SMA will it ever work?
Hi, I am having a dreadful experience with SMA and after nearly a year I am frankly considering returning the lot, claiming it is not fit for purpose and suing for my money back. I really don't want the hassle of this so am asking for any input you guys can give me. Application is off grid in rural Spain with the need for five hours a day of bore hole pump for irrigation. I'm using a Sunny Boy PV inverter, 3KW of panels, 290 AH Rolls AGM batteries at 48 V and a Sunny Island 6H. From day one I could not get a generator to work for more than a couple of minutes. SMA blamed the generator and its control. I tried five generators, all failed to connect. Finally SMA switched out the Sunny Island and the replacement worked with the generators no problem. Now I have two issues. The first is that state of charge never rises above 80% even though State of health is 100%. The Sunny Island seems to ignore charging current drop as a parameter to end charging instead using just time and also ignores the end of a full charge as an indication of a full battery. Without an accurate SOC I am worried about the long term health of my batteries. Secondly the AC coupling between the Sunny Boy and the Sunny Island is frequency controlled. When I turn off a load like the pump the Sunny Island bangs the frequency up with a time constant of about half a second. The Sunny Boy simply cannot respond that fast and so the frequncy hits the cut off point, the Sunny Boy switches off and then tries to connect again with the same result. I can fix this by adding a 800 W dummy load but should I really have to do this? The batteries draw 400 w or so at the state of charge this normally happens at with another 400 w going to the house. Any insight very welcome, thanks
Tagged:
Comments
If this is for your AGMs how does the Sunny system determine these 2 values? Is there an algorithm you can access?
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Mine are Telco purposed and I have extended the End Amps to 1 % of C-20 to max out the charge time as they were designed for Float service and it seems to work for these brutes. Also set Absorb to the max setting for the winter as it is - 25C these days, drop it back in the summer though.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Otherwise the SB output alone may be greater than the total remaining load.
The SI cannot drop its output below zero, so something has to cover the period before the SB responds to the frequency shift.
One solution is to run your pumps off VFDs (Variable Frequency Drives) and program the VHDs to ramp the pump speed down slowly at turn off instead of just shutting the load off instantly. FWIW this kind of ramped shutdown of the pumps will also be gentler on the pipes.
As a side benefit you will not have to supply a surge/startup load when turning a pump on. And as a further benefit, if it is one for you, you can run the pumps at reduced speed to save power if you want to operate over a longer time span.
Use one technology to keep the operation within the parameters that another technology requires.
If your sunnboy is the TL series it might be Bluetooth. You can connect a laptop and use the small "sunny explorer” software to set off grid mode.
Will
I agree. It stinks. My neighbors who use SMA also have the same issue. SMA seems to use a charging profile that rarely brings Battery SOC up to 100% each day even if the sun is blazing. Their belief is that 80% SOC is fine with the rare foray up to 95-100%.
I admit that there seems to be disagreement about the perfect FLA battery charging profile. But I think most FLA battery manufacturers would encourage off gridders to shoot for 100% daily.
SMA seems to be hardy and well engineered Kit, but their manuals are frustrating (perhaps the translation from German?), and they don't seem to be as well suited for off-gid application. My 2 cents.
There is an alternative flooded cell lead acid battery operation of cycling between 80 to 50% SoC, and recharging >90% once or twice a week. And I think one vendor that suggested once every 4 weeks. As long as the battery is cycling every day, there is the suggestion that they will not sulfate if the cells are actively cycled.
If the lead acid cells are not cycled--Then you do want to keep the battery fairly well charged to reduce sulfation.
I am not a battery expert/engineer/chemist by any means--Just things that I have read here over the last few years.
-Bill
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
For 24 volts, it would be 200 AH. And 12 volts would be 400 AH.
-Bill
The fix was to use the usb adapter in the sunny boy and tighten up the FSPC range(frequency shift power controll)
I had it start sooner and end sooner. I think i moved it 1 hz each way
Its a 10 kw array and would not throttle down soon enough so the sunny island would shoot up the hz and trip it off
Now the sunny boy can hold 23 watts
Before it was screwing up the lights,security sys and Ac thermostat
And not charging all the way
If you want higher SOC
Raise the vpc. A little and lower the cycltmful
From 14 days to 7.
None of this i would recommend. Just letting you know how to get it to 95-98%
100% you need to equalize
Sunny islands are by far the best. They're not for someone that does not know what there doing.
Find an installer that has put in and opperated 10-20 and you will need not worry.
Temporary system while i build house
8.5 kw pv, 70kwh's tesla model S batteries, 4548 xantrex
2 60A xw cc 1 80A outback cc. 25kw diesel gen
Looking at skybox for 20kw ac 18.5kw dc pv when done
I also have the same problem with not achieving a full Soc... never have after 5 years... also the problem is the invrfrequency raising to near 52hz and throttling back the input... 92's 95's is all i get. and Yes only ever see 100's when an Eq charge has run...
Not only that, the eq and full charges that are set to run are constantly reset so that they never run anyway!!!!....
My installer and i are in constant comms with Sma .... still trying to figure out the fix.. i reckon rhino66 is onto something...
If this thread is still active id greatly appreciate some feedback...
Cheers from Australia all...
stay charged
48 x 265w Canadian Panels
2x Sunny Boy 5000 tl-21
Sunny Island 8.0-11
2v Gel Toyo 600a/h 48v
8kva Remote start Petrol Gen.
Welcome to the forum
Regarding the frequency drive, you may want to check for harmonic distortion caused by the drive itself, thus upsetting the inverter, this requires a power quality analyzer. There are filters however they generally/all? are 3 phase, one way to isolate harmonics from the inverter is to use a 1:1 (230V - 230V ) transformer of suitable kVA on the line side as hamonics cannot migrate through but rather manifest as heat in the core, depending on duty cycle cooling may be required for the transformer.
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Yes harmonic disturbance was one possibility that did come up in the list of possible causes... we will look into that...my small mig welder also trips the sunny boys off as well.. not everytime but around 50%.. also the timer on the oven has never kept time. . All appliances seem to work fine after 5 years so im happy in that respect. . I think all these smaller issues are pointing in the one direction though. .. many thanks for your reply..
48 x 265w Canadian Panels
2x Sunny Boy 5000 tl-21
Sunny Island 8.0-11
2v Gel Toyo 600a/h 48v
8kva Remote start Petrol Gen.
48 x 265w Canadian Panels
2x Sunny Boy 5000 tl-21
Sunny Island 8.0-11
2v Gel Toyo 600a/h 48v
8kva Remote start Petrol Gen.