Re: Old Trace 2012 inverter/charger ??'s
The generator would not limit the charging capacity of the inverter. If the gen was overloaded it would just shut down completely. Having a 120 VAC input means the inverter-charger will work up to the current limit of the input.
50 Amps @ 12 Volts is 600 Watts. On the 120 Volt side that's a mere 5-6 Amps (expect some losses) and it wouldn't phase even a Honda EU1000i (800 Watt gen).
If the AC Voltage is too low the inverter will just drop it, as per previous post.
Now if the inverter is programmed with a maximum AC IN of 5 Amps and the charger is set to 120 Amps the charger will be limited because it won't allow the higher setting. How exactly the Trace would deal with that I don't know. Charger maximum current always has to be lower than AC IN maximum current (expressed in like units). -
Re: Old Trace 2012 inverter/charger ??'s
one more ? for Coot, i see u have a OB 3524, seems to be 85a charger, does your EU2000 run the charger?? If so with only 232 amp hrs of batt. do u limit charger to lower amps when required to use it4x240w panels,Classic 150 CC, 4x380AHR L16's, antique Trace 12V inverter -
Re: Old Trace 2012 inverter/charger ??'sone more ? for Coot, i see u have a OB 3524, seems to be 85a charger, does your EU2000 run the charger??
Yes it does. No problem at all. Especially since I have a 232 Amp hour battery bank so the charger doesn't run at 85 Amps!Nice thing about the Outback chargers: they start at zero and ramp up to their max setting instead of starting at full power which can be very hard on a small generator.
If you actually tried to pull 85 Amps @ 24 Volts the EU2000 would not do it because it is only a 1600 Watt gen and the power demand would be over 2kW. -
Re: Old Trace 2012 inverter/charger ??'s
By the way, for a sine wave to have 164 volts peak:
164 volts / srt(2) = 116 VAC (sign wave, RMS--Root Mean Square--True RMS reading DMM)
But as Marc/Cariboocoot says, some generators tend to sag on the peak AC voltage/AC current load from the battery charger.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed