Xantrex SW aux. relay ratings
wirenut
Registered Users Posts: 22 ✭✭
Does anyone know the ratings of the aux. relays on a Xantrex SW inverter? I can't seem to find anything about their current or voltage limits in the manual. I would like to use one to trigger a load shedding contactor. Ideally I would use a contactor with a 120v ac coil and run this thru the aux. relay but I don't know if it will handle that voltage. I could also use a contactor with a 48v dc coil (if I can find one) and run that thru the aux. relay. I get the feeling from the manual that they are for 12v dc only but it doesn't really say.
Any help is greatly appreciated.
Re: Xantrex SW aux. relay ratings
6.3 amps @ 250vac max. (From the SWplus GSM start module which uses same relays)
SW manual states to use a 5 amp fuse to protect relay contacts. It also shows a 120vac relay hookup diagram. -
RC, thanks,
I didn't see the 120v diagram in the manual but I downloaded it so maybe that part wasn't in there. Just in case it matters, these are regular SW units, not SW plus. Anyway, thanks again, I guess I'll use a regular old 120v contactor. -
Look at page 89 of rev B or C regular SW manual.
There is a diagram showing a connection for a PV on-off regulator using the SW's battery voltage monitor through RY9. It uses a 120 vac relay coil.
- 234 Forum & Website