Any PV Electricians?
funidea
Registered Users Posts: 6 ✭
I am installing 30 Kaneka 60w (67V,0.9A) on my garage to a Fronius 3000 inverter (max 500V, max current 13.6A). Can anyone help me on string configuration. How do i configure these 30 modules to one inverter?
Comments
-
Re: Any PV Electricians?
A guess would be 6 strings, of 5 panels.
330V string, .9A total 5.4A@ 330V
I have no idea if that's within your inverters capacity, or in it's MPPT range. It's about the only way to slice up those panels though.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Any PV Electricians?
It depends on what your coldest day is. I have one of those inverters and am satisfied with it so far.
solarvic -
Re: Any PV Electricians?
You should look on the fronuis web site and get thier configuration chart. Thier chart is color code. Yellow= array may be undersized. Green means optium and orange too high of voltage. Actually your !G 3000 is lots bigger than needed, Ig 2000 will do12 strings of 3. Can you get 6 more panels? To get out of the yellow zone you need at least 12 strings of of 3 to get in the green. At 10 strings of 3 you get 1809 watts @ stc of 201 v total. You are in the yellow zone. For my area I would want strings of 4 do to the cloudy weather. Your ig 3000 can do 13 strings 0f of 4 down to -4 degree F. So when someone ask about how to do something like this they should say thier coldest day and hottest day on record. The amount of 30 panels is kind of low. If it were me I would get at least 6 more to get in the green. I thought about getting a pallet of those also but I decided Against that because I get snow on my roof that stays there a couple months of the year and the output of them is too low to be putting on top of pole mounts. S:-)larvic -
Re: Any PV Electricians?3 strings of 12.
67v x 12 cells =804 Volts. That won't last very long !Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Any PV Electricians?
Solarvic has the chart inverted.
It's 12 strings of 3 (etc), not 3 strings of 12. These are very high voltage panels.
Don't know your temperature ranges, but with the defaults it only likes strings of 3 or 4 modules, so that means 10 strings of 3 I reckon.
If you're in an area that never gets below freezing you can do 6 strings of 5.
For strings of 3 you're probably going to want to look at what the real temperature effects will be - coefficients and all, because you might occasionally have too low a voltage.
And the inverter is bigger than you need, but I guess it would still work fine - but someone else can probably answer that with more certainty. -
Re: Any PV Electricians?Solarvic has the chart inverted.
It's 12 strings of 3 (etc), not 3 strings of 12. These are very high voltage panels.
Don't know your temperature ranges, but with the defaults it only likes strings of 3 or 4 modules, so that means 10 strings of 3 I reckon.
If you're in an area that never gets below freezing you can do 6 strings of 5.
For strings of 3 you're probably going to want to look at what the real temperature effects will be - coefficients and all, because you might occasionally have too low a voltage.
And the inverter is bigger than you need, but I guess it would still work fine - but someone else can probably answer that with more certainty. -
Re: Any PV Electricians?
http://www.xantrex.com/support/gtsizing/index.asp?lang=eng#calculator
It has your panel in the list, on the bottom left will give min/max voltages
Looks like 4 in series is fine, 5 maybe if your not to cold ( for each string )
Don't forget, you need each string to be fused -
Re: Any PV Electricians?A guess would be 6 strings, of 5 panels.
330V string, .9A total 5.4A@ 330V
I have no idea if that's within your inverters capacity, or in it's MPPT range. It's about the only way to slice up those panels though.
Categories
- All Categories
- 220 Forum & Website
- 128 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 606 Discussion Forums/Café
- 300 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed