Questions regarding 12 volt loads on a 24v system? Ultracapacitors?

PNW_Steve
Registered Users Posts: 79 ✭✭
Hello Everyone,
As I am tweaking the design for my bus electrical system I have begun to consider going 24v on my house batteries. My single largest (by far) DC load will be the inverter. My lighting will be LED and I won't have any major DC appliances. So, I expect my 12v loads should never exceed 30A.
I have looked at various options for supporting 12v loads from my 24v bank and am not excited about the 24/12v converters.
I did see mention of someone using a 30amp MPPT charge controller to charge a separate 12v battery from the 24v battery bank. That idea caught my eye but adding another battery opens a can of worms.
Could I follow that example but substitute something like this for the 12v battery:
I will not mount a battery inside the living space and I would have to build a new support & battery box on the frame rail to place one outside. From what I can see, I could mount this in my electrical cabinet where my charge controller, inverter etc are.
Any thoughts?
Thanks.
S.
As I am tweaking the design for my bus electrical system I have begun to consider going 24v on my house batteries. My single largest (by far) DC load will be the inverter. My lighting will be LED and I won't have any major DC appliances. So, I expect my 12v loads should never exceed 30A.
I have looked at various options for supporting 12v loads from my 24v bank and am not excited about the 24/12v converters.
I did see mention of someone using a 30amp MPPT charge controller to charge a separate 12v battery from the 24v battery bank. That idea caught my eye but adding another battery opens a can of worms.
Could I follow that example but substitute something like this for the 12v battery:
coolestore® 16V 83F Ultracapacitor Engine Battery Starter Booster Car Ultra/Super Capacitor
https://www.amazon.com/coolestore®-Ultracapacitor-Battery-Starter-Capacitor/dp/B00PU4J7GYI will not mount a battery inside the living space and I would have to build a new support & battery box on the frame rail to place one outside. From what I can see, I could mount this in my electrical cabinet where my charge controller, inverter etc are.
Any thoughts?
Thanks.
S.
Comments
-
The simplest is the DC DC converter, have used them extensively on 24V Land Cruiser's to run stereo systems, got them from Samlex, that capacitor is just an electrolytic capacitor which dumps it's charge for a short duration to prevent voltage sags, at least that is the theroy. As I always caution, NEVER be tempted to tap off one 12V battery in a 24V string as this WILL dammage one if not both batteries1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:The simplest is the DC DC converter, have used them extensively on 24V Land Cruiser's to run stereo systems, got them from Samlex, that capacitor is just an electrolytic capacitor which dumps it's charge for a short duration to prevent voltage sags, at least that is the theroy. As I always caution, NEVER be tempted to tap off one 12V battery in a 24V string as this WILL dammage one if not both batteries
Any thoughts regarding using an MPPT charge controller feeding an ultracapacitor bank to support 12v loads?
Thanks again. -
I would suggest that using an ultra capacitor on a 12 volt battery is both expensive, unnecessary, and risky.
Expensive... A super cap stores very little energy vs a true battery bank. They are suggested for cars audio systems that are crazy loud and when you have ripple current in the 100's of Hz range (bass) to provide momentary peak current. In general, a large enough bank to feed needed power to operate the inverter/loads for 2+ days an 50% maximum depth of discharge is large enough to supply needed surge current. True super caps do not have a very long life--Generally a few years for the ones I have researched.
Unnecessary... The super cap for audio is just to carry through power for a 1/2 cycle of audio or a few 1/10'ths to 1/100'ths of a second. An inverter needs to supply surge current for multiple cycles lasting upwards of several seconds--Supplying power for 1/10 second "extra" is not going to really do much to start a well pump motor.
Risky... A super cap into a dead short can do massive amount of damage. The wiring and fusing/breakers run the risk of simply vaporizing instead of stopping the current. Particularity if the system is >12 volt battery bus (~12 volts and below, sustaining an arc is not very easy--Over ~12 volts, you have an arc welder).BB. said:Re: Using Deep Cycle Battery as Car Starting Battery
Be very careful with "true" super caps... They usually only have a few year life and are very sensitive to over voltage. Also, a dead short with a super cap can be hugely more dangerous than with a lead acid battery (which can be scary enough).
And the actual amount of stored power (relative to a lead acid) is relatively low:
Looking at your numbers... Say you can crank an engine for ~1 minute at ~100 amps:
100 amps * 1 minute * 1/60 minutes per hour = 1.67 Amp*Hour (@ 12 volt) "useful" stored energy
-Bill
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Why are you thinking of going to 24v in the first place? Do you have concerns about wire size to a load? Want bigger inverter?Off-grid.
Main daytime system ~4kw panels into 2xMNClassic150 370ah 48v bank 2xOutback 3548 inverter 120v + 240v autotransformer
Night system ~1kw panels into 1xMNClassic150 700ah 12v bank morningstar 300w inverter -
PNW_Steve said:Thanks for that.
Any thoughts regarding using an MPPT charge controller feeding an ultracapacitor bank to support 12v loads?
Thanks again.
The cost of the "super capacitor " is around the price of a 12v battery which has a stable voltage, larger capacity and will work with a controller, so for this reason I would recommend the battery.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:The charge controller would probably charge the capacitor in a milisecond with no load, and the capacitor would discharge rapidly when something is turned on, prompting the controller to try and charge, after a delay (takes a little time to recognize the voltage drop) and most likely end up with a series of pulses, which would most likely damage the controller and load. This is my theroy as I wouldn't even entertain putting it to a test.
The cost of the "super capacitor " is around the price of a 12v battery which has a stable voltage, larger capacity and will work with a controller, so for this reason I would recommend the battery.
I have seen a number of people replace (as an experiment) their starting battery with an ultracapacitor array with reasonable success. I have no want to support a load drawing near that much current. Primarily 12v LED lights, cell & laptop charger. If I am pulling a relatively steady 10-20A load from a source that is capable of providing enough energy to start a car I would expect at least a few minutes of run time not milliseconds or seconds.
The ultracapacitor "battery replacements" that I have been looking at cost about 1.5 times what a decent group 27 battery. Battery lifespan= 2-3 years.
If I add a battery I will need to build a carrier attached to a frame rail and put an access door in to get to it. I will NOT place a vented lead acid battery in my living space. The cost of the longer battery cables and the fabrication of the mount etc. far exceeds the cost of the ultracapacitor that CAN be mounted in the living space.
As far as the instantaneous current availability, I would think that fusing both legs (12v+/12v-) with a 100A fast acting fuse would provide adequate protection for my application. Am I mistaken? Obviously a catastrophic short in a piece of gear could allow damage to occur to the gear before the fuse blows with either the battery or the ultracapacitor.
Lastly, If the MPPT charger won't play well with the ultracapacitor the the idea is useless.... -
You pretty much need a "minimum size" battery bank with a typical MPPT type charge controller. If you have too small of bank, it is possible for the MPPT controller to over voltage the capacitor/small bank (part of the MPPT cycle for many controllers is to pull as much power from the solar array and pump it into the battery bank to figure out the Vmp*Imp=Pmp equation.
Solar charge controllers (and even car alternators) really use the battery bank to "buffer" and hold the DC bus voltage within nominal range.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
PNW_Steve said:
I have seen a number of people replace (as an experiment) their starting battery with an ultracapacitor array with reasonable success. I have no want to support a load drawing near that much current. Primarily 12v LED lights, cell & laptop charger. If I am pulling a relatively steady 10-20A load from a source that is capable of providing enough energy to start a car I would expect at least a few minutes of run time not milliseconds or seconds.Lastly, If the MPPT charger won't play well with the ultracapacitor the the idea is useless....Once the capacitor is charged it will work fine. If you try to start into a discharged ultracap the MPPT won't even turn on; you'd have to charge it manually to some reasonable voltage first.
-
For this application (charging a supercap), I would NOT use a MPPT controller as a down converter. I'd use a 3 terminal switching regulator or DC-DC supply http://www.mouser.com/Power/DC-DC-Converters/Non-Isolated-DC-DC-Converters
some 3A for $25 or whatever you need to maintain your load requirements. No worries about the 12V side going so low the MPPT shuts off.
You may need to pre-charge the 12v super cap via a automotive light bulb and voltmeter to not have the supply current limit for the initial powerup.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:For this application (charging a supercap), I would NOT use a MPPT controller as a down converter. I'd use a 3 terminal switching regulator or DC-DC supply http://www.mouser.com/Power/DC-DC-Converters/Non-Isolated-DC-DC-Converters
some 3A for $25 or whatever you need to maintain your load requirements. No worries about the 12V side going so low the MPPT shuts off.
You may need to pre-charge the 12v super cap via a automotive light bulb and voltmeter to not have the supply current limit for the initial powerup.
-
If you are concerned about several loads piling on at the same time, split it up and use several smaller DC-DC converters
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I use a 1.o farad capacitor in my solar system hasent blown up yet takes the load of my inverter and batterys but im going to try a car audio battery on my primary system think the car audio battery will be safe to use with deep cycle battery and 4000watt inverter i got a 12000 watt on order
-
I us a 60amp pwm controler and marine rv deepcycle battery with 3 100 watt panels but my 1farad capaciter handels startup loads on microwave and stuff 1000 watts and below but im going to try a car audio battery capaciter
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 195 Solar Information links & sources, event announcements
- 892 Solar Product Reviews & Opinions
- 255 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 427 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 616 Discussion Forums/Café
- 309 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed