Solar Expert Posts: 9,583 ✭✭✭✭✭
Adding a new structure to the compound, and it will have it's own Fridge. I'm planning on a 24V based system, to power lights, laptop and an energy star fridge. I'm looking at 3 inverters, in the 600w range, that I think would be able to start a fridge, but wondering about feedback on how to chose between them:
Samlex PST 600 Watt http://www.solar-electric.com/inverters-controllers-accessories/inverters/sasiwain1/samlex-pst-series-pure-sine-wave-inverters/samlex-pure-sine-wave-inverter-pst-600-24.html
Samlex SA 1,000 Watt http://www.solar-electric.com/inverters-controllers-accessories/inverters/sasiwain1/samlex-sa-series-pure-sine-wave-inverters/sa1wa24vosiw.html
Exeltech XP600 24-volt 600 watt http://www.solar-electric.com/inverters-controllers-accessories/inverters/exsiwain/xp-600-24.html
Any feedback on sleep mode, or if the remote control is useful ? The inverter will be sheltered, but outside the house envelope and will see 100F daytime highs, and 20F winter lows. Some look like they have integral outlets, can they all be wired to to a conventional single phase panel.
I plan to use a Midnight Classic 150, on a 60V 800W PV array, and use it's output amps limit to protect batteries in the summer. (I have to size for winter usage.)
Then there is the backup charger. Is there an efficient 24V integrated inverter/charger that can run off a generator, or am I better off with an Iota charger ?
Samlex PST 600 Watt http://www.solar-electric.com/inverters-controllers-accessories/inverters/sasiwain1/samlex-pst-series-pure-sine-wave-inverters/samlex-pure-sine-wave-inverter-pst-600-24.html
Samlex SA 1,000 Watt http://www.solar-electric.com/inverters-controllers-accessories/inverters/sasiwain1/samlex-sa-series-pure-sine-wave-inverters/sa1wa24vosiw.html
Exeltech XP600 24-volt 600 watt http://www.solar-electric.com/inverters-controllers-accessories/inverters/exsiwain/xp-600-24.html
Any feedback on sleep mode, or if the remote control is useful ? The inverter will be sheltered, but outside the house envelope and will see 100F daytime highs, and 20F winter lows. Some look like they have integral outlets, can they all be wired to to a conventional single phase panel.
I plan to use a Midnight Classic 150, on a 60V 800W PV array, and use it's output amps limit to protect batteries in the summer. (I have to size for winter usage.)
Then there is the backup charger. Is there an efficient 24V integrated inverter/charger that can run off a generator, or am I better off with an Iota charger ?
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048
inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A
NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole |
Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor
(1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Comments
-
Re: mid-power inverter choices
Some observations.
The Samlex PST 600 is not likely to start any refrigerator. The SA 1000 should.
The Exeltech 600 might start one, depending on what other loads are on at the same time.
The SA 1000 uses more power than the Exeltech 600 but the latter doesn't have a sleep mode (that I can see) and the SA does, meaning over-all it is likely to use less power.
Buying a stand-alone charger to go with one of these is cheaper than any quality sine wave inverter-charger I know of. When they put that charger in they tend to go up in power (2kW or more) to make it worthwhile, and hence they go up in price. A lot.
None of these are designed to be hard wired, but that doesn't mean it's impossible. -
Re: mid-power inverter choices
Our host has generally recommended 1,200 to 1,500 Watt minimum AC inverters for refrigerator usage.
Question--Is the refrigerator going to be a frost free (internal defrost heaters) or a non-frost free (or freezer converted with a refrigerator temperature control)?
In general, a frost free refrigerator has a ~12 hour timer... Approximately 1 hour or so of "defrosting" every 12 hour cycle. And (Niel?) found that running a frost free refrigerator without the heater would start icing up the evaporator in ~24 hours.
The cheap frost free refrigerator have a mechanical timer and it "May" work OK on an inverter with "search mode"--But it stretches the 12 hour cycle out by the compressor duty cycle (~50% duty cycle, 24 hour defrost cycle). Also--When the defrost cycle is running, your heater will probably turn on and off--Which will probably cause the 6 watt search mode to cycle on and off too--Sort of a mess trying to mix frost free + search mode inverter.
Some refrigerators use an electronic timer--Which as been reported as starting a new defrost cycle every time AC power is restored. Not good for a defrosting cycle.
Probably just easier to just get a larger solar panel array and battery bank to allow the AC inverter to run 24 hours per day (assuming 10 Watt Tare losses and 4 hours per day minimum sun):- 10 Watt "tare losses" * 24 hours = 240 Watt*Hours
- 240 Watt*Hours * 1/0.52 system eff * 1/4 hours minimum sun (~9 months of year without generator backup) = 115 Watt larger array (guessing)
- 240 WH * 1/24 volt battery bank * 2 days no sun * 1/0.50 maximum discharge = 40 AH @ 24 volt larger battery bank
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: mid-power inverter choices
I bought one of these to fill a gap on a 24V bank and run a full size refrigerator on. It even has a 30 amp built in charge controller that I haven't used and a small AC charger and AC transfer switch.
The 48 V is a heck of a deal @ $500
http://www.powergatellc.com/mean-well-tn-1500-dc-ac-inverter.html -
Re: mid-power inverter choicesI'm looking at 3 inverters, in the 600w range, that I think would be able to start a fridge, but wondering about feedback on how to chose between them
Have you looked at Victron's Phoenix line of inverters? They have some incredibly low tare losses.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: mid-power inverter choices
Going to be a standard energy star (frost free) 19CF fridge, so it's likely to have the electronic timer. Drat. forgot about that. No snooze for me.
The SA 1000 looks to be the sure thing to start a fridge, if something else happens to be on. Bummer that it's nearly 20watts idle. Have to double the calcs that BB Bill did.
Sure wish Morningstar came out with a suresine that had enough beef to start a fridge. That would be sweet. I wonder what Midnight's inverter offering will be?Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: mid-power inverter choices
My"cheap"fridge and freezers have a simple clock work motor timer. It may be possible to wire the motor to a separate small ac inverter. However even the small tsw inverters seem to use 6 watts or so. Probably not worth the cost, time, or expense (or use a DC timer to drive the defrost circuit/cut the compressor.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: mid-power inverter choices
I have the Samlex PST-1500-24. It has dual output - hard wire and GFCI and both can be used simultaneously. Tare is ~18W, no snooze/standby function. It starts and runs a 1200W microwave without a hiccup, and I suspect that it will start a fridge. -
Re: mid-power inverter choicesHave you looked at Victron's Phoenix line of inverters? They have some incredibly low tare losses. --vtMaps
only 5 watts for the 24v/1200w version But not sold in North America except for the small 12V models.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: mid-power inverter choicesonly 5 watts for the 24v/1200w version But not sold in North America except for the small 12V models.
try: http://baymarinesupply.com/store/electrical/chargers-inverters/victron/victron-phoenix-24-1200-inverter.html
by the way, the only reason I haven't bought one is that they are not listed for hard-wiring into a system. They have some sort of marine listing/certification.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: mid-power inverter choicesCariboocoot wrote: »The Exeltech 600 might start one, depending on what other loads are on at the same time....
...None of these are designed to be hard wired,...
NAWS has a very good price on the XP1100, and they say pretty good stuff about them!We have been selling Exeltech inverters for over 15 years, and we have never had one single report of any failure of any type. In fact, we have never even heard of one going bad that was not grossly abused (i.e. like hooking the battery terminals to AC power).
Exeltech inverters have an MTBF(mean time between failure) in excess of 20 years and offers the most competitively priced ultra-reliable true sine inverters available anywhere
And Exeltech via NAWS (and I hoped they checked this since they just updated their website)...We also still support and repair units from 20 years ago, and do so for a flat fee. Case in point: If you accidentally reverse connections on an XP1100 inverter you bought in 1994, or an MX module from 1993 .. or even an old SI1000 from 1991, and blow it up .. if it's repairable, we'll fix it for $100 and (if possible) upgrade it at the same time. Turn-around time generally averages less than a week.
Here is the back showing the user neutral ground bonding at the hard wire points, which can be removed, it also has outlets on the other side.
Attachment not found.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: mid-power inverter choices
oh goodie ! more choices !!Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: mid-power inverter choices
The Exceltech XP1100 looks good. I just question the size of the conduit knockouts and wire bending space in its AC/DC enclosure. -
Re: mid-power inverter choices
You can take the enclosure off, I wired my xp1100 somewhat light, with 4 gauge about 18 inches from breaker (heavier to battery) I don't think I would have any problem with 2 gauge, then again I ran 4 - 4gauge in 1 inch (max allowed) The knock outs are is 3/4".Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed