Solar Panels 400ft From House....19360 KW system with 3 SMA SB 7.0-US inverters
Dan_C
Registered Users Posts: 2 ✭
I'm trying to figure out how to get the power from my panels back to my house, with acceptable Voltage drop.
I'm wondering if I can run DC back to house with 3 x 2 Pairs of 4 AWG aluminum then hook to inverters, or should I have a breaker box and inverters out with solar panels and run the AC back on 350mm wire?......Thanks for the help in advance....Dan
I'm wondering if I can run DC back to house with 3 x 2 Pairs of 4 AWG aluminum then hook to inverters, or should I have a breaker box and inverters out with solar panels and run the AC back on 350mm wire?......Thanks for the help in advance....Dan
Comments
-
Your dc runs could be much higher voltage.
Each of your 3 arrays would be connected to roughly 6500w.
Run that at something like 450v. Would leave you with about 14.5 amps to move at peak power.(per array)
A pair of 10awg gauge copper wire could do that.
http://www.calculator.net/voltage-drop-calculator.html
At ac transmission you would be transmitting at 240v
That is 80 amps at peak. 1/0 should handle that approximately 100kmils
Price your options. Will you ever need or want ac power out by the array? If so transmitting via ac maybe benificial. -
Thanks for helping me on this.
So, I was trying to stay with alumninum for the 400ft long, and in order to maintain 3% Voltage drop or less, the tools were saying I needed like #250 aluminum or like 4/0 copper (which looks really expensive).
Is the 3% voltage drop the real target (as all the tools seem to say so) or can I go higher?
Here is output of the voltage drop tool..Results
1 conductors per phase utilizing a #250 Aluminum conductor will limit the voltage drop to 2.64% or less when supplying 80.0 amps for 400 feet on a 240 volt system.For Engineering Information Only:205.0 Amps Rated ampacity of selected conductor0.09 Ohms Resistance (Ohms per 1000 feet)0.041 Ohms Reactance (Ohms per 1000 feet)7.199999999999999 volts maximum allowable voltage drop at 3%6.328. Actual voltage drop loss at 2.64% for the circuit0.9 Power Factor
-
For long runs, it makes economic sense to use higher voltage drops than for short runs.
I am available for custom hardware/firmware development
-
AFAIK the 3% was established based on the (old) High cost of PV panels say 10 or more years ago.... So now with cheap PV prices, you need to do a calculation to see what the cost of losing 3% is vs the cost of adding another cheaper PV to send more watts to the inverter(s)....
Agree with all comments about sending higher DC current.
hth
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
I get 1 awg copper would get you a 3.3% drop at 80 amps 240v
But a more realistic 65 amps 2awg copper gives a 3.39% drop
2/0 awg aluminum gives a drop of 3.28% at 80amps 240v
These are much smaller than what you thought you may need. But I am cheap and even 2awg is expensive to me.
3 pairs of 10awg cabling would do your 3 arrays.
So calculate rate of 1200ft [400x3] 2 conductors. 10awg.
Vs
400ft of 2
Only reason I see to do ac transmission is if you need ac power out that way anyway.
I am going to do an array at a similiar distance yours is. Mine will do ac transmission because I need power out there anyway.
-
I would lean toward HV DC transmission, and if you need AC out there, drop in some 1/2 PVC and pull AC back out to there while you have a trench open. I think AC & DC can go in the same trench, but not in the same conduit.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed