Phase Imbalance & NEC 690.63
System
Posts: 2,511 admin
NEC 2008 690.63 (A) states:
<< Single-phase inverters for photovoltaic
systems and ac modules in interactive solar photovoltaic
systems shall not be connected to 3-phase power systems
unless the interconnected system is designed so that significant
unbalanced voltages cannot result.>>
My question is what exactly is meant by "unless the interconnected system is designed so that significant unbalanced voltages cannot result"?
I've been told by an inverter rep in a training seminar that phase imbalance of up to 6 kW is tolerated by most utilities.
Can anyone offer any guidance on this?
Who determines the definition of 'significant' -- the local electrical inspector or the utility?
I know that installing 3 single-phase inverters, 1 on each phase, is a common practice to avoid imbalance, but I have a commercial client who wants a small array (5kW). More for showing off to customers than serious load reduction and energy savings.
And they just don't make 5 kW 3 phase inverters, to my knowledge.
This my first post here, thanks in advance to responders.
<< Single-phase inverters for photovoltaic
systems and ac modules in interactive solar photovoltaic
systems shall not be connected to 3-phase power systems
unless the interconnected system is designed so that significant
unbalanced voltages cannot result.>>
My question is what exactly is meant by "unless the interconnected system is designed so that significant unbalanced voltages cannot result"?
I've been told by an inverter rep in a training seminar that phase imbalance of up to 6 kW is tolerated by most utilities.
Can anyone offer any guidance on this?
Who determines the definition of 'significant' -- the local electrical inspector or the utility?
I know that installing 3 single-phase inverters, 1 on each phase, is a common practice to avoid imbalance, but I have a commercial client who wants a small array (5kW). More for showing off to customers than serious load reduction and energy savings.
And they just don't make 5 kW 3 phase inverters, to my knowledge.
This my first post here, thanks in advance to responders.
Comments
-
Re: Phase Imbalance & NEC 690.63
I believe that will be decided by the utility...
There are many variations for 3 phase power drops to smaller companies... Many only install one transformer for the "heavy" 1 phase loads and a second smaller transformer to power the random 3 phase loads (Open Delta configuration).
For a small 3 phase system, you could look at an Enphase (micro inverter) installation... However, many codes/regulations seem to require that if 1 phase of 3 phase power is lost--then the generators/sources of the other two phases have to be cut too...
Personally, I think that this is probably a bit of overkill--especially for smaller solar installs (see open delta configurations).
You utility with their information on the local connection for the commercial customer is the best approach to a solution.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Phase Imbalance & NEC 690.63
Thanks Bill. I think I'll go bug the utility company about it. -
Re: Phase Imbalance & NEC 690.63
Relates to requirement specified in 690.63(B) for de-energizing when any of three phases become 'significantly' unbalance voltage-wise.
This is typically +/- 12.5% but is up to local power company.
I don't believe NEC would specify a number less it causes someone to point a finger at local power company to their supplied voltage being 'out of spec'. -
Re: Phase Imbalance & NEC 690.63For a small 3 phase system, you could look at an Enphase (micro inverter) installation...
-
Re: Phase Imbalance & NEC 690.63Was going to suggest that, too. Then you can do a 3-phase install with as little as one panel.
now that may prove difficult to do unless they have changed their microinverters specifically for 3 phase. you most likely would need one for each phase and from what i have gathered is that that is not legal to do as one leg may fault and the others are required to react to the fault which 3 separate inverters will not do. i do disagree with the need for this rule as inverters only follow the source and will disengage in the absence of the utility provided legs of 3 phase. if the utility is only properly providing on 2 of those legs (or worse) they penalize the solar installation while allowing the utility to violate the very same ruling only because they are the source of the problem. way to go whiles. -
Re: Phase Imbalance & NEC 690.63now that may prove difficult to do unless they have changed their microinverters specifically for 3 phase.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed