PV array breaker sizing and voltage rating
ctann
Registered Users Posts: 12 ✭✭
Hi all,
Putting the last touches on my 4kW off-grid solar installation design. Right now I am running through the wiring and breaker sizing. This will be a 12x325W panel, Magnum PT-100 charger, Magnum PAE inverter, and 48V battery bank.
The panels have VOC = 46.1V, ISC = 9.48A and TC_VOC = -0.304%. I am sizing as 3 panels in series, 4 parallel strings.
My breaker sizing calc shows that I need 12A 100% duty cycle breakers (1.25*9.48), although wiring should be sized for 15A (I'm still a little confused about the two 25% derating factors). However, what worries me is the breaker voltage rating. 3*46.1 = 138.3V, but if I derate for my worst case ambient temperature (-10C), that comes to 153V - just pushing me past the 150V breaker rating.
So, two questions
- Will 150V PV breakers meet NEC code for my system?
- Are 150V breakers safe to use in this installation?
I really don't want to go to the 300V breakers - my current installation plan has exactly 4 open fuse slots in the panel, and going to the 300V breakers would require me to go to a larger 8-slot combiner box.
Thanks,
Chris.
ps - The breakers in question are the Midnite Solar MNEPV12 or MNEPV12-300. The combined PV source will be going through an MNEPV50-300 to the charge controller.
Putting the last touches on my 4kW off-grid solar installation design. Right now I am running through the wiring and breaker sizing. This will be a 12x325W panel, Magnum PT-100 charger, Magnum PAE inverter, and 48V battery bank.
The panels have VOC = 46.1V, ISC = 9.48A and TC_VOC = -0.304%. I am sizing as 3 panels in series, 4 parallel strings.
My breaker sizing calc shows that I need 12A 100% duty cycle breakers (1.25*9.48), although wiring should be sized for 15A (I'm still a little confused about the two 25% derating factors). However, what worries me is the breaker voltage rating. 3*46.1 = 138.3V, but if I derate for my worst case ambient temperature (-10C), that comes to 153V - just pushing me past the 150V breaker rating.
So, two questions
- Will 150V PV breakers meet NEC code for my system?
- Are 150V breakers safe to use in this installation?
I really don't want to go to the 300V breakers - my current installation plan has exactly 4 open fuse slots in the panel, and going to the 300V breakers would require me to go to a larger 8-slot combiner box.
Thanks,
Chris.
ps - The breakers in question are the Midnite Solar MNEPV12 or MNEPV12-300. The combined PV source will be going through an MNEPV50-300 to the charge controller.
Tagged:
Comments
-
153V - just pushing me past the 150V breaker ratingWhat's the kill voltage for your charge controller ? Usually it's 150V, that would worry me more than the breaker. Most controllers have a high voltage logger for warranty exclusion . Exceed that and you are SOL.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Well, I think I have answered myself for #1. http://www.solarabcs.org/about/publications/reports/expedited-permit/map/ shows my location (95120, San Jose CA) "Extreme Minimum" as 0 degrees C. I'm not sure where I got the -10 degrees C from that I was using before - probably from a gardening website when looking into planting fruit trees! That is a reasonably realistic number for this area though - maybe once every 20 years. At 0 degrees C, my VOC = 149V - so from a code perspective, it looks like I am OK with the 150V rated breakers.
Still interested in #2, the safety aspect, but it seems that under any condition that generates significant current, the temperature of the panels will never be under 0 degrees C. -
mike95490 said:153V - just pushing me past the 150V breaker ratingWhat's the kill voltage for your charge controller ? Usually it's 150V, that would worry me more than the breaker. Most controllers have a high voltage logger for warranty exclusion . Exceed that and you are SOL.
-
I don't think VOC is relevant since it would only apply when there was in essence no current. Sillier things have been written into the code though...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed