Xantrex SW aux. relay ratings

Does anyone know the ratings of the aux. relays on a Xantrex SW inverter? I can't seem to find anything about their current or voltage limits in the manual. I would like to use one to trigger a load shedding contactor. Ideally I would use a contactor with a 120v ac coil and run this thru the aux. relay but I don't know if it will handle that voltage. I could also use a contactor with a 48v dc coil (if I can find one) and run that thru the aux. relay. I get the feeling from the manual that they are for 12v dc only but it doesn't really say.
Any help is greatly appreciated.
Thanks
Any help is greatly appreciated.
Thanks
Comments
6.3 amps @ 250vac max. (From the SWplus GSM start module which uses same relays)
SW manual states to use a 5 amp fuse to protect relay contacts. It also shows a 120vac relay hookup diagram.
RC, thanks,
I didn't see the 120v diagram in the manual but I downloaded it so maybe that part wasn't in there. Just in case it matters, these are regular SW units, not SW plus. Anyway, thanks again, I guess I'll use a regular old 120v contactor.
Look at page 89 of rev B or C regular SW manual.
There is a diagram showing a connection for a PV on-off regulator using the SW's battery voltage monitor through RY9. It uses a 120 vac relay coil.