Use of AFCI/GFCI breakers in Off-grid system

I'm wondering if folks can weigh in on their experience with AFCI or GFCI breakers (not receptacles, breakers) in an off-grid system on the AC side of things. I've seen combo AFCI/GFCI breakers available for sale, but am wondering if they are more trouble (nuisance tripping, etc.) than they're worth. Anyone care to share their real-world experience with these combo AFCI/GFCI breakers (or just AFCI breakers)?

I will have an off-grid system (no grid tie!) and will have a Magnum MS-4448PAE (120v/240v) inverter that will be connected to a standard AC panel (i.e. Load center), which feeds various home-run circuits throughout the house (no shared neutrals). Right now I have no 240volt circuits, but could in the future. Nothing more than 20 amp circuits in EMT conduit serving the various receptacles are planned for now. I'm debating whether to just use GFCI receptacles at the point of use, and not bother with AFCI/GFCI breakers at all. The county we live in does not require an electrical permit, so no AHJ will be reviewing the system. That being said, I would like to be as safe as possible and follow NEC guidelines where possible.

Your suggestions/comments are welcome!
100% Off-grid with: 8 Solarworld 275 Watt Panels, 8 Concorde SunXtender 405aH 6v AGM Batteries, MS-4448PAE 48v Inverter, MidNite Solar Classic 200 Charge Controller, 10,000 gallon rainwater collection system, etc.

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Re: Use of AFCI/GFCI breakers in Off-grid system

    Arc Fault was to "protect" against somebody running an extension cord under the carpet in a bedroom --- Getting walked on, breaking or shorting, and the arc starting a fire.

    If your home wiring is done to code--Arc faults are not very common (with the possible exception of home wiring done in the 1960's-1970's range with aluminum wiring).

    http://inspectapedia.com/aluminum/Aluminum_Wiring.htm

    Whether the Aluminum wiring failures would be helped with Arc Fault Breakers--I don't know--But in any case it is probably not an issue that you have with your home (I hope).

    The complaint I have read most often is that brushed motors (universal motors) used in vacuum cleaners are a common cause of arc fault trips. And tend to tick people off.

    For GFI--They do not appear to have significant issues with false tripping (unless the GFCI its self fails--Which does happen--Just replace and you are good to go).

    For me--I prefer GFCI to be outlets near point of use (kitchen sinks, outdoors, bathrooms, etc.). That way, if you have a fault--It is pretty much isolated to the point of use and easy to debug/find the problem (or replace the bad GFCI outlet).

    What I do not like, is to put a single GFI outlet or breaker on a branch circuit that has both outlets and lighting. In many off grid homes, the actual number of branch circuits is small (not much power is used from a single, small AC inverter), so it is possible to share a GFI Breaker between lighting (and/or ceiling lights) and outlets.

    A ground fault not only turns off the offending load, it can kill the lighting in the home/cabin/RV and plunge you into darkness.

    So--My two cents--Don't bother with Arc Fault breakers, and only install GFI breakers on dedicated circuits with outlets. If you have circuits that share outlets+lights, put in GFCI outlets in where needed (you can have one GFI outlet connected to several down stream outlets and be protected--There is an "INPUT" and an "OUTPUT" on the GFCI outlet so you can use one GFCI to protect several down stream outlets.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Re: Use of AFCI/GFCI breakers in Off-grid system
    BB. wrote: »
    For me--I prefer GFCI to be outlets near point of use (kitchen sinks, outdoors, bathrooms, etc.). That way, if you have a fault--It is pretty much isolated to the point of use and easy to debug/find the problem (or replace the bad GFCI outlet).

    I have never had to debug/find the problem... It seems that a couple of times a year the GFCI receptacle just trips for no obvious reason, often when no one's home. Be certain that all GFCI outlets are conveniently located... not behind the refrigerator, for example. (Speaking of which, do not put the fridge on a GFCI outlet... you may come home to a warm fridge). Some GFCIs come with a little green LED that is lit when the receptacle is powered, others come with a little red LED that is lit when the GFCI trips.... either way, locate the receptacles so that you can easily see the lights when you walk in the room.
    BB. wrote: »
    (you can have one GFI outlet connected to several down stream outlets and be protected--There is an "INPUT" and an "OUTPUT" on the GFCI outlet so you can use one GFCI to protect several down stream outlets.

    I'm not sure why GFCIs seem to nuisance trip on occasion... I think that the larger the circuit that the GFCI protects, the more likely it is to nuisance trip. This is an argument against GFCI breakers. In my opinion, a GFCI receptacle should only protect one or two nearby downstream receptacles.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Hill_Country
    Hill_Country Solar Expert Posts: 96 ✭✭
    Re: Use of AFCI/GFCI breakers in Off-grid system

    Thanks y'all! Because we are off-grid, we won't be using a vacuum cleaner at all (we'll only have concrete floors, no carpet!), so that won't be a problem.

    Sounds like the preferred route is to go with GFCI receptacles (aka "outlets") at the point of use and not bother with AFCI/GFCI breakers. It's tough because the NEC 2014 calls for AFCI on many of the non-GFCI rooms (i.e. family areas, bedrooms, etc.), so it's tough to see a requirement like that for AFCI protection that does not lend itself to real-world practicality.

    I appreciate your help on this, thanks!
    100% Off-grid with: 8 Solarworld 275 Watt Panels, 8 Concorde SunXtender 405aH 6v AGM Batteries, MS-4448PAE 48v Inverter, MidNite Solar Classic 200 Charge Controller, 10,000 gallon rainwater collection system, etc.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Re: Use of AFCI/GFCI breakers in Off-grid system

    I guess "they are worried about fires where people may sleep... An alternative would be to ensure you have working smoke alarms in these areas.

    -Bill

    PS: I keep misspelling "receptacles" as "recepticals" (browser spell check does not even auto correct this bad of misspelling), so I use "outlets" instead. :blush::cry:
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,746 ✭✭✭✭✭✭
    Re: Use of AFCI/GFCI breakers in Off-grid system

    Not to worry about the lack of a vacuum cleaner, you can still trip the GFCI with a good blender and thirsty guests. If you can stay away from AFCI, you will not be powering the beasts! You can feel the heat they give off, even in summer! Maybe they build better AFCI than I have seen? Good Luck
    Thanks y'all! Because we are off-grid, we won't be using a vacuum cleaner at all (we'll only have concrete floors, no carpet!), so that won't be a problem.

    Sounds like the preferred route is to go with GFCI receptacles (aka "outlets") at the point of use and not bother with AFCI/GFCI breakers. It's tough because the NEC 2014 calls for AFCI on many of the non-GFCI rooms (i.e. family areas, bedrooms, etc.), so it's tough to see a requirement like that for AFCI protection that does not lend itself to real-world practicality.

    I appreciate your help on this, thanks!
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Hill_Country
    Hill_Country Solar Expert Posts: 96 ✭✭
    Re: Use of AFCI/GFCI breakers in Off-grid system
    vtmaps wrote: »
    ..Some GFCIs come with a little green LED that is lit when the receptacle is powered, others come with a little red LED that is lit when the GFCI trips....--vtMaps

    I've wondered about this with GFCI outlets...in an off-grid situation in which the inverter is sometimes "searching" (i.e. in my case the Magnum inverter is configured such that it will take a minimum AC load of 5 watts to wake the inverter), do the green LED's act as a phantom load at all? Or, a better question, do the green LED's on the GFCI outlets just do not come on until there is a sufficient load to wake the inverter? And does this cause any issues with these GFCI outlets at all in a setting where the inverter will be "searching"?
    100% Off-grid with: 8 Solarworld 275 Watt Panels, 8 Concorde SunXtender 405aH 6v AGM Batteries, MS-4448PAE 48v Inverter, MidNite Solar Classic 200 Charge Controller, 10,000 gallon rainwater collection system, etc.
  • Mountain Don
    Mountain Don Solar Expert Posts: 494 ✭✭✭
    Re: Use of AFCI/GFCI breakers in Off-grid system

    With the search function on our VFX Outback the green LED's on the GFCI would blink in time with the search function pulses. Ours was fine tuned to power up with as little power demand as an LED night light. Never had any miscues or failures until the lightning struck.
    Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M
  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Re: Use of AFCI/GFCI breakers in Off-grid system

    Just to give the other side of the story:
    The U.S. Consumer Product Safety Commission (CPSC) estimates that Combination Arc Fault Circuit Interrupters could prevent more than 50 percent of the electrical fires that occur every year. Square D™ QO Combination Arc Fault Circuit Interrupters (AFCIs) are the first commercially available circuit breaker designed to meet the National Electrical Code® (NEC®) requirements for Combination AFCI protection. Combination AFCI’s, also known as Combination Arc Fault (CAFI) Circuit Breakers sense and respond to a broader range of arcing incidents than the standard AFCI circuit breakers, providing enhanced protection against electrical fires for homes and families.

    Series arcing is often associated with damaged devices or cord sets. A series arc is an arcing incident across a break in a conductor. A common example is a cut across one of the two wires in a lamp cord, with a dangerous arc forming in the gap.

    The CAFI Circuit Breaker detects the arcing condition and turns off or trips the circuit, thus providing the enhanced electrical safety and protection. Square D Combination Arc Fault Circuit Breakers are UL® listed, available in QO® and HomeLine™ 1-Pole and 2-Pole circuit breakers with 15 and 20 ampere ratings.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Re: Use of AFCI/GFCI breakers in Off-grid system

    Sounds to me like no one should use a gift of an old fashioned lamp or whatever from grandma's house before replacing the internal wiring and switch....

    Also a problem for slum landlords...
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • Hill_Country
    Hill_Country Solar Expert Posts: 96 ✭✭
    Wanted to provide an update for those that may be reading this post...we pretty much have our electrical system (DC and AC) ready to go. I just need to finish wiring the outlets and installing some smaller EMT conduit runs. On the AC side of things I have chosen to go with the GFCI outlets where GFCI is necessary (bathroom, outdoor, etc.) as per NEC.
    100% Off-grid with: 8 Solarworld 275 Watt Panels, 8 Concorde SunXtender 405aH 6v AGM Batteries, MS-4448PAE 48v Inverter, MidNite Solar Classic 200 Charge Controller, 10,000 gallon rainwater collection system, etc.
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    Attachment not found.

    NEC requires ARC fault DC breakers for PV arrays over 80 volts, I would be more worried on the DC side than the AC side of things. Strange the sponser of this site does not sell them online and they are a code requirement for all installations. So you may want to look into that also..
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    ...NEC requires ARC fault DC breakers for PV arrays over 80 volts, I would be more worried on the DC side than the AC side of things. Strange the sponser of this site does not sell them online and they are a code requirement for all installations. So you may want to look into that also..
    Not all areas have adopted the latest code

    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Hmm... It depends on what NEC means by Arc Fault breakers... NAWS does sell ground fault breakers which were an early attempt at addressing arc fault issues:

    Ground Fault Protection Circuit Breakers

    Personally, I think DC GFI Breaker and the "current sense" circuit (generally a fuse or small breaker between earth ground and return/negative ground lead of the solar power system) is dangerous as defined by the NEC.

    There are true Arc Fault breakers and systems. The Classic MPPT Solar Charge Controller does have an Arc Fault detection circuit to protect against solar array arc faults.

    And MorningStar has a standalone DC Arc Fault standalone breaker setup:

    http://www.morningstarcorp.com/products/ground-fault-protection-device/

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    That morningstar unit looks good, but that is it actually listed as an Arc fault device I'm not sure. Also my Schneider mppt-60-150 has a built in GFI also, and i think it will give visual indication when tripped on the led display. Do you think that the Schneider buit in PVFG is a dangerous design? It has a 1 amp 600v fuse to ground, also you can;t ground the battery dc- anywhere else in the system. These devices look pretty good for arc fault detection but they need an external source and external trip relay. These came out in 2013 so they should be available.
    http://www.sensata.com/uses/solar.htm
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
  • zoneblue
    zoneblue Solar Expert Posts: 1,220 ✭✭✭✭
    BB. wrote: »
    For me--I prefer GFCI to be outlets near point of use (kitchen sinks, outdoors, bathrooms, etc.). That way, if you have a fault--It is pretty much isolated to the point of use and easy to debug/find the problem (or replace the bad GFCI outlet).

    In NZ RCDs (GFCI) are now required on all branch circuits, with some minor exceptions, (dedicated heavy loads like commercial driers). The code does make mention of the desirability of avoiding situations where a RCD popping cuts all lighting, as a safety issue. But thats generally taken care of by splitting lighting into more than one circuit and using seperate RCDs.

    Personally, ive gone with a single house wide RCD. Make sure you buy a top quality brand. And, here our lighting is all DC. Thats becasue the inverter is off overnight and at other times such as bad weather events. (People tend to underestimate the burdon that inverter tare is on small to medium systems.)
    1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
    http://zoneblue.org/cms/page.php?view=off-grid-solar


  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    new2PV wrote: »
    Do you think that the Schneider buit in PVFG is a dangerous design? It has a 1 amp 600v fuse to ground, also you can;t ground the battery dc- anywhere else in the system.

    The reason you cannot ground your DC system anywhere else is because the 1 amp fuse is the bond to ground (there must be only one bond). Therefore it is dangerous because when the fuse blows there is no bond at all.

    Disclaimer: I am not familiar with the Schneider design... I base my conclusion on my knowledge of similar designs that use a 1 amp fuse and permit no other bonding.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    I will ask Schneider about that..but it seems to make sense what your saying..
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    I have asked Schneider if there design leave the PV array ungrounded in the event of a Ground fault. They have not answered the question, they just explained not to bond the ground anywhere else. I Don;t know if I should use this built GF fuse or go with the morningstar PVGFI. Opinions?
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
  • jet1200
    jet1200 Registered Users Posts: 1
    I have the Midnite Classic 200, a Samlex 2000 watt pure sine wave inverter and a Reliance Controls transfer switch. The inverter has a terminal block labeled (L AC) on one side and (N OUTPUT) on the other side. The transfer switch has 3 input lines, a red a black and a neutral. It has 2 watt meters, I expect that switch is divided to distribute the loads from a generator. I took the N OUTPUT from the inverter and tied it to the whit wire of the transfer switch. this continues on out to the mains panel neutral. I took the L AC from the inverter and tied it to both the red and black wires in the transfer switch. there is also a ground wire running from the transfer switch to the mains panel. The transfer switch is a 10 position switch.
    All seems to be working OK, except one line that is attached to an EATON arc fault circuit interrupter breaker, breaks instantaneously. There appears to be a problem with the neutral connections. I removed the neutral between the Mains panel and the transfer switch and it doesn't break, but I think the voltage was about 80 volts.

    Can anyone help me solve this problem?