Determining the Wind Rating for a DIY Solar Ground Mount
Hey Guys!
I'm constructing a ground mount for my solar panel that is similar to the one found in the video. While putting the system in pretty straightforward, I still live in Florida, so I want to be reasonably sure that the system can withstand some of the weather that we get here. The system is not a grid tie-in, nor does it need to signed off by PE; but I would still like to know what kind of wind rating my system will have (I would like for the system to be able to withstand at least 150 MPH winds). I have an undergraduate degree in Mechanical Engineering, but it's been awhile since I've worked with any structural equations. Do you guys have any recommendations on how to proceed?
    soil analysis to see how stable it is when wet. Then you size the anchors to hold the wind load in n soil You may need to hire an engineer to check or school you in the method. I'm an EE and don't know the mech side too well.
    Dave Angelini Solar Expert Posts: 7,094 ✭✭✭✭✭✭
    A test commonly used is to calculate the wind force and then weigh the mount down and check the deflection. There should be very little. The 2 inch pipe should not have holes but clamps. At least I have never seen holes in a pipe on the mounts of Pro Solar, UniRac. DPW, or Array Technology.
    Unless you have a very large diameter vertical pipe--I would be wanting to see diagonal bracing.
    To give yourself an idea of what level of forces you are looking at:
    http://www.solar-electric.com/lib/wind-sun/SOLARWORLD_280_4.0_FRAME_%2833MM%29.pdf
    Design Loads*
    Two rail system
    113 psf downward
    64 psf upward
    Design Loads*
    Three rail system
    178 psf downward
    64 psf upward
    Design Loads*
    Edge mounting
    178 psf downward
    41 psf upward
    * Please refer to the Sunmodule installation instructions for the details associated with these load cases.
    That 280 Watt panel is about 11.85 square feet. A 64psf loading would be 758 lbs per panel. Put three of those on a rack and that is the equivalent of hanging your car the structure.
    And given that a typical design factor of 10x (the structure has to support ~10x more design load before failure)--You can see that this can add up really quickly (~20,000 lbs to "break" the mount for 3 panels).
    -Bill.