2x100W solar panels in parallel issue
rafi
Registered Users Posts: 2 ✭
Hello!
I have an issue with the solar system I am trying to install in my RV. I purchased 2x100W panels from HQST and a morningstar 30 amp charge controller (with lcd screen).
I installed the solar panels in parallel to get the same 12V voltage and supposedly add the amps from both panels.
THe problem is I am getting right now with both panel a reading of about 4 amps jumping up and down of solar amp. It's not a lot and the jumping around seems weird (sun is shining 100% right now).
When i disconnect 1 panel from the pair, I get a very stable 5.2 AMPs on the screen. (both panels outputs about 5.2 amps on their own)
What could be wrong ? I dont get it I used standard Y MC4 connectors to link them up, and i tried other Y connectors too without any changes.
Thank you!!
I have an issue with the solar system I am trying to install in my RV. I purchased 2x100W panels from HQST and a morningstar 30 amp charge controller (with lcd screen).
I installed the solar panels in parallel to get the same 12V voltage and supposedly add the amps from both panels.
THe problem is I am getting right now with both panel a reading of about 4 amps jumping up and down of solar amp. It's not a lot and the jumping around seems weird (sun is shining 100% right now).
When i disconnect 1 panel from the pair, I get a very stable 5.2 AMPs on the screen. (both panels outputs about 5.2 amps on their own)
What could be wrong ? I dont get it I used standard Y MC4 connectors to link them up, and i tried other Y connectors too without any changes.
Thank you!!
Comments
-
Does it read 5amps regardless of which panel you have connected?
You did connect a battery first? Could the battery be nearing fully charged?
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Yes battery is connected. Possible that the battery might be charged soon although the charging light is blinking, manual says it blinks when charging (PWM regulation), and stays on when near fully charged.
I tried to look for the voltage input on the charge controller (full sun, winter) : with 1 panel 18.5V, with 2 in parallel 19.7
Specs for my panel: Optimum Voltage : 18.5
open circuit : 22.5V
100W
hope it helps -
I think that explains it, I think you are just near fully charged and the battery taking less input. 19.7 is likely above your VMP so reading between VMP and VOC might indicat it switching rapidly.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
what loads are you going to run tonight?
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
rafi said:Yes battery is connected. Possible that the battery might be charged soon although the charging light is blinking, manual says it blinks when charging (PWM regulation), and stays on when near fully charged.
I tried to look for the voltage input on the charge controller (full sun, winter) : with 1 panel 18.5V, with 2 in parallel 19.7
Specs for my panel: Optimum Voltage : 18.5
open circuit : 22.5V
100W
hope it helps
Do you have any loads connected when you are conducting this test?
When you state the current is fluctuating, is the PWM % display fluctuating correspondingly ie 45% 70%?
Did you set the voltage with the dip switchs 2&3 or did you leave it in auto select?
Most importantly did you connect the battery first, let the start sequence GYR led's flash one by one, before connecting solar?
1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed