Battery bank wiring help, inconsistent discharge
jimmyaz
Registered Users Posts: 114 ✭✭
Hey guys,
I have 4x AGM 12volts 105 amps hour battery. I currently have it wire in series then parallels to make a 24volts 210ah bank....
But I am having problem when I drain the battery more than 20-25%.... Picture attached. When they are all charge up, the voltage seem to be within .30volts difference. But after discharging about 20-30ah.... Battery 1 and 4 voltage always drop significantly lower...
#1: 9.9v
#2: 11,9v
#3: 11.8v
#4: 9.9v
My actual wiring, instead of the negative going to battery 4 like the diagram, I have it connected to battery 2. But I can't imagine the distance of 6 inches would make that much of a difference?
DId I config it wrong, or is my battery dying? I am now thinking, maybe I should have parallels 2x together first, then series it? But everywhere I see online show series first than parallels.... But I also see Testa battery, they parallels all the cells first, then series?
thanks
I have 4x AGM 12volts 105 amps hour battery. I currently have it wire in series then parallels to make a 24volts 210ah bank....
But I am having problem when I drain the battery more than 20-25%.... Picture attached. When they are all charge up, the voltage seem to be within .30volts difference. But after discharging about 20-30ah.... Battery 1 and 4 voltage always drop significantly lower...
#1: 9.9v
#2: 11,9v
#3: 11.8v
#4: 9.9v
My actual wiring, instead of the negative going to battery 4 like the diagram, I have it connected to battery 2. But I can't imagine the distance of 6 inches would make that much of a difference?
DId I config it wrong, or is my battery dying? I am now thinking, maybe I should have parallels 2x together first, then series it? But everywhere I see online show series first than parallels.... But I also see Testa battery, they parallels all the cells first, then series?
thanks
Comments
-
-
My batteries are set up similar to your first configuration. I think there may be a problem with the individual batteries; not the wiring.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
-
-
Put some yellow paint on battery #1.
Keep wiring the same as you have it now.
Move battery 1 to #3 position, and move battery 3 to #1 position.
Then check to see if the yellow battery still drops to 9.8 volts.Camden County, NJ, USA
19 SW285 panels
SE5000 inverter
grid tied -
jimmyaz said:Hey guys,
I have 4x AGM 12volts 105 amps hour battery. I currently have it wire in series then parallels to make a 24volts 210ah bank....
But I am having problem when I drain the battery more than 20-25%.... Picture attached. When they are all charge up, the voltage seem to be within .30volts difference. But after discharging about 20-30ah.... Battery 1 and 4 voltage always drop significantly lower...
#1: 9.9v
#2: 11,9v
#3: 11.8v
#4: 9.9v
My actual wiring, instead of the negative going to battery 4 like the diagram, I have it connected to battery 2. But I can't imagine the distance of 6 inches would make that much of a difference?
DId I config it wrong, or is my battery dying? I am now thinking, maybe I should have parallels 2x together first, then series it? But everywhere I see online show series first than parallels.... But I also see Testa battery, they parallels all the cells first, then series?
thanks1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
jimmyaz : Are you aware that 10.5v is a dead battery? That is the point where you have removed all of the rated capacity.
You can drain them lower - just like you can rev your engine way past its rated limit - but there are consequences.....
I know that you said that they are within 0.30v from each other when charged. But what are the voltages that you are seeing when fully charged?
What brand of battery do you have and what was their manufacture date?
Marc
I always have more questions than answers. That's the nature of life. -
I think you have 2 bad batteries. One in each string. Shuffling positions around won't fix anything, Sorry
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
And a 0.30 volt difference between batteries is, in theory, the difference between a battery at 100% state of charge and at 70% state of charge (at least for typical flooded cell batteries, not so sure if AGM are quite the same). (basically assuming ~12.7 volt rest voltage--AGMs can read higher on their rest voltages).
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Well, add another mistake to my list for buying slightly used battery... One of them die after 2 months, so I had the supplier replaced with a different one, this may be why the whole bank is now screwed.
I'm now quite disappointed with AGM... but oh well, can't and won't spend more money on battery. Leaning toward them salvage Tesla Model s module. A guy locally here is parting out, stating the car only has 1050miles and selling each 24v 5kw module for 1000.00 ea... Price is not bad right? Considering it a 5kw pack and you can safely use 3kw.
If my inverter shut off is fixed set to 19.00 volts, is this ok for use with LI-ION? 3.2volts X 6 = 19.2, 3.2volts cut off for Li-Ion sound about right?
-
Doe the tesla battery management system come with the battery? (Voltage and temp monitor)
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
why is it being scrapped? How old is the car, when was it made? A friend with an S model is thinking about what to do if his battery shows weakness, probably in 2 years.. He has read that Tesla does NOT sell repair parts on the street, have to go to an authorized dealer!
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
The guy said its a wreck and battery is fine. Car was at 1050miles.
He said each module does have some type of circuit board but he said it require the main bms in order to work and probably need all the module to work. -
My personal opinion for what it's worth, is you are thinking beyond your current knowledge, dealing with sophisticated battery systems is the last thing you should be thinking of, these companies research and spend millions developing battery monitoring systems, more than likely they will not share their information and furthermore they would be unlikely to sell parts to complete anything you have in mind. Tesla builds cars, for now, they have other aspersions, but they will keep their cards close so as not to liberate technology, although they claim not to.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
I would venture a guess that you bought used batteries that were far more than "slightly" used. One failed in two months and now you feel that the rest have also failed. So now, you are "quite disappointed" with AGM batteries.
I see that you are contemplating buying a different type of used battery bank of untested condition. The type of battery is more specialized relative to the monitor/management system - but you will not likely get the entire control system with the batteries.
Seems like there might be a lesson in there somewhere.
Marc
I always have more questions than answers. That's the nature of life. -
Thank you for all the positive comment... lolz. This is simple a small test project and there's no reason to spend all my money on it. I am no idiot when it come to battery, I have been using Lithium Polymer in RC for 15 years now and have used a lot of batteries.
For the past couples day I undo the batteries, put them all in parallels then charged it all together. Hook it back but this time, I parallels first the two, then series the pack. I after testing, I believe this is a much better way to wire it.
After a few charged and discharge. I was able to sync the voltage much better...
They are both get to 13.10volts when fully charged. Both packs are within .05 volts from each other at rest now. But under 25amps load, there's a .10 volts difference.
-
I didn't mean to be negative - just cautious. Best of luck!
I always have more questions than answers. That's the nature of life. -
jimmyaz said:Anyone else guys? Would I better off wiring it like this?
My opinions, for what they are worth.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:
jimmyaz said:Anyone else guys? Would I better off wiring it like this?
My opinions, for what they are worth.
-
Even if they were new there would be imbalances during charge and discharge, so conventional wisdom would prevail. What Tesla is doing is completely different, they are using small cells to create a single large cell, then stringing these cells to create a battery, a lot more complex setup, but essentially it is still one battery, not multiple batteries fighting one onother.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed