Conext xw 4548 with -48v battery bank
11JAGAN
Solar Expert Posts: 34 ✭✭
The requirement is for remote telecom application
current scenario
There will be two generator (complete off grid) each run twelve hours a day to take care of 3500w load (combination of 230Vac and -48Vdc load)
if i stop the generator the the ipms battery bank will take care of -48 Vdc load
but the AC load will be off
i am searching a solution for it
Can i use conext XW 4548 with a positive grounded battery bank?
if so how can i do that?
or any other inverter can function at -48Vdc
Thanks in advance
current scenario
Thanks in advance
Re: Conext xw 4548 with -48v battery bank
I don't know about + gnd battery bank, but why can't the 4548 inverter/charger, actually invert and provide the 3500w AC too ?
And I'd throw in at least one more generator, because you are going to be running those 2 into the dirt really quick. The $300 big box store generators have a 500 hour design life, you should be looking at a small water cooled diesel, I think Yamar engines are used in them. Kubota makes one (7Kw) too.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
The isolated power modules(IPMS) is a charger with a battery bank (which is positive grounded).
i don't want additional battery bank ,since the battery bank inside ipms is sufficient for me.
i just want an inverter which should operate at -48v dc -
Try this and see if it suits you. Ck with Schneider customer service if in doubt about a XW.
http://legacy.outbackpower.com/pdf/tech_notes/Positive_Grounding_of_OutBack_Devices_Rev2.pdf -
Just be careful with any I/O (communications, RS 232, RS 422, i/o ports). They will usually be referenced to the negative battery bus voltage (i.e., that will be "signal ground"). If you connect to external/other equipment--The shifted "positive" ground can blow wiring between devices with mix positive/negative grounds.
Some interfaces, like 10/100/1,000 BaseT Internet, are (usually) transformer isolated interfaces and a good way to communicate between positive and negative ground referenced devices.
i am not going to use any communication device in this
any other issues -
Re: Conext xw 4548 with -48v battery banki am not going to use any communication device in this
any other issues
How do you program it? The Combox or SystemControlPanel run off the Xanbus. I don't know if it is isolated or not.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
- 234 Forum & Website