Generator/Inverter generator options
photonboy
Registered Users Posts: 23 ✭✭
Looking for help selecting/sizing a generator for my off-grid cabin. I have an Outback VFXR3524A which suggests 2230VA of power to charge. Is there a reason I need to get an inverter/generator or can I go with a just a generator (considerable cost savings); I was going to go with a Honda EM 6500. I planned on using the generator for battery charging through the inverter, 240V well pump, and power tools. My computers are laptops and I have an AC fridge. Any guidance/advice appreciated.
Chris
Comments
-
Any well tuned conventional generator should be stable enough to work for you. An inverter-generator is an unneeded expense
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Thanks Mike. That is what I was thinking. Appreciate the helpChris
-
When picking a genset... Sizing the genset to the load is also important....
For gasoline/propane type genset, the "standard" alternator type, is most efficient when running from 50% to 100% of rated output. When running a standard type genset below 50% of rated output, the fuel flow only drops a little from 50% loading to 0% loading (motor must keep generator spinning at 3,600 or 1,800 RPM for constant 60 Hz output).
Inverter type generators--They are fairly fuel efficient down to 25% of rated load... So if you spend lots of time with light loads, an inverter-generator can save you lots of money on fuel bill.
In your case, needing a 240 VAC genset--You are limited in how many "smaller capacity standard or inverter gensets" that have 120/240 VAC output...
So, what is the AH and voltage rating of your battery bank... Typically 10% to 20% charging current suggested for your battery bank. And I suggest that your load your genset for 50% to 80% of rated output (residential gensets should be derated to 80% for continuous loads like charging a battery bank).
Running the genset (when needed during bad weather) in the early mornings and letting solar take over the late morning/afternoon is fuel efficient. Also, charging the battery bank from 50% to 80% with genset (even if there is "no sun") is also fuel efficient and good for battery health (you only need to charge to >90% SoC once a week to even once a month--If you are daily cycling the battery bank). One need to charge >90% when putting system away for winter (and/or leave on solar charging during winter)....
The other option is to have two gensets--One large genset for heavy power needs (battery bank charging, running shop tools, etc.). And a smaller 2k-3kWatt or so genset for emergency backup / portable 120 VAC power. Years ago, Honda was (pretty much?) the only company that offered true sine wave inverter-generators. Today, PSW/TSW inverter generators seem to be the standard (MSW is "hard" on some AC electronics/induction motors/refrigerators/etc.).
Also for electric start generators--You might want to look at a small solar panel + charge controller to float charge the battery when not in use.
https://powerequipment.honda.com/generators/models/em6500AC Output 120/240V 6500W max. (54.2/27.1A) / 5500W rated (45.8/22.9A)iAVR Output 7000W (58.3/29.2A) for 10 sec.Fuel Tank Capacity 6.2 GallonsRun Time per Tankful 6.4 hrs.@ rated load, 9.8 hrs. @ 1/2 load
full power Watt hours per gallon = 5,500 Watts * 6.4 hours * 1/6.2 gallons = 5,677 WH per gallon
1/2 power WHpg = 5,500 Watts * 1/2 load * 9.8 hours * 1/6.2 gallons = 4,347 WH per gallon
Fuel flow full power = 6.2 gallons / 6.4 hours = 0.97 GPH
Fuel flow 1/2 to 0 power = 6.2 gallons / 9.8 hours = 0.63 GPH
https://powerequipment.honda.com/generators/models/eu2200i-companion
AC Output120V 2200W max. (18.3A) , 1800W rated (15A)Fuel Tank Capacity 0.95 gal.Run Time per Tankful 3.2hr @ rated load 8.1 hrs @ 1/4 load
full power WH per gallon = 1,800 Watts * 3.2 hours * 1/0.95 gallons = 6,063 WH per gallon (full power)
1/4 power WH per gallon = 1,800 Watts * 1/4 loading * 8.1 hours * 1/0.95 gallons = 3,837 WH per gallon (1/4 power)
Fuel Flow full power = 0.95 gallons / 3.2 hours = 0.30 GPH (full power)
Fuel Flow 1/4 power = 0.95 gallons / 8.1 hours = 0.12 GPH (1/4 power)
To run "light loads", the 6,500 Watt genset will use (0.63 gph/0.12 gph = ) 5.25 times more fuel -- So it is very important (fuel cost wise) to size your genset to your needed/expected loads & usage.
Charging a good size battery bank for hours at a time at 50% to 80% loading, a "standard" genset will be very nice and cost effective.
For building your cabin/home (as an example) where you are running circular saw and charging power tool batteries for relatively short periods of time, but running the genset 8-10 hours of day (at low power, or no power) a standard genset will just suck down the fuel.
I used Honda here as they have pretty good specifications (they tell you 100%/50%/25% fuel usage). But there are a bunch of other brands out there in standard and inverter genset types--And it makes it hard to ignore the cheaper brands out there...
Plus those of us in California--The present SMOG/Emmisions laws seem to have kicked Honda out of the market for now.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed