.4 volts depending on the state of charge of the battery. You can crudely charge your battery by monitoring the voltage but to do it properly you need a charge controller to do the absorb phase which holds the voltage steady at a predetermined voltage and allowing amperage to flow and complete the charge cycle . After absorb the controller will go into float and maintain your battery at 100% full until your battery loads pull it below full at which time the charging cycle begins again, provided there is sun, Ie; the next day.
Thanks little, my cc croaked
-
Kau, your welcome. Apparently the description wasn't necessary. Sounded from your opening post in the solar beginners corner you might not have done this before.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
You will also want to keep an eye on temps as voltage reaches absorb. You might be able to do a sort of crude PWM absorb by connecting and disconnecting the panel.Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
Heh, actually you will undercharge if you just pull the panel off the battery when it reaches say 14.4v and you have an eagle-eye on your voltmeter. However, If you leave it connected, the voltage of the battery will eventually try to reach the voltage of the panel, about 18v for a nominal 12v panel, and you will quickly kill it.
In a total pinch on a deserted island, this technique might be enough to start your vehicle, even though it is not fully charged.
If you use the eagle-eye voltmeter monitoring method, you'd have to emulate the old style ping-pong hysteresis controllers. That is, let the terminal voltage rise to say 14.4v, pull the panel, and then let it rest until the voltage of the battery drops to 13.2v. Re-attach the panel, and once again remove it when the voltage is 14.4v. Rinse and repeat hundreds of times. Each cycle of this gets quicker and quicker. Take a phone call, turn around, and you are cooking your battery with high voltage.
Even if you DO have a "hysteresis" type controller (such as cheap HF, Coleman, Sunforce 7a types), hysteresis charging is VERY inefficient and was common back in the 1970's.
In other words, unless you are on a deserted island with nothing but a panel, voltmeter, time on your hands, and a battery, get yourself a solar controller - pwm at least.
-
@PNjunction - that's pretty much the crude PWM I had in mind. Note OP said his cc "croaked". I assume he wasn't talking about a sound it made :-)Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
kau said:Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.
when attached to the 70 Watt solar panel and in the full sun ?
It really depends upon the size of the battery, in Amp-Hours.
A typical 100 AH wet battery would reach 15 Volts @ 4.6 amps and will be about ~95% recharged.
The above describes a typical Bulk Charge.
At this point, we would normally switch to a constant 15 Volts ABSORB, to taper the amps until 100% recharged.
But that is not going to happen if you leave the battery connected to the Solar Panel.
So at this point, if you do leave the Solar Panel connected ...
You would only need about another 5 AH ( 100 AH battery x 5% remaining )
That means another ~1 hour (max) of charging at 4.6 amps.
That would push the final voltage near 16 volts !
I would disconnect the solar panel from the battery when either:
a) The battery reaches 16 volts @ 4.3 amps or
b) one hour has passed since the 15 volt reading
which ever occurs first.
The battery will be very near 100% recharged.
Voltages at 70° F.
Measuring the SG and reading no increase is the best way to know 100% recharged.
-
How about a potentiometer in the circuit to give a specific voltage drop, to regulate the voltage after absorb voltage is achieved?
Okay, a high-power pot could be expensive. What other kind of variable load would be appropriate in a pinch?
Edit: I was thinking potentiometer, not variac -
I would get a cheap 10A charge controller <$15, and call it a day, there are better things to do with time, unless you're locked up in jail somwhere.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
> @mcgivor said:
> I would get a cheap 10A charge controller <$15, and call it a day, there are better things to do with time, unless you're locked up in jail somwhere.
Oh, no doubt. A charge controller is the way to go. I was trying to think outside of the box, MacGyver-style. There have been a couple of winter days that my battery bank was in dire need of a charge and there was no propane for the generator, because the weather kept me from driving the 8 miles of mud to get to town 20 miles away. Pop the hood. Hook up the jumper cables to the inverter to power the battery charger. Yeah, the battery charger was underpowered, but it got me through the day. I would have jumped it all the way to the battery, but my cables weren't long enough. -
Maybe we could make a charge controller out of coconuts and seashells. Eh, Professor?
-
Marc Kurth said:kau said:Is it okay to charge a 12 volt battery straight off a 70 watt panel putting off about 19 volts, if I monitor manually and remove before batt is over charged.
Generally, it is never a good plan to feed batteries uncontrolled voltages.
Marc
-
stranger said:Maybe we could make a charge controller out of coconuts and seashells. Eh, Professor?
-
You should be able to edit your post up to 1 week after it has been posted... There should be a little black "gear" in the upper right of the box around your post... Click on that and you should see Edit/Delete.
If you need to change something later--Just send me a PM and I can take care of it.
-Bill "moderator" B.
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
and you have to click on that option too, "EDIT 1 week" is a bit of a misleading statement...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Hi Kau,
Thanks for this query. A panel with 36 cells means that it's a 12 volt nominal panel. If you connect the battery, your voltage output might drop. Well, sure you can charge it, but you're going to have to monitor the voltage. It'll have to go through the absorb phase wherein you'll need to have a charge controller.
Thanks,
Archsabino
-
kau said:stranger said:Maybe we could make a charge controller out of coconuts and seashells. Eh, Professor?
But at the end, the amps needed to be used depends on the size of the battery size.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed