Xw6048 with grid breaker turned off
fca1
Solar Expert Posts: 124 ✭✭
Hi just a question when I turn off the breaker that feeds the xw ac1
It shows this in ac voltage ....it's Strange
48.9v ?? Attachment not found.
Re: Xw6048 with grid breaker turned off
Check the neutral and earth ground at the Inverter and see if you get that on a dvm. -
Shows 0V on mine.
Did you try to measure what it really is at AC1 terminals? -
I had a guy once that had a charger hooked up and some how it would back drive to a 2 way switch he had wired in a hallway and it would pass DC voltage back to the Inverter through the neutral and ground if it was plugged in. Gremlins !!Shows 0V on mine.
So reading it with multimeter
It matches the reading of the xw6048
50v and DMM 49v
With ac grid breaker on I got 3v between neutral and earth ..
With ac grid breaker off I got 100v between neutral and earth..
I don't have batteries negative conected to earth..
At least intentionally only if xw do it by itself -
Apparently, your neutral is not connected to the ground, or it couldn't be 100V in there.
But also, I guess the XW neutral is not connected to the grid neutral.
- 234 Forum & Website
