Please help, Very confused
Comments
-
Re: Please help, Very confused
You may be one of the first people here to get the new Xantrex TC2 series chargers... Reading through the user manual (PDF download) shows a very flexible charger. I like you can get the 40 amp (12 volt) charger and program the maximum DC charging current to much less--allows it to be used on smaller gensets as a backup up charger for power outages.
What your battery bank temperature--if it swings hot or cold a lot--get the remote battery temperature sensor.
Regarding what to do with the charger:Float mode When the ready and charging indicator LEDs
both illuminate, all batteries are fully charged and ready for
use. If you selected the three-stage charging mode, the
Truecharge™ 2 Battery Charger is in float mode and will
maintain the batteries’ charge.
Standby mode Or Rest mode. If you selected the two-stage
charging mode, the ready indicator LED shows the charger is
now in rest mode and is continuously checking battery
voltage.
With either charging mode, the Truecharge™ 2 Battery
Charger will begin a charging cycle 21 days after the last
completed cycle, or when the minimum battery terminal
voltage drops to below 12.5V (12V chargers) or 25V (24V
chargers) for 15 minutes.
Leaving the charger on will probably prevent any charging by your solar panels--so it will be your choice.
Yes, you can leave it plugged in and do nothing (if in 3-stage charging mode)... Leave AC power turned off (if solar powered charging). Or disconnect from DC power (removes power from charger's status LEDs/panel).
It appears that you need to manually turn on the equalize function--be careful with attached DC loads--equalize voltage appears to be 16.0 volts... Very high and may turn off/negatively affect many DC loads (15.5 seems to be the assumed maximum for many DC loads).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Please help, Very confusedSo is it set it and forget it basically?
You will need to monitor the water level in the batteries and the state of charge ... adjust your usage if you start to draw the batteries down too much.
It appears to me that you are loosing power through all of this. I presume you have the charger pluged into the grid? The battery charger has loses, the batteries have big loses and then there are losses at the inverter. I'm guessing that your loosing ~30% going this route.
Something else has me confused; you say your 220v loads are still on the grid and that the inverter is powering the 110v loads, do you have two breaker boxes or, are you running extension cords all around the house? -
Re: Please help, Very confusedNo part of this is forget it..
You will need to monitor the water level in the batteries and the state of charge ... adjust your usage if you start to draw the batteries down too much.
It appears to me that you are loosing power through all of this. I presume you have the charger pluged into the grid? The battery charger has loses, the batteries have big loses and then there are losses at the inverter. I'm guessing that your loosing ~30% going this route.
Something else has me confused; you say your 220v loads are still on the grid and that the inverter is powering the 110v loads, do you have two breaker boxes or, are you running extension cords all around the house?
I have 2 breaker boxes. One that is 100% solar and the other 100% grid. THe solar system I started is 110v and is 100% on the solar breaker box.
I just returned from picking up 2-6v 395ah@20 hr. crowns model cr-395. I disconnected all the deep cycles and layed them to the side. NOW, if I understand correctly I need to go pos to neg and neg to pos to make the 12v right? then how do I connect it to the inverter? Do I take the POS from either battery and the neg from the other even though they are connected to the other batteries opposite? Hope that is not a confising question. Thanx -
Re: Please help, Very confusedif I understand correctly I need to go pos to neg and neg to pos to make the 12v right?
-
Re: Please help, Very confusedI really hope you didn't try to connect with two jumpers or HOLY smokes, are you still alive? Just use one very heavy jumper from the NEG of 1st battery terminal to the Pos terminal of the 2nd. Then hook neg inverter cable to the still empty neg battery terminal of 2nd battery and POS inverter wire to empty POS terminal of 1st battery.
LOL still alive as I wasnt going to attempt it till I understand it.. Gonna tell the wife to follow your instructions..... I will ledt you know if she's still alive in just a sec..................LOL Just a joke! Thanx and going downstairs to hook it up. BRB as this ONE battery running the house isnt cutting it. -
Re: Please help, Very confusedI really hope you didn't try to connect with two jumpers or HOLY smokes, are you still alive? Just use one very heavy jumper from the NEG of 1st battery terminal to the Pos terminal of the 2nd. Then hook neg inverter cable to the still empty neg battery terminal of 2nd battery and POS inverter wire to empty POS terminal of 1st battery.
also when I hook up the solar im doing the SAME thing I did for the inverter right? so in otherwords, the solar will be connected to the SAME posts that the inverter is hooked up to? Thanx -
Re: Please help, Very confusedalso when I hook up the solar im doing the SAME thing I did for the inverter right? so in otherwords, the solar will be connected to the SAME posts that the inverter is hooked up to? Thanx
-
Re: Please help, Very confusedI have 2 breaker boxes. One that is 100% solar and the other 100% grid. THe solar system I started is 110v and is 100% on the solar breaker box.
-
Charge controllers
ok right now I use a sunforce 30amp digital charge controller on 3 solar panels (120w each) I have 3 more on the way and need to know do I just put the new 3 on another sunforce 30amp like the one I already have hooked up or is there a charge controller that handles more then 30amps? In total I will eventually have 10 panels. -
Re: Please help, Very confused
There are many charge controllers that will handle more than 30 Amps. How much do you want to spend?
Sometimes using multiple small controllers can be advantageous, especially if panel can't all be oriented in the 'ideal' direction. Or if the panels are of significantly different spec.
Otherwise, going up to an MPPT controller is a good idea with larger arrays. Check out some of the choices available from our host NAWS: http://store.solar-electric.com/chco.html
Morningstar, Outback, and Xantrex all have units capable of 60 Amps. -
Re: Please help, Very confusedCariboocoot wrote: »There are many charge controllers that will handle more than 30 Amps. How much do you want to spend?
Sometimes using multiple small controllers can be advantageous, especially if panel can't all be oriented in the 'ideal' direction. Or if the panels are of significantly different spec.
Otherwise, going up to an MPPT controller is a good idea with larger arrays. Check out some of the choices available from our host NAWS: http://store.solar-electric.com/chco.html
Morningstar, Outback, and Xantrex all have units capable of 60 Amps.
All my panels are going to be the same in every way. I only buy one brand/model because I get the 120w panel for 299 delivered. (hope I am not paying alot..) -
Re: Please help, Very confusedCariboocoot wrote: »There are many charge controllers that will handle more than 30 Amps. How much do you want to spend?
Sometimes using multiple small controllers can be advantageous, especially if panel can't all be oriented in the 'ideal' direction. Or if the panels are of significantly different spec.
Otherwise, going up to an MPPT controller is a good idea with larger arrays. Check out some of the choices available from our host NAWS: http://store.solar-electric.com/chco.html
Morningstar, Outback, and Xantrex all have units capable of 60 Amps.
OK so since im a pretty poor guy, BUT dont want the cheapest as we always know cheap isnt always good... What is reasonable? Thanx -
Re: Please help, Very confusedOK so since im a pretty poor guy, BUT dont want the cheapest as we always know cheap isnt always good... What is reasonable? Thanx
Don't ask me, I live in Canada; nothing is reasonable here!
Plan out your eventual system and see what fits your needs/budget. You're the only one who can determine that. -
Re: Please help, Very confused
If you can wait a month or two, there is a new controller that is coming out. One of our members is testing it now. Looks to be hands down the best. Otherwise all three that Marc mentioned are good and it gets to be a choice of color! -
Re: Please help, Very confused
Oops, with 10 100 watt panels on a 12 volt system you are looking at 100 amps! You are going to need two controllers! -
Re: Please help, Very confusedmy average usage per day (when the elec. co meter was running everything) is 28 kw per day. Now that the only thing on the electric company is 220v appliances and a outlet for the charger it is 7kw a day which would be 210kw per month. Our elec. co charges .11 per kw.
Why do you think 11 cents a kw is so high? You are going to spend many more bucks to avoid your electric co. -
Re: Please help, Very confused
Buy the best controller you can afford. If you have to wait a couple of months then do so. You could always ask on here if anyone is upgrading. Maybe they're looking to get rid of there old one.
Doug -
Re: Please help, Very confused
So lets run some more numbers; 7 KWh a day, 2 days backup, 4.1 hrs of sun / day (Erie PA), 48 volt battery bank 50% discharge
19 120watt panels @~ $3.00 / watt = $6,840
1 Charge Controller @~ $529
24 CR395 Batteries @~ $285 (less the four you allready have) = $5,700
Outback 3648 Inverter @~ $2,000
Sub Total = $15,069
Still need to add; wire, PV combiners, fuses, breaker panels, PV racks ect.
And, every 5 or so years you will need another ~ $7,000 worth of batteries.
11 cents a KWh is not bad ... 9 cents base line then 12 cents here ... I would be connected if they were reasonable about bringing me the wire. -
Re: Please help, Very confused
11 cents per kilowatt is what VanDuesen rate is. He thinks electric co is charging him too much.
My electric co. Pennpower which is a division of First Energy has a message on the bill that I would have to be able to pay below 9.44 cents if I wanted an alternate supplier. -
Re: Please help, Very confused
As I stated, I would connect if the power co was more reasonable in bringing me the wire. Would do a grid connect with battery backup. $0.66 to $0.77 a day is cheap! One wonders how they can do it for 0.11 / KWh considering line losses and infrastructure upkeep...
Battery costs alone put me at $.059 / KWh. ($7,000 every 5 years)
$0.421 / KWh if the batterys last 7 years -
Just got a combiner... Help please!
ok so I just got in the MNVPV6 (COMBINER) AND just need to make sure I understand what I am doing. THe combiner IS NOT a breaker box correct? It is a way to combine the solar panels right? To my understanding instead of cutting the wires and running the solar panels pos to pos for 6 of them and have a big mess you would use the combiner to neatly connect all of them together, This is providing you have at least a 60amp controller right? If I am correct, then I would run the solar panels to the conbiner then take the pos and neg from the combiner and run it to the controller then to the batteries right?
I have NOT started to hook up the combiner yet because I want to make sure that I am correct. If I also understand it, then each solar panel will have a 15a breaker between the solar panel and the controller to help save the controller?
Thanx in advance. -
Re: Please help, Very confused
The meter was not damaged? -
Re: Please help, Very confusedTHe combiner IS NOT a breaker box correct?
Then a pos + wire connects to the comb and a neg - wire to the bus bar the, these go to the charge controller.
Before you connect, what charge controller did you get? What are the specs on your panels? Are you going to run any of your panels in series of all in parallel? -
Re: Please help, Very confusedYes it is a breaker / fuse box. The "hat track" at the top is a DIN rail. you mount either breakers or fuse holders to this rail. The pos + from the panels goes to the bottom of the breaker/ fuse and a comb goes into the tops of the breaker/fuse. The neg - from the panels go to the bus bar.
Then a pos + wire connects to the comb and a neg - wire to the bus bar the, these go to the charge controller.
Before you connect, what charge controller did you get? What are the specs on your panels? Are you going to run any of your panels in series of all in parallel?
I need to stay with 12v so That would mean that I would have to remain with parallel right? I currently have 4-120w solar panels 3 of which are hooked up to a sunforce 30amp controller BUT I just ordered the Morningstar TriStar TS 60 PWM Charge Controller Solar -
Re: Please help, Very confusedI need to stay with 12v so That would mean that I would have to remain with parallel right?
-
Re: Please help, Very confusedAs I stated, I would connect if the power co was more reasonable in bringing me the wire. Would do a grid connect with battery backup. $0.66 to $0.77 a day is cheap! One wonders how they can do it for 0.11 / KWh considering line losses and infrastructure upkeep...
Tax breaks, tax breaks, tax payer funded bailouts, free right-of-ways, environmental avoidance (let the taxpayers clean up the mess). Oh and tax breaksPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Please help, Very confusedTax breaks, tax breaks, tax payer funded bailouts, free right-of-ways, environmental avoidance (let the taxpayers clean up the mess). Oh and tax breaks
And in the case of BC Hydro, selling power to 'sucker' California utilities for 10 times its worth. -
Re: Please help, Very confusedParallel will probably be correct but, not because of the 12 v. What is the Vpmax of your panels?
7.6 I deo believe. If you are asking what is the max it puts out. -
Re: Please help, Very confused7.6 I deo believe. If you are asking what is the max it puts out.
-
Re: Please help, Very confused7.6 would be the amprage ... looking for the operating voltage should be ~ 15 v
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed