Generators and non-linear loads

Sun Dog
Sun Dog Solar Expert Posts: 115 ✭✭
So I thought I had a handle on how to size the generator for my system and then I find out that charging batteries is a non-linear load and is hard on the generator head. My original goal was to use the smallest 1800rpm diesel generator I could find that would allow me to charge my battery bank and keep the house running. If I do that it sounds as though I will likely end up giving the generator head a pretty hard life.

The best solution seems to keep the non-linear loads to a minimum (don't charge the batteries at the max rate) and get a generator with an oversized head to deal with extra heat and run it with a smaller motor to keep the fuel consumption down. I'm guessing this will mean a higher price vs an off the shelf design so one could argue to buy the off the shelf unit and use the savings to pay for a lot of diesel. Any other solutions out there?

Comments

  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: Generators and non-linear loads

    Ever heard the phrase "over-thinking a problem"? :roll:

    Buy a gen set that meets the needs. Where maximum loads are 50% - 75% of the capacity. Don't run it for long times lightly loaded (especially if it's diesel). Stop worrying.

    A large number of off-gridders use generators for back-up/supplemental charging with no problems.

    Bill will be a long in a minute to link to the choosing a generator thread. :D
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    Re: Generators and non-linear loads

    Actually "AD" and I have been having a long email discussion about this issue...

    For me, I believe there is a big difference between the average non-power factor corrected battery charger (PF down to 0.6 or so) and a Power Factor Corrected battery charger (PF around 0.95).

    I was looking over some generator head specifications from Hardy Diesel and it appears that the kWatt rating of a genset at PF not equal to one derates really quickly... 0.8^2 = 0.64 kW derating. 0.6^2=0.36 kW derating.

    And this confirms what one dealer was telling Arctic... To run a genset at 3x the battery charger watt rating...

    But this gets us to the whole issue of "wet stack"/coking/cylinder wall glazing when the genset is operating at 40-60% or less of engine power rating.

    Their suggestion was to put some electric heaters on the genset to help better load the unit (OK in winter, not so good in summer).

    Any way, I suggested he come here and ask his questions. AD already has a Schneider/Xantrex XW 4048 on order (does have PFC charging). So--looking for others real life experiences and suggestions for 6-10 kW diesel gensets. The two vendors (that I know of) that he has spoken with:

    www.northern-lights.com
    hardydiesel.com

    Obviously, he has some dark winters in the Arctic (as I recall, he is losing his Grid Power from the Utility--and it is beyond his power to change that decision)--So a reliable installation is probably even more important than raw fuel use.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: Generators and non-linear loads

    Change the order from the XW to a Magnum which has the PF corrected charger? Cheaper solution, I would think, than a custom-fit generator.

    Any generator is going to need maintenance. Just keep on top of it. Have a back-up gen if your really generator dependent. Heck, I've got four generators! All work, all have lots of hours (one ridiculously so), all have had minimal servicing. None are diesel, though.

    I suspect the whole wet stacking issue is one of using diesel gens insufficiently loaded as prime power: long hours of running without getting up to temp. I used to have a diesel that needed to be revved up before you shut the fuel off or else you'd not get it started again due to the excess fuel in the cylinders (acts as coolant and keeps the temp down so it won't reach combustion temps). Similar problem.

    One fellow here, oil pan 4, has experimented with propane fumigation on diesels to keep combustion temps up. Might be something to consider, especially in arctic climes ('cause you can't by ether in 55 gallon drums :p ).
  • Sun Dog
    Sun Dog Solar Expert Posts: 115 ✭✭
    Re: Generators and non-linear loads

    Morning guys,

    I fully admit to the paralysis of analysis, it's just how I learn. I have followed the lead from both of you and picked up a EU2000i and already have another 5.5kW gasoline generator. As Bill mentioned, it just gets a little confusing when a generator manufacturer says something that appears to contradict with the direction I was planning on going.

    Not that it matters, but for just for clarity it is the XW4024 that I have gone with. Like the Magnum line it has a PFC charger.
  • dwh
    dwh Solar Expert Posts: 1,341 ✭✭✭
    Re: Generators and non-linear loads

    These guys build some pretty sweet gensets.

    http://www.nextgenerationpower.com/



    Their smallest I think is a 300cc Kubota single cylinder engine driving a 5kw Markon (Cummins) head. Using differential pulley sizes they reduce the engine RPM to 2800 and still get a 3.5kw continuous rating out of the unit. Between the engine's rather beefy flywheel and the oversized alternator, it can obviously handle surges up to 5kw without a problem until the flywheel momentum bleeds off and the engine starts to slow down.

    Can be had in several variations, including marine:

    http://www.nextgenerationpower.com/3kwlow.html

    Here's some pics of both sides:

    http://www.hackneys.com/mitsu/photos/buildup_album_16/image007.htm

    http://www.hackneys.com/mitsu/photos/buildup_album_16/image008.htm
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Re: Generators and non-linear loads
    dwh wrote: »
    These guys build some pretty sweet gensets.

    http://www.nextgenerationpower.com/



    Their smallest I think is a 300cc Kubota single cylinder engine driving a 5kw Markon (Cummins) head. Using differential pulley sizes they reduce the engine RPM to 2800 and still get a 3.5kw continuous rating out of the unit. Between the engine's rather beefy flywheel and the oversized alternator, it can obviously handle surges up to 5kw without a problem until the flywheel momentum bleeds off and the engine starts to slow down....

    The fine print taketh away:
    3.5 kw, 120VAC, modified sine wave, electronic voltage regulation.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • dwh
    dwh Solar Expert Posts: 1,341 ✭✭✭
    Re: Generators and non-linear loads
    mike90045 wrote: »
    The fine print taketh away:
    3.5 kw, 120VAC, modified sine wave, electronic voltage regulation.

    If you got that from the caption under the pic on Doug Hackney's site - that's a typo on his part. There is no such thing as a modified sine wave *alternator*.
  • RCinFLA
    RCinFLA Solar Expert Posts: 1,485 ✭✭✭✭
    Re: Generators and non-linear loads
    dwh wrote: »
    If you got that from the caption under the pic on Doug Hackney's site - that's a typo on his part. There is no such thing as a modified sine wave *alternator*.

    Possible on inverter-generator but I doubt the Hackney site picture is DC alternator.

    The pictures do show a strange pully ratio. Engine pulley is slightly larger then alternator pulley.

    This would put generator rpm lower then alternator. It is usually the other way around with 1800 rpm four pole alternator run from diesel at 2000 to 2400 rpm to get up to a more optimum HP on diesel. Pully ratio doesn't look great enough to be driving a two pole alternator at 3600 rpm's unless diesel is running close to 3000 rpm which would be a bit high for a diesel. Maybe this is the case for the small HP diesel.

    I know the Chinese make 5-6 kW portable generators running 10 HP diesel at 3600 rpm but I just feel a diesel with high compression ratio running at 3600 rpm is not going to be a very long lasting engine. Does anyone own one of these? How do they hold up?
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Re: Generators and non-linear loads
    dwh wrote: »
    If you got that from the caption under the pic on Doug Hackney's site - that's a typo on his part. There is no such thing as a modified sine wave *alternator*.
    Well, I'm just reading whats there. And it's not a typo, it would be a mis-statement.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,893 ✭✭✭✭✭✭
    Re: Generators and non-linear loads

    One of the best Marine diesels ever built was the Isuzu 4AB1/C240 and the whole series of 4, 3, and 2 cylinder engines spun at near 3000 RPM. all of these were less than 50HP. 10,000 hours easy!
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Sun Dog
    Sun Dog Solar Expert Posts: 115 ✭✭
    Re: Generators and non-linear loads

    Thanks for the input guys. FWIW I ended up going with an off the shelf 10kW Perkins unit from Hardy Diesel. Seemed like a reasonable compromise as it has a bigger alternator than their 8kW but uses the same engine. Surrette says the max charge rate for my batteries is just under 11% at the 20 hour rate. If that seems like too large of a non-linear load (assuming I can tell :roll:) I could it lower the current and run the genni longer. The minimum charging current is ~5% based on the 20 hour rate.