Ok so we have decided on having about a 1 kw continous sytem design. using a 24 volt battery bank
I have calculated that that 1000 w*24 hours *1/24 volts*1/.85*1/.5= 5647 AH so to find how many batterys i need i devide that number by the @20 hr amp hour rate of my battery
this is the battery the group wants to go with
Smart Battery™ SB100
12V 100AH Lithium Ion Battery
Size: Group 31
Nominal Voltage: 12.8V
Amp Hours: 100
1000 Cranking Amps
300 min @ 20A
120 min @ 50A
Max Continuous Discharge 100A
after doing the peukerts equation i find that value to be only 2.73 ams
20=(50*(50/2)^(1.05-1))/x^1.05
does that mean it would take 2068 batteries for this system
I have calculated that that 1000 w*24 hours *1/24 volts*1/.85*1/.5= 5647 AH so to find how many batterys i need i devide that number by the @20 hr amp hour rate of my battery
this is the battery the group wants to go with
Smart Battery™ SB100
12V 100AH Lithium Ion Battery
Size: Group 31
Nominal Voltage: 12.8V
Amp Hours: 100
1000 Cranking Amps
300 min @ 20A
120 min @ 50A
Max Continuous Discharge 100A
after doing the peukerts equation i find that value to be only 2.73 ams
20=(50*(50/2)^(1.05-1))/x^1.05
does that mean it would take 2068 batteries for this system
Comments
-
Re: Battery question
If you want to output 1kW for 24 hours, you need to store 24kWh /0.85 = 28kWh
12V 100AH battery discharged to 50% will give 12*100*0.5 = 0.6kW
So, you need 28/0.6 = 47 batteries. 48 is probably a better number. -
Re: Battery question
Why you should always do math in order.
1kW * 24 hours = 24 kW hours.
Conversion efficiency of inverter 90% = 26.7 kW hours
Inverter consumption in 24 hours (assuming a reasonably good inverter) = 576 Watt hours
Needed stored energy: 27,276 Watt hours. Round up for losses.
28 kW hours @ 24 Volts = 1167 Amp hours
Battery bank @ 50% DOD = 2334 Amp hours. Round up to nearest available size. Calculate recharging capacity from that.
Ridiculous to try and get that much capacity from 100 Amp hour batteries. It will be a mare's nest of wiring.
But hey; feel free to do any way you like.
Batteries that give specs on cranking Amps and reserve capacity are probably not suitable for RE applications. -
Re: Battery question......
after doing the peukerts equation i find that value to be only 2.73 ams
20=(50*(50/2)^(1.05-1))/x^1.05
does that mean it would take 2068 batteries for this system
Peukerts is designed for Lead Acid batteries. Applying it to LiOn will give vastly different results. Same idea, but the
ratios are different.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Battery questionCariboocoot wrote: »Battery bank @ 50% DOD = 2334 Amp hours. Round up to nearest available size.
2400.
24 series of 100AH batteries.
2 batteries per series.
24 x 2 = 48
Same result as mine
24 series probably not going to work anyway -
Re: Battery question2400.
24 series of 100AH batteries.
2 batteries per series.
24 x 2 = 48
Same result as mine
24 series probably not going to work anyway
Uh, two 12 Volt 100 Amp hours in series to get 24 Volta & 100 Amp hours.
Twenty-four such strings in parallel to bring the capacity up to 2400 Amp hours.
It's that last one that's ludicrous; there is no way those batteries are going to share current equally no matter what.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed