Proper Electrolyte Level
pyintheye
Registered Users Posts: 35 ✭✭
I have been working to get my SOC back to factory specs, following the advise on this and other forums. Specifically raising AB time and AB voltage. My SG's are close to 1.27 but the fluid level is about a 1/2 inch below where the manufacturer wants the fluid to be. Do I add more water, dilute the SG's and keep charging, OR is the fluid already at the "right" level?
Thanks.
Thanks.
Midnite Panel Box for MS4448PAE, FM60- 720w, FM80- 2340w, 8 Trojan L16H AC- 48V, NH600 Turbine, DHW 2000w opp/div load.
You know the answer ...
"... the fluid level is about a 1/2 inch below where the manufacturer wants the fluid to be ..."
Hey mvasmvas said:You know the answer ...
Too early in the year to be gob smacked like that. But if it's that simple, I like that.
Midnite Panel Box for MS4448PAE, FM60- 720w, FM80- 2340w, 8 Trojan L16H AC- 48V, NH600 Turbine, DHW 2000w opp/div load. -
Assuming the battery is fully charged and the SG is as high as it will rise, this would be the time to add water to the correct level. Note: Adding water will lower lower SG readings as the water and acid will be stratified, an EQ will mix the electrolyte and bring the water into solution. That being said the EQ will raise the temperature of the electrolyte and SG readings will be offset and will need to be compensated for, the EQ voltage should also be reduced as temperature of the battery rises using a remote temperature sensor. After cooling and no loads, say overnight, take your SG readings. Alway follow the manufacturers recommendations as not all batteries are alike, age is another factor which affects readings.
http://batteryuniversity.com/learn/article/how_to_measure_state_of_charge1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS