In my earlier response about battery size, I forgot about the ripple current the AC sinewave inverter puts on the battery. The ripple current from inverter sinewave power profile will put ripple current on battery at twice the AC line frequency rate.
The net charge to battery may be zero due to PV charge controller supplied power but for high inverter output AC power push, the ripple current that is impressed on batteries can be quite large.
With a solar charge controller tied to batteries, the PV output is mostly a smooth continuous PV illumination based current push to batteries and inverter DC input. The batteries act as large filter capacitor to smooth the inverter's AC power profile ripple current.
This means the battery size must be large enough to take the large ripple current even though the average power taken from battery is zero.
-
I think I understand now, is it sort of like water hammer is to plumbing, slamming of the water for a split second it bounce back and essentially the inverter it turning on and off starting and stopping that load from the batteries. We need bigger capacitors
3kw solar PV, 4 LiFePO4 100a, xw 6048, Honda eu2000i, iota DLS-54-13, Tesla 3, Leaf, Volt, 4 ton horizontal geothermal, grid tied - Green Bay, WI -
If your application is to primarily provide AC power supplementation with only occasional grid power outage you are better off to use PV grid tie battery-less inverter to supplement AC power. Using an XW with DC coupled PV power puts a large continuous ripple current on batteries that will wear them out.
You could use an AC coupling arrangement, but I would probably keep GT inverter directly on grid mains most of time to avoid the issues with reverse power surge push into XW output when grid is down. GT PV inverter power output control with frequency shifting by XW is slow reacting.
With no grid power, battery backup operation, during high PV production, if you switch off a large house load there is a sudden overproduction that must be sucked up by XW inverter until it does the frequency shifting, GT inverter recognizes it and backs down its production. This can also happen when grid drops out eliminating ability for PV power grid push. This can take up to a couple of seconds to correct during which the XW is getting hit with the large back surge current from PV GT inverter.
There is no battery charge current regulation for AC coupling back surge, other than inverter shutting down for DC input voltage over high end limit. Generated power always has to go somewhere. -
This is helpful in understanding all this. Our situation is I wanted significant loads to be backed up essentially via solar, but our utility wants $20 a month of a PV meter and then $.02 per kWh credit back, that wasn't going to work so what I have now is to disconnect from the grid during on peak or high rate and re-connects during off peak or low rate. I did consider leaving the XW connected to the grid (it is set to not sell back to the grid but the lowest input I could set was 1 amp. so it was drawing 240w all day.3kw solar PV, 4 LiFePO4 100a, xw 6048, Honda eu2000i, iota DLS-54-13, Tesla 3, Leaf, Volt, 4 ton horizontal geothermal, grid tied - Green Bay, WI
-
Hey Brock, are you using a timer to make that determination? I've been tinkering with this device to switch to the utility (could alternatively use a generator) to charge the batteries and/or remove the load on the batteries and to default to the batteries when they are up to the task.My transfer switch is a Generac 200amp and the whole house switches with the transfer switch. My current bank of batteries is almost enough to do this off grid testing, but it is dependent on worst case factors. Hence my looking into more batteries...For now, no permanent changes are contemplated until the dust settles with PG&E and their attempts to modify the solar environment instead of modifying their business model.Nick
-
The funny thing is for 15 years we actually had a normally open lead from our meter, it would close for on peak and critical peak and stay open for holidays and weekends. Our local utility got bought out and now, for some reason they say our meter can't control it anymore, go figure. I have a plain old digital timer feeding the contactors, so holidays are a manual switch for us. The only annoying part is if they schedule a critical peak during off peak times, I have to run home or have someone at home turn everything off, very annoying. You would think they would have liked it the way it was before where they could hit a button and all kinds of loads shed from the grid...
Even on a "busy" day with the kids home the most we have pulled is about 5 kWh of the 20 kWh bank so I am not as worried about a low battery disconnect, although then it would be more automated overall.
3kw solar PV, 4 LiFePO4 100a, xw 6048, Honda eu2000i, iota DLS-54-13, Tesla 3, Leaf, Volt, 4 ton horizontal geothermal, grid tied - Green Bay, WI -
Open loop would be the XW or it's chargers not actively managing charge/ discharge from BMS data. You will not get Soc data on the SCP or Insight devices out to the Cloud. The BMS in closed loop would actively monitor the xanbus network. You probably are fine with a 400AH bank.Brock said:What is an open loop charge/discharge? I do have the xantrex set to only 25 amps charge if needed in the middle of the night. Each 48v 100a battery has its own 100amp BMS so I really have 400 amps at 48 (54) volts with 800 amps surge, which I hope to never need. Most of the time I am pulling under 1000w or about 20 amps from the bank or 5 amps per pack.
A 100AH bank could be damaged by XW in a big surge or charging from a large source if it were open loop.
The homes below with the green 100 (in bat Soc) are closed loop systems that get Soc out to the cloud or your phone.
"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
I have the same problem...dc over voltage...on the xw4548 it is f63
I found the problem to mine is the amperage sensor that detects how many amps are coming in from the batteries after the board with all the capacitors on it
the thing in this picture on my post .....the solder connections are bad
https://forum.solar-electric.com/discussion/comment/404751#Comment_404751
this could be your problem
12 panels 6 series 2 parallel 2100 watts, 1 XW60-150 CC, 16 trojan 6V batteries 8 series 2 parallel 450 Ah, 1 XW 6848 pro, 1 5500 watt champion inverter generator( I know...I need a 12Kw ) -
For what it's worth I recently changed from eight L-16's to four 48v 100A LiFePO4 server rack batteries with built in BMS to power our Xantrex 6048. It wasn't cheap, but so far I am really liking it, no maintenance, no venting, smaller, cleaner. I just set the xantrex to the bulk / float setting for the new batteries and it works great."Hi Brock, just getting back to this and I reread this entire thread. Your post comes close to answering the one question that nags me about LiFePO4 batteries. The XW6048 does not have a Lithium selection for the battery type. I saw that you posted that you used the stated battery bulk and float settings, but what Battery type did you use and did you change the charge type to "no absorption"?Hopefully all is still going ok?TIA, Nick
Categories
- All Categories
- 229 Forum & Website
- 136 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 179 Solar Information links & sources, event announcements
- 892 Solar Product Reviews & Opinions
- 252 Solar Skeptics, Hype, & Scams Corner
- 22.5K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.6K Off Grid Solar & Battery Systems
- 428 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 656 Solar Water Pumping
- 816 Wind Power Generation
- 620 Energy Use & Conservation
- 622 Discussion Forums/Café
- 316 In the Weeds--Member's Choice
- 74 Construction
- 125 New Battery Technologies
- 107 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed