What size pure-sign-wave 12 volt inverter to run
10 laptop computers
3 Desktop Computers
3 Floor standing domestic fans
1 Internet Router
and 10 x 5 watt LED lights
10 laptop computers
3 Desktop Computers
3 Floor standing domestic fans
1 Internet Router
and 10 x 5 watt LED lights
Comments
-
Too many variables, Desktops can run 150-1500 watts, floor fans 50-300+, Laptops from 25-200+Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
It's going to be too large for a 12V system, Start looking at 24V gear
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
I don't mean to sound like a smartass but I would start by adding up the watts that are usually listed on the device power block or name plate.Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M
-
Get a Kill-a-Watt type meter... They should be pretty common now almost anywhere for your power needs (120/230/50hz/60hz).
http://www.solar-electric.com/kiacpomome.html
And you will want to conserve as much power as possible--Especially if you are looking at solar power.
However, that does raise the question--Is this going to be a UPS type system instead (AC mains -> battery bank -> AC inverter) used to provide power for ~4 hours per day during afternoon blackouts?
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yes you are right, this set-up is going to be charged by a mains battery charger and is a back-up system when there is a power outage. The frequency is such that probably even a 10 amp charger has enough time to re-coup the batteries.
-
In general, I would suggest that you look at a 5% minimum rate of charge for the battery bank (if using AGM or GEL).
And, you have to decide on the type of batteries you want to use... If your power outages are rare, then a "float service" battery type (used for UPS systems) would be a better choice... The downside that these batteries, if cycled deeply, will not have very good cycle life. From my limited experience, I would suggest replacing batteries of this type (typically GEL and AGM) every two years, or after a couple of deep cycle events.
Note, when designing a solar power system, we suggest using ~1/4 of the battery bank's power per day... For a UPS system, the banks are designed to support the systems for ~15 minutes, so the battery bank may have 30 minute capacity (C*2 discharge rate).
This keeps your battery bank "small" and relatively cheap to replace every 2 years (for reliability).
If, however, you have "scheduled" power failures every weekday afternoon, you are probably better off designing this as we would for an off grid system. Design the battery bank to meet both conditions:- 8-20 hour discharge rate (nominal battery bank current draw).
- Maximum draw on battery bank 5 hour discharge rate (minutes to 1 hour). And 2.5 hour maximum draw rate for surge current (seconds, starting water pump, fans, etc.).
- 25% to 50% draw of battery bank capacity for "afternoon power failure" (battery bank should be 2-4x daily use AH capacity).
- Suggest 10% rate of charge--Deep cycle batteries may do better with >5% rate of charge.
And there is always the question about long term power outages (days)--Solar/fuel based genset, etc...
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
I shall be posing a new question which is an expansion of the previous topic.
Unfortunately it will seem even more unspecific as to exact consumption.
I thank you for your input thus far which is helping toward my provision of power in Cambodia.
-
Having been through power failures last year, here is a quick summary of what you may need for a UPS:
10 laptop computers - average of 100w = 1000w
3 Desktop Computers - average them on 250w = 750w
3 Floor standing domestic fans - average 50w = 150w
1 Internet Router - negligible
and 10 x 5 watt LED lights - 50w
Total +-2000w
You do not want to run inverter at 100%, and users are going to add more stuff, so start at a 3000w pure sine wave inverter.
Then to calc how many batteries you need: How long do you want to power the load for?
Make SURE you take into consideration that you do NOT want to drain the batteries below 50% DOD.
Now that you know how many batteries AH you need, decided 48v or 24v for the inverter, for it impacts on battery costs.
Type of batteries, I want to add to Bill posts, is that UPS inverters are not too clever with charging batts, generally speaking.
So do not go for the expensive deep cycle solar batteries. 99% of the time batteries in UPS'es are just sitting there.
Get maintenance free 'deep cycle' batteries. They last about 2-4 years depending on usage, but must NEVER be drained, ever, below 50% DOD.
5kVA Victron Multiplus II, 5.2kW array, 14kWh DIYLifepo4 bank, all grid-tied.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed