Starting my generator from a remote building.
wrdaigle
wrdaigle Solar Expert Posts: 65 ✭✭✭✭
I am in the process of wiring a shop building. I think I have finally decided to make 2 different wire runs to the shop: one from the house so I can run lights and small power tools off of my batteries and one directly from the generator so I can run tools like my table saw and compressor directly off the generator. The generator (Kohler 12Res) sits about 200ft from my shop, so I would like to be able to start and stop it remotely. My outback system in the house is already hooked up to the 2-wire start on the generator.
Can I run start it from a second location? If so, what would I need. I considered getting a second mate and mounting it in the shop building, but it doesn't look like that option is option is functional yet.
  • stephendv
    Re: Starting my generator from a remote building.
    2-wire start is just a switch, so you can wire as many switches in parallel as you like. If you can't run an additional wire for the extra switch in the shop, you could use a remote controlled relay like this: http://www.seeedstudio.com/depot/315mhz-remote-relay-switch-kits-2-channels-p-150.html?cPath=139_140&zenid=88650bf642df0178599f80a4b43b4bcd
  • blackswan555
    blackswan555 Solar Expert Posts: 246 ✭✭
    Which end is your aux relay ? gen or inverter ? If you can get to it or the "2 wires" that go TO the gen FROM the relay, As said it is simply a case of paralleling a switch alongside them,(2 wire start, just join the 2 wires together, it starts, take em apart it stops)
    If it is before the aux relay, The FX output`s 12v to trigger the relay, so is a little more difficult, (Be careful not to bridge these, it will kill the board)
    You can not use more than one mate, Although if you have computers & network available there are other options, (I would stick with wire & switch,As long as it`s mechanically suitable, Wire size / type is not that important)
    Tim
  • wrdaigle
    Got it. The 12v relay is what was confusing me. This sounds simple enough. I can certainly run wires for the switch. Do I need to get any particular type of switch, or will any old household switch suffice?
    Thanks, Bill
  • blackswan555
    Any switch will do, but as it is low voltage, keep it away from the AC as much as poss, If you want to be posh/ your workshop is far away/ you feel like it, You could use 2 way light switches and wire it as fig 2 http://www.electronics-project-design.com/LightSwitchWiring.html substituting AC & lamp for your 2 wire, one either end,and if you forget to turn it off, you will not have to walk :D
    Tim
  • JayWes
    JayWes Registered Users Posts: 6
    One thing to consider on an AC control circuit is distance; there the capacitance between two control wires in series with an inductance of a relay and this can cause enough current to flow in the open circuit to operate a relay. For this reason in a lot of remote control circuits a DC source and relay is used. Also keep in mind even though you are talking small currents, a long run with small wire can have a large voltage drop.
    :roll:Some manufacturers also provide remote control panels for generators. These can also provide annunciators and pilot lights to indicate the generator status.
    :blush:A warning sign should be placed on the generator to indicate that it can be remotely started. A means to disconnect the remote starting circuit should be provided for protection during servicing.
    JayWes wrote: »
    So far, the contactor (120V coil, 240V contacts) and float switch for my pump (700' each way) has been working ok. I think it will take a lot more distance to get a tuned circuit to start flipping around. I hope. I stayed with 120VAC, because of the distance, and that's what the contactor coil was.
  • nsxnitro
    nsxnitro Registered Users Posts: 19 ✭✭
    Is Kohler 12res generator two wire connection 3 and 4?
    BB. Super Moderators, Administrators Posts: 33,723 admin
    WR has not been back since 2013--You probably will not get an answer from him.
