fuse size for #10 wire
bobdog
Solar Expert Posts: 192 ✭✭
Comments
-
Re: fuse size for #10 wire
Depends... Are you going with NEC (National Electric Code)? Is the wire type Listed in the NEC? Is it going in Conduit? Conduit Fill Factor? Open Air?
This chart lists maximum amperage (no insulation type listed) for chassis (open air?) type wiring.
For example, typically NEC lists 14 AWG as 15 amp fuse. That chart lists at 32 amps maximum. For sending energy any distance, it seems to be very conservative (14 awg = 5.9 amps).
This chart seems to list generic NEC type ratings (fill factor?).
If you are going to do this a lot using "house wiring"--then you should get a copy of the current NEC. (no--I don't have a copy ).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: fuse size for #10 wire
Thanks Bill., The NEC chart is what I was looking for. I book marked it. It is for the battery bank back to the panel. I am using #10 right now and would like to fuse it at the post via the Blue Sea terminal post fuses that Tony talks about. I ordered a 40 amp and now will ask them to change to a 30 amp fuse. -
Re: fuse size for #10 wire
I've always used the romex calc,
10ga = 30A
12ga = 20A
14ga = 15APowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: fuse size for #10 wire
The NEC charts are based on heating per foot which does not assure a satisfactory voltage drop for any given total run length.
Wire types that have multiple layers of insulation like SOOW cord have a lower max current rating for their wire size because of inability to dissipate heat. The heat dissipation also derates for number of current carrying conductors in a conduit/cord bundle which generates more heat in a given confined area.
Original reasoning was elevated heating will progressively degrade wire insulation, making it brittle. Modern wire insulation is much better at resisting enbrittlement.
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed