mppt controller input is 150v and have 3 panels of 48v 500w each in parellel total is 144v .(3x48v)
Is it ok or too risky
Bob
mppt controller input is 150v and have 3 panels of 48v 500w each in parellel total is 144v .(3x48v)
Is it ok or too risky
Bob
Comments
-
robocop said:Hi
mppt controller input is 150v and have 3 panels of 48v 500w each in parellel total is 144v .(3x48v)
Is it ok or too risky
BobOff Grid. Two systems: 1) 2925w panels, OB VFXR3648, FM80, FNDC, Victron BMV-712, Mate3s, 240 xformer, four SimpliPHI 3.8; 2) 780w, Morningstar 30a, Grundfos switch, controller and AC/DC pump, 8 T105. Honda EU7000is w/AGS. Champion 3100. HF 4550, Miller Bobcat. -
Bob, it is "close"... The system is installed in the southern Caribbean sea off the coast of Venezuela (as I recall).
Curaçao island, West Indies
Your minimum temperature is around 68F (20C)? The Voc/Isc/Vmp/Imp are based on 25C spec sheet rated panel temperature.
What is the panel rating of 48 volts--Is that Voc or Vmp @ 25C?
If that is 48 volts Vmp--Then 3 panels in series would be >150 Volts (Voc-array-cold) as Vmp is lower voltage than Voc (voltage open circuit.
If that 48 volts is Voc-panel-std -- You might not exceed 150 VDC Voc-array-cold for your area (Voc and Vmp array rise as temperatures drop below 25C).
A 3*48volt Voc series array would reach ~146.4 volts Voc-array-cold using this array calculator:
https://www.midnitesolar.com/sizingTool/index.php
It is close--But could work OK. However, if some weird cold front moves through your place several years down the road--All bets are off.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
As BB mentioned, the correct term is SERIES, not parallel. In parallel the voltage doesn't add, the current (amps) does.
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Hi especially for Bill you were right I gave wrong details the voc is 58.95 NOT 48v this is the vmp .
so has to put only 2 panel in series . So if use panel has to combine 2S3P .
now only look for a photo with combination to illustrate how to combine.
again I am thankful for your advice . -
Typical Combiner box. Often installed near the PV array. Strings in, one pair of larger wire out
2.1 Kw Suntech 175 mono, Classic 200, Trace SW 4024 ( 15 years old but brand new out of sealed factory box Jan. 2015), Bogart Tri-metric, 460 Ah. 24 volt LiFePo4 battery bank. Plenty of Baja Sea of Cortez sunshine.
-
Think of the combiner box as very similar to a standard power panel (main power in, multiple branch circuits out)... However the combiner box is just multiple solar panels in, and the "main power" out to the input of the MPPT charge controller.
MidniteSolar (supplier to our host Northern Arizona Wind & Sun / NAZ) has quite a few documents & videos on their products... For example:
https://midnitesolar.com/productPhoto.php?product_ID=77&productCat_ID=9&sortOrder=5&act=p
Also--Think about lightning protection (surge suppressors) if that is an issue for you(?). Mostly, you want to keep the lightning energy outside of your home (to the best of your ability/design).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
thanks for your advice of the combiner box BUT I meant how to wiring the 5 solar panels in 2 serial and 3 parallel (2S3P).
best regards
Bob -
You cannot... Your options are:
2s*2p (4 panels only, one "unused" panel)
2s*3p (6 panels, purchase one more)
1s*5p (5 panels, only if the battery bank is 12 or 24 volts--Not high enough voltage for 48 volt bank)
There are other options such as 2s*1p (2 panels) on your present charge controller, and purchase a 2nd "higher voltage" 3s*1p (other 3 panels).
Or purchase a much higher rated array voltage controller and run a 5s*1p array (5 panels total).
Or am I "not understanding" your question?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Yes yes Bil thank you understood and thnks for your time.
Bob
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed