How many Batteries do I need?
hmong2017
Registered Users Posts: 39 ✭✭
Item:
Water Pump for pond that has no access to grid.
250 WATT
120 VOLT
Plugged in and running 24-7.
Current System, NO BATTERIES YET.
x6 of 12v 100 WATT Solar Panel in Parallel.
40A MPPT Charge Controller
2000 WATT Power Inverter
I plan to use 200AH Lithium Battery vs. the Gel or AGM Batteries. Please advise if I should go with these instead.
Will 2 battery in parallel to make 400AH be enough to run day and night?
DIRECT SUN INFO:
Winter; Aprox 17 HOURS NONE or NO DIRECT SUN
Summer; Aprox 10 HOURS NONE or NO DIRECT SUN
Water Pump for pond that has no access to grid.
250 WATT
120 VOLT
Plugged in and running 24-7.
Current System, NO BATTERIES YET.
x6 of 12v 100 WATT Solar Panel in Parallel.
40A MPPT Charge Controller
2000 WATT Power Inverter
I plan to use 200AH Lithium Battery vs. the Gel or AGM Batteries. Please advise if I should go with these instead.
Will 2 battery in parallel to make 400AH be enough to run day and night?
DIRECT SUN INFO:
Winter; Aprox 17 HOURS NONE or NO DIRECT SUN
Summer; Aprox 10 HOURS NONE or NO DIRECT SUN
Comments
-
Will this be a stand alone system? Does it get below freezing? If so lithium is likely a poor choice.
The available power/sun is better figured out using this site, it will give you the average available power by month for an array. Including the orientation of the array.
PVWatts Calculator (nrel.gov)
Strongly recomend not buying anything else until you calculate your needs.Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
You need to first tell us about how much energy per day your pond pump will take... Is this a 24x7 operation, or just a few hours per day? Using a Kill-a-Watt type meter will be much more accurate:
https://www.amazon.com/s?k=kill+a+watt+meter
Is this to "go green" or because there is no 120 VAC power close to the pond?
Where is the pond located (nearest major city)? The "hours of sun" per day--In reasonably sunny South West US location, you are looking at >3 hours per day of "good sun" in the winter... Is the pond seasonal (less/no pumping in winter)?
http://www.solarelectricityhandbook.com/solar-irradiance.html
Based on what you have said so far, this is what a system would look like for 24 hour per day pumping all year long:- 24 hours per day * 250 Watt AC load = 6,000 WH per day
- 6,000 WH per day * 1/0.85 AC inverter eff * 1/0.70 lithium "usage factor" * 1/12 volts = 840 AH @ 12 volt lithium bank for 1 day "no sun"
- 6,000 WH per day * 1/0.61 Li Ion battery bank solar efficiency * 1/3 hours per day Winter sun = 3,279 Watt array "winter sun" break even array
In general, solar power will cost you more money that simply burying 100-200 Feet of direct burial 14 or 12 AWG copper cable from your home to the bond (typical 18" deep at least, below the frost line in cold climates).
Also, looking for the most efficient loads (for a small pond, a 12 volt or 24 volt DC air or water pump, as small as would work for yoru place.
If you only need pumping air/water when the sun is up--You can also save on battery bank--Just power the pump directly from solar panels (not always easy either to match solar array output to DC pump input requirements.
-Bill
Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Great ideas people! How about this, Is there a device that I can plug into a wall outlet and the Solar system? Where as it automatically switches back and forth when solar or solar batteries are low to Wall outlet, then switches back when the Solar system is receiving sun and ready to use? I can have an electrician run a buried cable from the meter pole to the pond. There is a well on the property connected to the grid. But the Pond is very far away. What happen is in Summer when the water is very warm, Oxygen levels in the pond depletes. I need this pump 24-7 to produce oxygen. It's going to be around 900 feet of cable, but like you guys mentioned, the big solar offgrid system will cost me too much. I am just trying to Save money on my monthly bill, as I live in California. Electricity runs about $0.40 per Kwh. Bills can reach as high as $300 a month!!!! I am in zone 9B, where temps can get in the low 25F in winter. I will stick with 200AH Lithium batteries. Get two, to make 400AH. Hoping the times it run, I can save a few dollars a month. Also, when We are out at the pond, I can charge my phones, or add lights to a porch at night and utilize the solar system. If you know what I mean.
-
BB. said:You need to first tell us about how much energy per day your pond pump will take... Is this a 24x7 operation, or just a few hours per day? Using a Kill-a-Watt type meter will be much more accurate:
https://www.amazon.com/s?k=kill+a+watt+meter
Is this to "go green" or because there is no 120 VAC power close to the pond?
Where is the pond located (nearest major city)? The "hours of sun" per day--In reasonably sunny South West US location, you are looking at >3 hours per day of "good sun" in the winter... Is the pond seasonal (less/no pumping in winter)?
http://www.solarelectricityhandbook.com/solar-irradiance.html
Based on what you have said so far, this is what a system would look like for 24 hour per day pumping all year long:- 24 hours per day * 250 Watt AC load = 6,000 WH per day
- 6,000 WH per day * 1/0.85 AC inverter eff * 1/0.70 lithium "usage factor" * 1/12 volts = 840 AH @ 12 volt lithium bank for 1 day "no sun"
- 6,000 WH per day * 1/0.61 Li Ion battery bank solar efficiency * 1/3 hours per day Winter sun = 3,279 Watt array "winter sun" break even array
In general, solar power will cost you more money that simply burying 100-200 Feet of direct burial 14 or 12 AWG copper cable from your home to the bond (typical 18" deep at least, below the frost line in cold climates).
Also, looking for the most efficient loads (for a small pond, a 12 volt or 24 volt DC air or water pump, as small as would work for yoru place.
If you only need pumping air/water when the sun is up--You can also save on battery bank--Just power the pump directly from solar panels (not always easy either to match solar array output to DC pump input requirements.
-BillGreat ideas people! How about this, Is there a device that I can plug into a wall outlet and the Solar system? Where as it automatically switches back and forth when solar or solar batteries are low to Wall outlet, then switches back when the Solar system is receiving sun and ready to use? I can have an electrician run a buried cable from the meter pole to the pond. There is a well on the property connected to the grid. But the Pond is very far away. What happen is in Summer when the water is very warm, Oxygen levels in the pond depletes. I need this pump 24-7 to produce oxygen. It's going to be around 900 feet of cable, but like you guys mentioned, the big solar offgrid system will cost me too much. I am just trying to Save money on my monthly bill, as I live in California. Electricity runs about $0.40 per Kwh. Bills can reach as high as $300 a month!!!! I am in zone 9B, where temps can get in the low 25F in winter. I will stick with 200AH Lithium batteries. Get two, to make 400AH. Hoping the times it run, I can save a few dollars a month. Also, when We are out at the pond, I can charge my phones, or add lights to a porch at night and utilize the solar system. If you know what I mean.
-
> temps can get in the low 25F in winter. I will stick with 200AH Lithium batteries
Just until the first charge cycle below 32F. Then the batteries become damaged within minutes
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed