Looks like hot and neutral are reversed in the new inverter...
softdown
Solar Expert Posts: 3,896 ✭✭✭✭
Using an Ideal line checker, I got indicator lights showing that the hot and neutral are reversed at the end of the newest line. Switched them back and forth no less than three times!
Then I plugged the line checker into the outputs on the Cotek 1500 watt PSW inverter. Got the same reading.....hot and neutral are reversed.
It is amazingly easy for assembly line mistakes to be made. A perfect high tech product may be the exception, not the rule.
1) I think I know why I got such a "good buy" on a few of these inverters.
2) It doesn't seem to effect normal operations. Or does it? This concern is the primary reason for this thread.
Then I plugged the line checker into the outputs on the Cotek 1500 watt PSW inverter. Got the same reading.....hot and neutral are reversed.
It is amazingly easy for assembly line mistakes to be made. A perfect high tech product may be the exception, not the rule.
1) I think I know why I got such a "good buy" on a few of these inverters.
2) It doesn't seem to effect normal operations. Or does it? This concern is the primary reason for this thread.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
Comments
-
In theory, all you need to do is reverse the Back and White wires going to the outlets (you should phase tape the "original wires" to keep everything straight.
Also, you may be able to go into the inverter's AC panel and simply move the ground bond to the white/neutral wiring (depends on what was done wrong in the inverter--But it should be easy to fix). Or, you can "cut the ground bond" in the inverter, and ground bond in your AC main panel.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
BB. said:In theory, all you need to do is reverse the Back and White wires going to the outlets (you should phase tape the "original wires" to keep everything straight.
Also, you may be able to go into the inverter's AC panel and simply move the ground bond to the white/neutral wiring (depends on what was done wrong in the inverter--But it should be easy to fix). Or, you can "cut the ground bond" in the inverter, and ground bond in your AC main panel.
-Bill
It seems the only problem with this reversed polarity is the increased shock hazard....which I have already experienced. Fortunately I have a high tolerance for shock....perhaps from being shocked a few dozen times. That comes from working with water and electricity all the time. Standing in some salt water may be the final shock however. Pure water isn't bad....saltwater is the worst for carrying electricity (that leaps from solid to solid).
This new solar array does not go to any AC main panel. This second string is dedicated to a couple freezers and refrigerators. It is still a work in progress with three separate PV strings using three charge controllers.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Don't laugh off 120/240 VAC shocks... Today a 120 VAC hit will get you a doctor's visit and a 240+ VAC hit will get you an overnight stay in the hospital (electricians have died hours after a hit) with California OSHA (as I understand from a friend).
Grounding is the sum of many different issues (shock grounding, lightning grounding, the ability to trip a single breaker to ground/neutral vs needing paired breakers for floating systems, starting florescent tube fixtures, flame sensing on stove/water heater with spark ignition, etc.).
If you have "typical" TSW/PSW AC inverter--The AC output is isolated from the DC input. So, the "neutral bonding" is simply a connection from the "white wire" output of the transformer to the AC inverter chassis. What you do from there (typically ground the AC chassis to the ground rod/cold water pipe) finishes the AC grounding side.
On the DC grounding side, I like a 6 awg from battery negative bus to the same ground rod/cold water pipe.
If you have an MSW inverter (modified sine/square wave), the AC output should not be ground referenced White wire bonded to ground (will let magic smoke out of AC inverter)--Both wires are "hot" relative to the DC battery bus--And will show Neutral and Hot as "hot" relative to the DC battery bank ground (and how it looks to AC green wire ground and DC green wire ground connections.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Technically without grounding the inverter and one leg of the output you will never have a neutral, it is unlikely a manufacturer error .see arrachment1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:Technically without grounding the inverter and one leg of the output you will never have a neutral, it is unlikely a manufacturer error .see arrachment
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Same ground should be OK, the diagram is for graphical purposes, a common ground would probably be preferred as everything would be bonded to a common point.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
Grounding the battery and the inverter did not fix the problem. Wondering about an efficient way to ground an output leg. Grounding the inverter ought to have grounded the ground wire.
The vast majority of the people will simply use the inverter as is...many will ground it, others will not. The inverter has two 120 volt outlets. It supplies 120.3 volts at the end of an ~120' run with 12awg.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
What model is the inverter and if it is a US market unit, it should have a GFCI outlet.1500W, 6× Schutten 250W Poly panels , Schneider MPPT 60 150 CC, Schneider SW 2524 inverter, 400Ah LFP 24V nominal battery with Battery Bodyguard BMS
Second system 1890W 3 × 300W No name brand poly, 3×330 Sunsolar Poly panels, Morningstar TS 60 PWM controller, no name 2000W inverter 400Ah LFP 24V nominal battery with Daly BMS, used for water pumping and day time air conditioning.
5Kw Yanmar clone single cylinder air cooled diesel generator for rare emergency charging and welding. -
mcgivor said:What model is the inverter and if it is a US market unit, it should have a GFCI outlet.
It is also now possible that I reversed hot and neutral while trying to fix the problem.....three times.
First Bank:16 180 watt Grape Solar with FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries -
Wondered if anyone else has found this to happen? I have a Vevor 2500w Inverter without an external ground lug. I opened the case to look for one and saw that the hot and neutral are reversed on one of the three outlets. This is by design (see attached) or how the circuit board was built. The orientation of the 3 outlets are the same externally. Is this OK? What are the dangers of leaving it like this?
-
I had an inverter where the ground pin was connected to a 100k resistor and then to the case. Enough to drain off any capacitive leakage that might cause a tingle. But, not enough to damage the inverter if the device had a short to ground.
Recently got a triac speed control and it was switched and fused in the neutral. It also carried the ground to the output socket without grounding the metal case. The AC power cord had the international color code for indicating hot and neutral except that they were reversed. I'm pretty sure the Chinese company bought these defective cables because they were cheaper.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems