Wire sizing for battery interconnecting cables - 2/0 or 4/0
Hairfarm
Solar Expert Posts: 225 ✭✭✭
My battery bank will be 12VDC. Six, 6-volt 225ah batteries wired for 12 volts @ 675ah. My inverter is a 2000W Prosine 2.0.
The formula I'm using is 2000w / 12VDC = 166A. 2/0 should be able to handle that. That said, should I use 2/0 or 4/0 for wiring the batteries together? Am I missing something?
FYI, I'll be using 4/0 wire from the battery bank to the inverter.
thanks,
The formula I'm using is 2000w / 12VDC = 166A. 2/0 should be able to handle that. That said, should I use 2/0 or 4/0 for wiring the batteries together? Am I missing something?
FYI, I'll be using 4/0 wire from the battery bank to the inverter.
thanks,
Comments
-
For one or two parallel strings, I would use full size cable for batteries. For three our more parallel strings you could reduce by 1/2 cross sectional area (+3 awg gauges smaller).
Again, my personal opinion.
Going to fuse each string? (Three or more parallel strings).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Bill, I'll be using three parallel strings.For three our more parallel strings you could reduce by 1/2 cross sectional area (+3 awg gauges smaller).
I hadn't considered fusing the battery cables, but it wouldn't be a bad idea. -
Well--If you want to put me on the hot seat... First the inverter calculation:
- 2,000 Watt continuous * 1/010.5 volts cutoff * 1/0.85 AC Inverter eff * 1.25 NEC derating for wire/breakers = 280 Amp branch circuit rating for full load continuous
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
Between 250 and 400 cmil wire (or paralleled smaller cables).
If you use marine ratings:
http://www.boatus.com/boattech/articles/choosing-cables-and-terminals.asp
1/0 or 2/0 cable minimum...
So--If you use Marine wiring standards, 2/0 would be OK for main or battery string wiring... You should double check the voltage drop using a voltage drop calculator... Recommend you try for 0.5 volt drop maximum for Inverter and 0.1 to 0.05 for charging.
http://www.calculator.net/voltage-drop-calculator.html
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Thanks for your great info Bill. I will keep this in mind when setting up my battery system.
-
I think in a previous thread you spoke of this.
What might be missing is voltage drop over distance. I believe Prosine will have proper sizing in there manual for different distances. at higher amps voltage drop can be substantial particularly for low voltage systems.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
......166A. 2/0 should be able to handle that.....,
But can a string of 225A batteries (x3) handle that for very long ? 55A per string ? IF it's evenly split amongst the batteries. More than a couple minutes, and the batteries are going to start to sag under a 50a load.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed